Issue
Will the TE200AD24 sensor from Greystone Energy work with a MNB controller?
See the datasheet.
Product Line
TAC IA Series
Environment
MNB controllers
Cause
Retrofitting an existing 3rd party control system with a MNB controller
Resolution
Any 10k thermistor Type G (U.S. Sensor), Type 9 (Dale/Vishay) or Type III (ACI Series AH) can be used with the MNL/MNB controllers.
An 11k shunt resistor wired in parallel with the sensor (1/8 watt, +/- 0.1% tolerance) is also required.
See What 10k Thermistor sensors are compatible with the I/A Series MNL and MNB families of controllers?
The inputs only take a 10k resistive load. So, for the setpoint slider, use a 10k linear pot. The datasheet says the AP model comes with a 20-30k pot and that you’ll have to call for other values.
The 5 Vdc source required is not available on the MNB-300. It is available on the MNB-1000