Issue
Require LonWorks shadow device object for Danfoss device with program ID 80:0:8:3c:a:84:4:11
Product Line
TAC IA Series
Environment
I/A Series R2
Cause
The lonDanfoss module prior to version r2.301.529 does not have the shadow device object for Danfoss device with program ID 80:0:8:3c:a:84:4:11. Some NCIs cannot be read if a DynamicDevice is used.
Resolution
The shadow device object for Danfoss device with program ID 80:0:8:3c:a:84:4:11 (VltFc100V121) is available in lonDanfoss JAR file version 2.301.529a. You can download the JAR file here.
This is also available in I/A Series R2 version r2.301.532.
Refer to How to install an I/A Series R2 JAR File for the procedure to install an updated JAR file to an I/A Series installation.