MNL-800 both the top green and amber LEDs are on continuously

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • MNL-800 both the top green and amber LEDs are on continuously
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1879 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

MNL-800 both the top green and amber LEDs are on continuously

Picard Product_Support
‎2018-09-10 12:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:03 PM

Issue

What does it mean on an MNL-800 if both the top green LED (Transmit) and the Amber LED (Receive) are on continuously?

Product Line

TAC IA Series

Environment

  • MNL-50
  • MNL-100
  • MNL-200
  • MNL-800
  • MNL-V1R
  • MNL-V2R
  • MNL-V3R

Cause

LEDs indicate LON traffic on the trunk

Resolution

For an explanation of the Transmit (Green LED) and Receive (Red LED) see F-26724, MNL-800 Installation Instructions,
Table 1 LED Indications:

LED Operation Status
Green ON Normally ON indicating controller is powered and not actively transmitting data on the LON.
Flashes OFF Flashes OFF while actively transmitting data on the LON.
Amber OFF Normally OFF unless actively receiving data from the LON.
Flashes ON Flashes ON while actively receiving data from the LON.
Red OFF  (Neuron - normal communications) indicates the Neuron is operating properly allowing normal communications to and from the HVAC application.
OFF  (Neuron - Offline) Neuron responds to network management messages only. In this state, communication to and from the HVAC application is not possible. To correct, place the Neuron online by downloading an application using WP Tech or configure using a third party management tool.
Blinking The service LED blinks at 0.5 Hz rate (1 second ON, 1 second OFF) to indicate that the Neuron is unconfigured (i.e. communications parameters not loaded). Corrective action: Configure the Neuron by downloading an application using the Work Place Technician's Tool or configure the neuron using a third party management tool.
ON Indicates Neuron is not operating properly. Replace controller. 
Heartbeat (Green LED) Blinking (Normal Operation) The heartbeat LED blinks at 0.5 second ON, 0.5 second OFF to indicate controller is operating properly.
Wink Mode Wink mode provides a visual means for identifying the controller using WP Tech or third party management tool. During wink, the heartbeat LED blinks as follows:
With revision 1.x firmware: 2 seconds ON, 0.5 seconds OFF; cycles five times for a total of 12.5 seconds of wink time.
With revision 2.x (or later) firmware: 3 seconds ON, 1 second OFF; cycles three times for a total of 12 seconds wink time.
Diagnostic Blink (RAM/ROM Failure) The heartbeat LED repeats a pattern of 2 quick flashes followed by pause. To correct, turn power OFF then ON. Replace controller if necessary.
Diagnostic Blink (ROM Failure) The heartbeat LED repeats a pattern of three quick flashes followed by a pause. To correct, turn power OFF then ON. Replace controller if necessary.
Diagnostic Blink  (RAM Failure) The heartbeat LED repeats a pattern of four quick flashes followed by a pause. To correct, turn power OFF then ON. Replace controller if necessary.
OFF Indicates controller is not operating properly. Check power. Replace controller if necessary. 

 

led-indicators.gif

 

If the amber LED is blinking fast enough, it appears to be ON continuously, so it is receiving data at a high frequency.

The other MNL devices on the same LON should all be behaving the same way, indicating a lot of LON traffic. Confirm with a LON protocol analyzer.

If excessive LON communications traffic is suspected, see How can LON communications be throttled in MNL-800 controllers? for a method of throttling LON traffic.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 5773
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of