Error when commissioning I/A MNL800 controller in LonMaker
  • Error when commissioning I/A MNL800 controller in LonMaker
  • CraigEl
    CraigEl
  • sesa145087_brid
    sesa145087_brid
‎2018-09-06 12:30 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:28 AM
When commissioning I/A MNL800 controller in LonMaker LNS network management tool, an error will happen:
One or more devices failed to update successfully, due to the following problem: "A device encountered an operational or messaging error while its configuration was being updated. (Subsystem: NS, #4031)"
TAC IA Series, TAC Vista
  • Vista
  • I/A MNL800
  • LonMaker
The issue is possibly due to more than one MNL800 controllers in the LonWorks network have the same Program ID defined in the WPT that causes the commissioning failed.
Open the program of the MNL800 in WPT, right click in the blank place and choose Hardware Wizard. Click Next and modify the Program ID so that each MNL800 has unique program ID. Then it will be fine to commission them in LonMaker.
There is also another method to deal with this issue. Please refer to Error: NS #4031 lcaErrNsUpdateFuncError A device encountered an operational or messaging error while....