A red exclamation mark is seen with a discovered MNB controller icon in WorkPlace Commissioning Tool
  • A red exclamation mark is seen with a discovered MNB controller icon in WorkPlace Commissioning Tool
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
  • CraigEl
    CraigEl
‎2018-09-11 08:08 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:25 PM
TAC IA Series
  • I/A Series WorkPlace Commissioning Tool
  • I/A Series Micronet BACnet controller (MNB)
The WorkPlace Commissioning Tool has lost communications with the BACnet device
Resolve the BACnet communications issue. Refer to BACnet MS/TP Bus Communication Troubleshooting Checklist.
Refer to the table below which is extracted from the IA Series MicroNet BACnet WorkPlace Commissioning Tool and Flow Balance Tool Users Guide.
Icon and Type Applicable Devices Meaning
Remote I/O Warning
MNB-1000 A remote I/O module connected to the MNB-1000 controller is in a state other than "online and configured" (status code 0x03).
Lost Communication
All Devices The Tool is no longer able to communicate with the device.
Operation in Progress
All MNB-xxxx Devices Device is in the midst of an operation. For example, the device may be undergoing a firmware upgrade, or an MNB-Vx VAV Controller may be performing a Check Rotation.
  • TAC IA Series
  • 13995