MN-S# sensor connected to MNB-1000 showing all segments lit up
  • MN-S# sensor connected to MNB-1000 showing all segments lit up
  • Kim_Baze
    Kim_Baze
  • CraigEl
    CraigEl
‎2018-09-10 05:17 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:10 AM
TAC IA Series
I/A Series MNB-1000
Connecting a UI to a Binary Input set as a binary type "pulse" in the MNB-1000's database will cause this.
Per UI inputs of the MNB-1000 do not support pulse inputs, pulse inputs connected to an MNB-1000 must use a DI input.
  1. Correct the database so the pulse input uses one of the DI inputs.
  2. Connect that DI to a Binary Input object set to binary type "pulse."
  3. Compile and download and the issue will clear.