Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • RyanSuar
    RyanSuar
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7449 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal

Picard Product_Support
‎2018-09-10 09:11 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:59 PM

Issue

Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal

Product Line

TAC IA Series

Environment

  • I/A Series R2 Universal Network Controllers:
  • UNC-410-1
  • UNC-410-1-N
  • UNC-520-2
  • UNC-520-2-N

Cause

There maybe a need to access the UNC via its serial port if the IP address of the UNC is unknown or for troubleshooting purposes when the UNC's Ethernet port is not functioning.

Resolution

Hardware required for connection to UNC's RS-232 port:

  • 8-conductor flat silver satin stranded cable with standard male (plug) RJ-45 connectors
  • RJ-45 to DB-9 adapter (part number: UNCC-405) or a socket-to-plug type RJ-45 to DB-25 adapter (part number: UNCC-430)
  • A functioning COM port on a computer
  • A 2-pin jumper for connection to the UNC's "Mode" connector

Refer to the Installations Instructions for UNC-520 (page 15) for details on the cable and adapter (applies for both UNC-410 and UNC-520). Pinout configuration for a RJ-45 to DB-9 Null Modem Adapter (part number UNCC-405) also refers to these pin outs.

Connection to UNC's VxWorks Target Shell using Windows HyperTerminal (for operating systems without HyperTerminal, please refer to Hyperterminal on Microsoft Windows Operating Systems😞

  1. Connect the cable and adapter between the UNC's RS-232 port and the RS-232 COM port used on the computer.
  2. Start HyperTerminal (Programs > Accessories > Communications > HyperTerminal).
  3. In the 'Connection Description' dialog, type a name for this session. For example, 'Connection to UNC'. Click OK.
  4. In the 'Connect to' dialog, use the 'Connect using' drop-down list to select the COM port used on the computer. Click OK.
  5. In the Com(n) Properties dialog, choose the following settings:
    • Bits per second: 9600
    • Data bits: 8
    • Parity: None
    • Stop bits: 1
    • Flow control: Hardware
    • Click OK.
  6. On the UNC circuit board, locate the 4-pin Mode connector and put a 2-pin jumper on the 2 outer pins. Refer to page 17 UNC-520 Installation Instructions for position of the Mode connector (top right corner).
  7. With the HyperTerminal session active, remove power from the UNC, let it cycle down, then reapply power. After some number of seconds, text should appear in the HyperTerminal window similar to:
    Press any key to stop auto-boot...
  8. To enter commands to the UNC, press any key to break out of the boot sequence. A prompt similar to the following is shown:
    [VxWorks Boot]:
  9. To determine the IP address / subnet mask of the UNC, do not break the auto-boot sequence as described in step 7. Allow the UNC to finish booting.
  10. When the controller stops displaying new messages, press ENTER to reach the command prompt. The prompt is similar to the following:
    ->
  11. Using the scroll bars on the HyperTerminal window, scroll up until the section that begins with the line 'Press any key to stop auto-boot...'. The IP address of the UNC is listed on the line that begins 'inet on ethernet (e)' The IP address is listed (in dotted decimal), followed by a colon, and then the subnet mask (in hexadecimal).

Disconnect from the UNC when complete.

  1. Press the 'Disconnect' button on the HyperTerminal toolbar.
  2. Exit from the HyperTerminal application, selecting to Save if planning to reuse this HyperTerminal setup for future connection to an UNC.
  3. Remove the 2-pin jumper from the Mode connector of the UNC.
  4. Reboot the UNC by removing the power connector, waiting for all lights to extinguish, and plugging the power connector back in.

* If troubleshooting the UNC, send the HyperTerminal start up messages to Product Support for analysis.

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (1)
  • Find more articles tagged with:
  • 7837
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore