Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,898
  • TAC IA Series 1,680
  • TAC INET 1,442
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 16
    • 17
    • 18
    • …
    • 500
  • Next »

Max Info Frames attribute in a Continuum BACnet controller

Issue What is the purpose of the Max Info Frames attribute in a Continuum BACnet controller? Product Line Andover Continuum Environment BACnet MS/TP, MaxInfoFrames Optimizing MSTP Cause Information on the Max Info Frames function. Resolution The Max Info Frames setting on the BACnet controller object editor specifies how many messages that the controller can send out to other controllers when it has the token on the network. For instance, a B3 controller has a default of 2 for this setting. If it receives the token on the MSTP network and it has 5 COV or Event notifications to send to other controllers or workstations, it will send the first 2, and wait until it gets the token the next time around and send 2 more, etc. The BCX controller has a default of 8 for Max Info Frames. This setting is changeable through the BACnet controller editor, however care should be taken not to increase it to too large a number. The larger the setting, the more time that particular controller can hold the onto the token, which in turn denies other controllers on the network the capability of sending out their data in a timely manner. It should only be adjusted if there is a definite need for increased messaging, but on the MSTP network it is not recommended to go above 10, although we do not limit the value. In a Cyberstation Version 1.8 or above the setting can be made on the details page of the BACnet controller device editor. If adjustment of this parameter is done using any Cyberstation prior to version 1.8, the setting will not stay at the new value after a controller reload from the Infinity side, it will revert to it's default. You will need to create a PE program in the controller to set this parameter to the desired value if it is reloaded. The program should be autostart and fallthru, and use the "Writeproperty" keyword to set the parameter. The syntax should be as follows: Line SetMaxInfo WriteProperty ("Full Bacnet path name of controller", MaxInfoFrames, "New Value") Stop
View full article
Picard Product_Support
‎2018-09-06 02:59 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-06-18 02:10 PM

Labels:
  • Andover Continuum
6658 Views

Managing Licensing distribution using the Option's file

Issue How can we exclude Hosts or Users from accessing the Workstation Professional license i.e. Script, Function Block and Graphic editors from another Workstation? Product Line EcoStruxure Building Operation Environment Building Operation License Server FLEXnet Cause When accessing various editors from within Workstation a particular license does not differentiate host or user who should have access to which editors. Using the option file taclic.opt allows you to exclude certain Host / Users of StruxureWare Building Operation from accessing these Workstation clients. The Workstation clients referenced are as follows: client.station (Workstation) client.script (Script Editor) client.functionblock.view (Function Block Editor) client.graphiceditor (Graphic Editor) Resolution FLEXnet Licensing provides the options file to be included in the License Server directory. Each time the License Server service is started this file is checked. Syntax and use can be found in the attached document - Chapter 13 The following option file must reside on the License Server in the following path: Building Operation 1.9 and below: C:\Program Files(x86)\Schneider Electric StruxureWare\Building Operation 1.x\License Server Building Operation 2.0 and above: C:\Program Files(x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server Once this file is copied into the License Server folder, you must restart the license service (via the Windows Control Panel, Administrative Tools, Services). Examples: # The following text excludes the features from Workstation Professional # # Use the following 3 Exclude statements if you wish to exclude an entire Workstation from accessing editors # EXCLUDE client.script HOST enter_host_name EXCLUDE client.functionblock.view HOST enter_host_name EXCLUDE client.graphiceditor HOST enter_host_name # # Use the following 3 Exclude statements if you wish to exclude a Building Operation User from accessing editors # (remove #'s below as required) # # EXCLUDE client.script USER enter_user_name # EXCLUDE client.functionblock.view USER enter_user_name # EXCLUDE client.graphiceditor USER enter_user_name # Notes: The HOST can be defined by either DNS or IP Address The USER is the user name as defined in Building Operation, this may be the same as the Windows username if using Windows Domain.
View full article
Picard Product_Support
‎2018-09-11 04:39 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
6750 Views

Why do Continuum controllers go into bootloader mode?

Issue Why do controllers go into bootloader mode? Product Line Andover Continuum Environment Bootloader NC2 BCX CX99xx CX96xx i2 b3 Cause Continuum controller are placed into bootloader mode if they repeatedly hit a firmware level exception. An exception is when the controller tries to do something that cannot be done.  Some examples of an exception are... A controller tries to read from memory that it cannot read from. A controller attempts write to memory that cannot be written to. On startup, flash generation controllers load the application from flash RAM.When they hit an exception, older, non-flashable controllers would simply clear the application software from ram, power up and wait for the software to be loaded from the front end.  If there is a bad application there needs to be a means by which a user can intervene before the application is loaded so that the controller firmware can be reloaded or upgraded.  When a flashable controller hits more than three exceptions within a ten minute time period the controller is placed into bootloader mode intentionally. Resolution When a controller repeatedly goes into bootloader mode it is time to take a close look at environment which might be driving the controller to hit exceptions A controller usually goes into bootloader mode due to environmental issues such as Heavy ARP traffic Controller grounding Controller power issues Problems with the communication bus. A controller that repeatedly hits exceptions is placed in bootloader mode by design.  Flashing a controllers firmware is the only way to get a controller out of bootloader mode. 
View full article
Picard Product_Support
‎2018-09-06 11:05 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-11 09:00 AM

Labels:
  • Andover Continuum
6642 Views

Determining the default IP address for a UNC, ENC, or Jace 8000

Issue Documentation supplied with new UNC, ENC, or Jace 8000 was discarded.  Is there a way to determine the default, the factory-defined IP address, for the Ethernet port on the controller? Product Line TAC IA Series Environment I/A Series (Niagara) R2 UNC I/A Series (Niagara) G3 ENC Niagara N4 or G3 Jace 8000 Cause Lost or discarded document, shipped with the controller, that contained the configured IP address. Resolution The default Ethernet IP address for an I/A Series (Niagara) UNC or ENC is based on the serial number and type of device. For a UNC or ENC, the default address is 192.168.1.14X where X is the last digit of the device serial number.  The default serial number is found on a sticker on the controller circuit board.  This sticker has the full model number, date code, and the serial number of the controller.  The serial number is preceded with S/N:.The subnet mask is 255.255.255.0 in all UNCs, ENCs, and Jace 8000 The default address base address (192.168.1.140) is the same for all UNC-410, UNC-510, UNC-520, ENC-410, and ENC-520 controllers. The default IP address of a Jace 8000 for PRI (LAN1) is 192.168.1.140.  SEC (LAN2) is by default disabled.
View full article
Picard Product_Support
‎2018-09-06 01:49 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-04-06 05:47 AM

Labels:
  • TAC IA Series
6632 Views

Replacement of Satchwell "M 1301" Actuator forming part of combined Actuator / 3-port Valve Body assembly due to obsolescence.

Issue Satchwell "M 1301" Actuator forming part of combined Actuator / 3-port Valve Body assembly requires replacement. Product Line Field Devices Environment Stand alone Satchwell “M 1301” Actuator forming part of combined Actuator / 3-port Valve Body assembly M 1301 Actuator 3-port Valve Body Cause Obsolescence of Satchwell "M 1301" forming part of combined Actuator / 3-port Valve Body assembly. Resolution There is no direct replacement for the "M 1301" Actuator and as a result both the "M 1301" Actuator and the 3-port Valve Body to which it is connected will also require replacement.  Replace Satchwell “M 1301” combined Actuator & 3-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “M 1301” combined Actuator & 3-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. It is possible that the "M 1301" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 05:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 10:00 PM

Labels:
  • Field Devices
6645 Views

Satchwell VEU 2-port Unit Control Valve replacement.

Issue Satchwell VEU 2-port Unit Control Valve is obsolete. Environment Satchwell VEU 2-port Unit Control Valve installations Cause Satchwell VEU 2-port Unit Control Valve requires replacement due to failure. Resolution Satchwell VEU 2-port Unit Control Valve may be replaced by Schneider Electric VZ219 series Unit Control Valve, although dimensional differences may apply. It should be noted that VZ219 series Unit Control Valves are available in both Flat Face and Compression fitting specifications. The latest issue of the Schneider Electric Valves and Actuators Catalogue should therefore be consulted in order to determine the availability of the particular size / kv / fitting combination required. It should also be noted that any Actuator installed on the Satchwell VEU 2-port Unit Control Valve will not be compatible with the replacement Schneider Electric VZ219 2-port Unit Control Valve and that a Schneider Electric MZ20 series Actuator of the appropriate operating voltage / signal type will also be required.
View full article
Picard Product_Support
‎2018-09-07 01:33 PM

Labels:
  • Field Devices
6606 Views

Replacement I/NET Controller NICAD Battery info

Issue Replacement I/NET Controller NICAD Battery info., I/Net Batteries Product Line TAC INET Environment All I/NET controllers Cause Controller battery has failed, because the battery on the controller is over 5 years old   Resolution The 3 pin version Battery is used for the NPR2000 and the DPU48K (MIP Board) -- part number 3/V80H-SLF (Note this battery has to be order from an outside Vendor and not Schneider Electric). Click here to view a PDF on this part. The 7910, 7920, 7930 7780 & 7940 use the 2 pin version -- part number 3/V80H-LPC (Note this battery has to be ordered from an outside Vendor and not Schneider Electric). Click here to view a PDF on this part. The battery used on the 7700, 7716, 7718, 7728, 7720, 7928, 7793, 7798B, & 7798C (and like controllers) is the Dallas/INET part number 801288-07. This also can be ordered from the Rockford order entry using 01-2100-545 (Old CSI P/N 801288-07). This battery also has an outside Vendor source from Power-Sonic P/N - PCBM-3.6 Click here to view a PDF on this part. For battery testing process see How to test the NiCAD Battery on a Controller
View full article
Picard Product_Support
‎2018-09-10 02:12 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:03 AM

Labels:
  • TAC INET
6619 Views

"Cloud SMS channel offline" system alarm

Issue The System Alarms: "Timeout Cloud SMS channel offline" and "Cloud telemetry channel offline" are never reset and therefore always present in the Alarm view. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Premium Building Operation Enterprise Server Cause When cloud connectivity is enabled, the EcoStruxure BMS sends data from the system to the central storage for diagnostics and analysis along with data from other buildings and sites. Under the Cloud Connectivity Tab, The default communication setting is "Auto". If the customer has the "server.cloud.customer" license feature, the BMS Server tries to activate the cloud communication. The alarms are generated if the ES/AS-P, at some point, was able to connect to the cloud, but then taken off the internet while the setting was "Auto/Enabled". Resolution Upgrade the system to EBO version 3.2.1 or to the latest available version. According to Release Notes for EBO version 3.2.1 this issue should have been fixed in that version, see defect 42293 in Release Notes If the issue is still present see the solution below. The only way to reset the alarm is to have a successful connection to the cloud(Internet) again. Make sure the ES/AS-P has internet access Now the Cloud alarms should go away. Verify that they disappear. Go to the Control Panel in Workstation and click Cloud Connectivity Set the Communication setting to Disable and save the changes. Take the BMS Server off the internet again
View full article
Janeway Jonas_Brissman Janeway
‎2019-09-16 03:04 AM

Last Updated: Guinan RandyDavis Guinan ‎2021-10-26 08:30 AM

Labels:
  • EcoStruxure Building Operation
6616 Views

DC1100 / DC1400 general problems after initial start-up.

Issue Issues being experienced can vary, here are some examples: The digital clock gains a minute every few seconds. The code (0112) when entered to accept alarms, is not accepted. Environment DC1100 controller DC1400 controller Cause The unit has not been correctly cold-started after first being powered on. Resolution The DC1100 / DC1400 controllers must be correctly cold-started after first powering up, this ensures that the default configuration is correctly installed. Cold-start the controller using the following process: Turn off the power to the controller. Press and hold in the ENTER and EXIT keys. Power up the controller whilst continuing to press the ENTER and EXIT keys. Release the ENTER and EXIT keys. The controller will now go through a self test programme and load its defaults. To review the DC1100 / DC1400 controller overview, select here To review the DC1100 controller general data sheet, select here To review the DC1100 controller installation, wiring and Commissioning information select here To review the DC1400 controller general data sheet, select here To review the DC1400 controller installation, wiring and Commissioning information select here
View full article
Picard Product_Support
‎2018-09-07 07:49 AM

Labels:
  • Field Devices
6606 Views

What is the part number for a flying lead temp sensor for Continuum?

Issue What is the part number for a flying lead temp sensor for Continuum? Environment Measuring air temperature in fan coil applications or exhaust ducts Cause On site or inability to find the HVAC Sensor Catalogue Resolution STD550 The 550 is intended for measuring air temperature in fan coil applications or exhaust ducts. The sensor, which are made of stainless steel, is delivered with a 2m (6.5 ft.) cable, PVC sheathed overall. Mounting details such as screw and clamp are included with the product. Description Duct Temperature Sensor STD550 Order Code 5123058400 Part Number STD550 For Continuum Systems   HVAC Sensor Catalog in pdf format
View full article
Picard Product_Support
‎2018-09-10 02:59 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 04:06 AM

Labels:
  • Andover Continuum
6611 Views

Using Sysman Alert Server with EcoStruxure Building Operation

Issue Is it possible to use Sysman Alert Server with EcoStruxure Building Operation? Product Line EcoStruxure Building Operation Environment Alarms and Events Cause Customers may wish to send important alarms to duty staff via SMS. Sysman Alert Server is one way of doing this and is easy to configure.  Resolution This is possible. The following document details the setup procedure: Sysman Alert Server with StruxureWare Building Operation The configuration will depend on the setup and location of the SysMan Server, but will generally involve "Write to File" Notifications if the Enterprise Server and Sysman Servers are installed on the same PC, or Emails to the SysMan Server (from Enterprise or Automation Server) More information can be found on Sysman's website. Part Numbers: SysManSMS ALERT SERVER: 900800600 SysManSMS GSM Modem: 900800610 In the UK when ordering please use the below part numbers. SysManSMS ALERT SERVER: 802000 SysManSMS GSM Modem: 100002
View full article
Picard Product_Support
‎2018-09-11 06:17 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Labels:
  • EcoStruxure Building Operation
6600 Views

What actuators can be used with the VG210R and VG310R ball valves ranges?

Issue What actuators are available? Environment VG210R VG310R Actuators Cause Choice of available actuators. Resolution Suitable Actuators for the VG210R and VG310R ball valves ranges are; Direct fit. MG600C, MG600C SR   With AV-823 Long Stem adaptor. M400 M800 M1500 MG900 SR To view the following data sheets, please select the data sheet required. VG210R,  VG310R, MG600C,  MG600C Installation,  MG600C SR,  MG600C SR Installation and Manual Override instructions
View full article
Picard Product_Support
‎2018-09-11 07:12 AM

Labels:
  • Field Devices
6611 Views

"Property write access denied" error when updating a BACnet trend

Issue Attempts to change the buffer size on an existing BACnet trend result in the following error. Saving Changes Property write access denied '~/BACnet Interface/IP Network_2/VAV01/Application/Trends/RmTmp/Buffer_Size' BACnet Product Line EcoStruxure Building Operation Environment BACnet Trend Building Operation Multi-purpose VAV Building Operation Multi-purpose Controller Cause The buffer size cannot be changed on an enabled trend. Resolution Right-click the trend in question and open the Properties window. Set Log enabled to False. Click OK Open Properties again and change the buffer size to the desired size. Click OK. Open Properties a final time to set the Log to enable back to True. Click OK.
View full article
Administrator DavidFisher Administrator
‎2020-02-25 06:28 AM

on ‎2020-02-25 06:28 AM

Labels:
  • EcoStruxure Building Operation
6629 Views

Router required open port numbers to run a Continuum system

Issue What port numbers do routers have to have open in order to run a Continuum system? Product Line Andover Continuum Environment Cyberstation Continuum BACnet / Infinet Controllers TCP/IP Cause There have been many questions on which network ports the Continuum system uses for communication. Below is a listing of the network ports along with what the port is being used for. Resolution The destination UDP port from the controller will always be one of the below port numbers. The source UDP port that the controller uses is completely arbitrary and will be anywhere from 32768 to 65534. (0x8000 to 0xFFFE) Controller/Cyberstation Application Packet type Decimal port number Hex Port numbers   Controller Error Log Tool - UDP 33487 0x82CF BACNet B4 controller Point Configuration UDP 33487 0x82CF BACNet B4 controller Alarm Configuration, Alarms, and COV UDP 47808 0xBAC0 BACNet B4 controller Controller flash TCP 33456 0x82B0 BACNet B4 controller Web Server TCP 80 NetController Point Configuration, Alarms, and Events UDP 33487 0x82CF Netcontroller Save from Controller TCP 33440 0x82A0 NetController Controller flash TCP 33456 0x82B0 Sending Email  TCP 25 NetController WebServer TCP 80 (but configurable) CX9702 ** Point Configuration, Alarms, and Events See Note 33487 0x82CF CX9702 ** Save from Controller See Note 33440 0x82A0 CX9702 ** Controller flash See Note 33456 0x82B0 CX9702 ** WebServer See Note 80 (but configurable) ** Note: UDP or TCP port (user configurable via the TransportType attribute) Remote View Remote view Video TCP 18772 0x4954 CyberStation Controller Alarms and Events UDP 33487 0x82CF CyberStation Peer Cyberstation communication UDP 44224 (1.4x and 1.5x), 47808 (all other revisions) 0xACC0 (1.4x and 1.5x), 0xBAC0 (all other revisions) CyberStation Workstation to SQL database TCP Determined by Microsoft, 1433 by default CyberStation BACNet communication UDP 47808 0xBAC0 CyberStation MSMQ TCP 1801 0x0709 CyberStation MSMQ UDP 3527 0x0DC7 CyberStation MSMQ UDP 1801 0x0709 CyberStation MSMQ RPC 135 0x0087 CyberStation MSMQ RPC 2101*,2103*, 2105* 0x0835, 0x0837, 0x0839 *Message Queuing message traffic and internal session management traffic between Queue Managers is delivered over Winsock through reserved TCP port 1801. The Message Queuing Independent Client multicasts a server discovery broadcast over reserved UDP port 1801. Message Queuing Servers listen on TCP port 2101* for RPC-based MQIS and Active Directory lookups. Message Queuing 3.0 independent clients and Message Queuing servers make MQIS requests directly to Active Directory by using LDAP on TCP port 389. Message Queuing Independent Clients and Servers listen on fixed TCP port 2103* and 2105* for RPC-based remote reads of their public queues and private queues. Also, the Dependent Client uses these two ports to communicate with its server for send and for receive. There is a dynamic RPC port that is assigned by the RPC layer for handshaking with an Independent Client or with an RPC server for the Message Queuing Server to determine the fixed ports. This is typically port 135. The internal "ping" mechanism for Message Queuing operates over reserved UDP port 3527. When you use HTTP messaging in Message Queuing 3.0, Message Queuing message traffic and internal session management traffic between Queue Managers is delivered over Winsock through reserved TCP port 1801. * These port numbers may be incremented by 11 if the initial choice of RPC port is being used when Message Queuing initializes. A connecting QM queries port 135 to discover the 2xxx ports. For more information on MSMQ ports check with Microsoft, http://support.microsoft.com/kb/178517 A .PDF document containing this Network Port information can be downloaded Here.
View full article
Picard Product_Support
‎2018-09-07 12:37 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:56 AM

Labels:
  • Andover Continuum
6624 Views

Identify the Sigma Version or Build Number Installed on a Computer

Issue Users need to determine the version or build number of the Sigma software installed on their system. Product Line Satchwell Sigma Environment Satchwell Sigma Cause Sigma software installations are identified by build numbers, not just release numbers. This can cause confusion when troubleshooting or verifying compatibility. Resolution To identify the Sigma release and build number: Open the Sigma Client on the Sigma Server. Navigate to Help > About System Manager. A window will display both the release number and build number. Reference Table Use the table below to match build numbers with their corresponding release versions and file dates. Sigma Release No. Build No. Software/Firmware File Date   SigmaX   Release 1 1.52 Software/Firmware 22.06.2001 SigmaX 4.5 Release 2 2.13 Software/Firmware 14.02.2002 SigmaX 5.2 Release 2 3.12 Supplement 14.02.2002 SigmaX 5.2 Release 3 3.12 Software 31.07.2002 SigmaX 5.2 Release 3.1 3.17 Software 17.09.2002 SigmaX 5.2 Release 3.3 3.3 Software 30.07.2003 SigmaX 5.2 Release 3.4 3.31.1 Software 03.10.2003 SigmaX 5.2 Release 3.6 3.32.10 Software 19.11.2003 SigmaX 5.2 Release 3.7 3.33.9 Software 22.12.2003 SigmaX 5.2 Release 3.7 SP2 3.33.11 Software 27.01.2004 SigmaX 5.2 Release 3.7 SP3 3.33.13 Software 19.02.2004 SigmaX 5.2 Release 3.10 3.34.11 Software 21.04.2004 SigmaX 5.2 Release 3.11 3.34.11 Supplement 31.08.2004 SigmaX 5.2 Release 4.00 3.36.11 Software 16.12.2005 SigmaX 6.0.1 Release 4.00 SP2 3.36.16 Software 02 03 2006 SigmaX 6.0.1 Release 4.00 SP4 3.36.20 Software 23.05.2006 SigmaX 6.0.1 Release 4.01 3.37.08 Software 07.09.2006 SigmaX 6.0.1 Release 4.01 SP1 3.37.09 Software 26 09 2006 SigmaX 6.0.1 Release 4.01 SP3 3.37.12 Software 20 10 2006 SigmaX 6.0.1 Release 4.01 SP4 3.37.13 Software 13 08 2006 SigmaX 6.0.1 Release 4.01 SP4a 3.37.16 Software 17 11 2006 SigmaX 6.0.1 Release 4.01 SP5 3.37.18 Software 05 01 2007 SigmaX 6.0.1 Release 4.02 3.39.09 Software 26 01 2007 SigmaX 6.0.1 Release 4.03 3.40.06 Software 06 06 2007 SigmaX 6.0.1 Release 4.03 Sp1 3.40.09 Software 09 08 2007 SigmaX 6.0.1 Release 4.04 3.41.14 Software 27.02.2008 SigmaX 6.0.1 Release 4.04 SP1 3.41.15 Software 09.05.2008 SigmaX 6.0.1 Release 4.04 SP2 3.41.16 Software 15 09 2008 SigmaX 6.0.1 Release 4.04 SP3 3.41.18 Software 08 01 2009 SigmaX 6.0.1 Release 4.04 SP4 3.41.19 Software 08 01 2009 SigmaX 6.0.1 Release 4.05 3.42.34 Software 06 11 2009 SigmaX 6.0.1 Release 4.05 SP1 3.42.43 Software 22 03 2010 SigmaX 6.0.2 Release 4.05 SP2 3.42.48 Software 26.08.2010 SigmaX 6.0.2 Release 4.05 SEB 3.43.18 Software 08 12 2010 SigmaX 6.0.2 Release 4.06 3.44.14 Software 01 12 2011 SigmaX 6.0.2 Release 4.06 SP1 3.44.16 Software 01 12 2011 SigmaX 6.0.2 Release 4.06 SP1 3.44.18 Hotfix 01 02 2012 SigmaX 6.0.2 Release 4.07 3 45 48 Software 20 08 2012 SigmaX 7.0.6 Release 4.07 SP1 3 45 51 Service Pack 09 12 2012 SigmaX 7.0.6 Release 4.07 SP2 3 45 58 Service Pack 20 12 2013 SigmaX 7.0.6 Release 4.08 3.46.57 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.62 Hotfix 21.05.2014 SigmaX 7.0.7 Release 4.08 3.46.70 Hotfix 23 07 2014 SigmaX 7.0.7 Release 4.08 3.46.72 Hotfix 04 08 2014 SigmaX 7.0.7 Release 4.08 3.46.73 Hotfix 12 08 2014 SigmaX 7.0.7 Release 4.08 3.46.79 Hotfix 08 10 2014 SigmaX 7.0.7 Release 4.08 (**1) 3.46.80 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.81 Hotfix 17 02 2015 SigmaX 7.0.7 Release 4.08 3.46.85 Hotfix 19 03 2015 SigmaX 7.0.7 Release 4.08 3.46.86 Hotfix 19 03 2015 SigmaX 7.0.7 Release 4.08 (**2) 3.46.89 Software 10 04 2014 SigmaX 7.0.7 Release 4.08 3.46.98 Hotfix 14 12 2016 SigmaX 7.0.7 Release 4.08 (**3) 3.46.104 Software 28 02 2017 SigmaX 7.0.9 Release 4.08 3.46.105 Hotfix 10 03 2017 SigmaX 7.0.9 Release 4.08 (**4) 3.46.106 Software 28 03 2017 SigmaX 7.0.9 Release 4.08 3.46.107 Hotfix 08 08 2017 SigmaX 7.0.9 Release 4.08 3.46.108 Hotfix 01 05 2018 SigmaX 7.0.9 Release 4.08 (**5) 3.46.110 Software 13 05 2019 SigmaX 7.0.9 Release 4.08 (**6) 3.46.111 Hotfix 15 11 2019 SigmaX 7.0.9 Release 4.08 (**7) 3.46.131 Software 29 01 2020 SigmaX 7.0.9 Notes:   **1 Sigma build 4.46.57 with StruxureWare Building Operation v1.5 or 1.6 transition support program installed. **2 Sigma build 4.46.57 with StruxureWare Building Operation v1.8 transition support program installed. **3 Sigma build 4.46.57 with StruxureWare Building Operation v1.9 transition support program installed. **4 Sigma build 3.46.57 with StruxureWare Building Operation v2.01 transition support program installed. **5 Sigma build 3.46.57 with StruxureWare Building Operation v3.0.1, v3.0.2 and v3.0.3 transition support program installed.. **6 Sigma build 3.46.57 with StruxureWare Building Operation v3.0.4, v3.1 and v3.2 transition support program installed. **7 Sigma build 3.46.57 with StruxureWare Building Operation v3.2 or later transition support program installed.   Notes: 1. SigmaX version 7.0.9 is now available and can be used on any Sigma version that supported SigmaX version 7.0.6. 2. This information can be downloaded as a PDF file: Sigma Build Numbers 2023 3. When SigmaX 6.0.2 is installed, the build information provided by Sigma (Help > About) can be wrong (later than the actual version). This arises because SigmaX installs a file with Build 3.42.47 in the c:\sigma\bin folder. This is only a problem prior to Sigma Release 4.05 SEB. ⚠️ Important Notice Sigma is not supported in EBO 2022 and later. To continue supporting Sigma devices, you can implement a multi-version system: Keep Enterprise Servers with Sigma devices on Building Operation 3.2. Add a Building Operation 2022 or later Enterprise Central Upgrade the rest of the system to Building Operation 2022 or later. You will not be able to upgrade EcoStruxure Building Operation servers that contain unsupported protocols, objects, or devices. Attempting to do so will result in failed upgrades or loss of functionality.
View full article
Picard Product_Support
‎2021-01-07 05:36 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-04 04:39 PM

Labels:
  • Satchwell BAS & Sigma
6604 Views

Building Operation Report Server SQL Database Full

Issue SQL Database is full, or the partition the SQL is installed is full Product Line EcoStruxure Building Operation Environment Building Operation Report Server Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Cause If a site is using SQL Express 2008, the limit is 10 GB. If using the full version(s), it is unlimited. If the database or the partition where the Reports Server resides is full, here are some steps to reduce the SQL table volume and offer a short-term solution. Resolution Before continuing, make sure there is a good backup of the database. Using SQL Server Management Studio, highlight the StruxureWareReportsDB and select New Query Use the following Script in that Query: SELECT t.NAME AS TableName, s.Name AS SchemaName, p.rows AS RowCounts, SUM(a.total_pages) * 8 AS TotalSpaceKB, SUM(a.used_pages) * 8 AS UsedSpaceKB, (SUM(a.total_pages) - SUM(a.used_pages)) * 8 AS UnusedSpaceKB FROM sys.tables t INNER JOIN sys.indexes i ON t.OBJECT_ID = i.object_id INNER JOIN sys.partitions p ON i.object_id = p.OBJECT_ID AND i.index_id = p.index_id INNER JOIN sys.allocation_units a ON p.partition_id = a.container_id LEFT OUTER JOIN sys.schemas s ON t.schema_id = s.schema_id WHERE t.NAME NOT LIKE 'dt%' AND t.is_ms_shipped = 0 AND i.OBJECT_ID > 255 GROUP BY t.Name, s.Name, p.Rows ORDER BY t.Name Select Execute to run that Query as shown in the screen capture below: The Results show each of the tables and the size of those tables as shown in the screen capture below: Purely for example purposes, a script to reduce the number of Events would be delete from tbEvents where DATEDIFF(day, datetimestamp, getdate()) > 180 To gain back the space after deleting rows, right-click on StruxureWareReportsdb > Tasks > Shrink > Database
View full article
Picard Product_Support
‎2018-09-11 02:54 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:36 AM

Labels:
  • EcoStruxure Building Operation
6584 Views

Locked Setpoint adjustment from SE8000 Room Controller

Issue Once the occupied cooling and heating setpoints are written from a BMS, the user is not able to change the setpoint from the room controller Product Line EcoStruxure Building Expert, EcoStruxure Building Operation Environment Automation Server Enterprise Server SE8000 Series Room controller Viconics branding VT8000 Series Multi Purpose Manager (MPM) BACnet Cause By default, the occupied setpoint value is written to Room Controller with priority level 16 by the BACnet front end. Attempting to change the setpoint locally using the up and down arrows on the SE8000 Room controller will not be allowed since the Room controller uses the relinquish value internally (priority 17) which will be automatically overwritten by the BACnet front-end. Resolution The work around is to release the BACnet front-end control over the BACnet object using a LUA4RC script. The script can be uploaded using one of the following two methods: 1 - Uploader Tool A USB cable is required to upload the script. The uploader tool can be downloaded from the Exchange Download Script Download Uploader Tool   2 - BACnet The script can also be directly uploaded via BACnet using the "Description" field as shown in the image below if (ME.AV92 == 6 or ME.AV92 == 7) then ME.AV39_PV[16] =nil ME.AV39_PV[10] =nil ME.AV40_PV[16] =nil ME.AV40_PV[10] = nil ME.AV92_PV[17] =0 end Where, ME.AV92 is the Keyboard value ME.AV39 is the Occupied Heating Setpoint ME.AV40 is the Occupied Cooling Setpoint Using this method, the script can be uploaded to multiple SE8000 Room Controllers by following the steps in Bulk Lua4RC upload via BACnet (Mass upload) For more information about Lua4RC, refer to the Lua4RC Programming Guide
View full article
Picard Product_Support
‎2018-09-10 02:08 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:51 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
6561 Views

Examples for the new native EBO Notification Reports

Issue Are there any Example Reports for the new native Notification Reports which came out in EBO 3.2 to replace the now deprecated WebReports and Report Server? Product Line EcoStruxure Building Operation Environment Building Operation Workstation Cause As of EBO 2022 (4.0) WebReports and the Report Server have now been deprecated and replaced by External Log Storage using Postgres SQL and Timescale DB, plus the new native Notification Reports which are now built into EBO 3.2 and above, but there are no examples to help new starters to get going. Resolution A Schneider-Electric Community page has been set up specifically for Notification Report users so that they can share their Reports and collaborate on Reporting ideas: https://community.se.com/t5/EcoStruxure-Building-Operation/Reports-showcase-share-your-reports/m-p/388619#M75732
View full article
Admiral David_Kendrick Admiral
‎2022-05-17 02:00 AM

Last Updated: Janeway Omaelk ‎2022-10-19 12:51 AM

Labels:
  • EcoStruxure Building Operation
6557 Views

TAC 5 Vista License Types

Issue Knowing the types of licenses, differences between each one, and the revisions supported by the license. Product Line TAC Vista Environment Vista 5.X Cause There are three different types of licensing for a Vista system. Resolution There are three types of TAC Vista software licenses. TAC Vista Demo License This type of license is for temporary use. It expires every thirty days. It is the full version license excluding OPC server licenses. The demo license is available on Schneider Electric buildings business extranet. (Products >TAC Vista > Vista Software > Evaluation License File). No activation required, ready to use after downloading. (Store the license file into C:\Program Files\Schneider Electric\License Files, by default.) Monthly demo licenses only work locally for the PC where they are installed.  You cannot use a License Server to serve up remote Workstation licenses to a remote PC, for example. For remote Workstation usage, please use the TS version of demo license instead. Demo licenses contain unlimited TAC Vista Webstation seats which allow multiple people log into Webstation simultaneously on the server PC and other computers.   TAC Vista Engineering Dongle This type of license is for Schneider Electric engineers or partners use. It comes with the full version license besides the OPC server licenses.  Please read Part number for Vista 5 engineering dongle for more purchasing information. No activation required, ready to use after receiving. Simply put the engineering dongle into one of the USB ports. You may be asked to install some software upon first time use. Note:  Insert the engineering dongle prior to starting the TAC Vista server. Engineering dongles only work locally for the PC where they are plugged in.  You cannot use a License Server to serve up remote Workstation licenses to a remote PC, for example. Engineering dongles contain only one (1) TAC Vista Webstation seat. In addition, user can log into Webstation only on the sever PC.   TAC Vista Customer License This type of license is for end user use. Depending on the customer needs, different features of Vista software can be purchased standalone or in packages. For more information about each software feature or packages, please read the Vista 5 Software license packages and Vista 5 product catalog. Customer licenses are restricted to the minor revision of the Vista software or lower. A Vista 5.0 license will not function on a Vista 5.1 installation. However a Vista 5.1 license will work for all 5.1.x installations as well as all 5.0.x installations. Maintenance agreements ( XXXX 1 year licenses) are available for most TAC Vista 5.1 software modules. An active maintenance agreement ensures that the license has access to any new, minor and major, versions. Maintenance agreements are automatically renewed at the end of each 12 month period. The termination notice is three months. Minimum agreement time is three years. Activation of the license is required. You can generate the license on the https://schneider-electric.flexnetoperations.com website with the entitlement ID received via email after purchasing. The license needs to be locked to: Computer MAC address If you lock the license to a computer's MAC address, the license needs to be stored on this particular computer (C:\Program Files\Schneider Electric\License Files, by default), and it can only be used on this computer.   An onsite dongle (end-user dongle) The dongle needs to be purchased separately (name: Vista 5 Hardware Dongle, part number: 000857510 on the iPortal).  If you lock the license to the onsite dongle, you can use TAC Vista software on any computer as long as this dongle is plugged in. You can re-host the license to another MAC address or onsite dongle up to 4 times in a 1 year period. If you exceed this re-hosting limit you will need to contact Product Support with a valid reason why this occurred, and the limit can be reset. For additional customer licensing information please read TAC Licenses Installation Manual and TAC Vista 5.0 to 5.1.7 license does not work after installation for how to use LMTOOLS to manually read site license.
View full article
Picard Product_Support
‎2018-09-07 03:45 AM

Last Updated: Crewman ContentModerator ‎2025-09-25 03:05 AM

Labels:
  • TAC Vista
6545 Views

WebReports/Report Server discontinuation in EBO 2022 or higher (Migration to External Log Storage)

Issue Sites using Report Server need to upgrade to EcoStruxure Building Operation (EBO) 2022 or higher, where WebReports/Report Server is no longer supported. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Report Server Building Operation Timescale Database Cause WebReports/Report Server is not supported in EBO 2022 (version 4.0) or higher. Resolution To address this, Schneider Electric provides a Data Migration Assistant (DMA) tool that: Reads data from WebReports 3.x Writes data to External Log Storage Download the DMA Tool External Log Storage Overview Stores historical data from EcoStruxure BMS Storage capacity is limited only by your hardware Historical data is displayed in WorkStation and WebStation (event and trend views) Any server can be configured to write data to TimescaleDB   Any server in the system can be configured to write historical data to the TimescaleDB database. Licensing Requirements External Log Storage requires a license Refer to: Software and Features that Require Licenses Part Number Summary and Hardware Software Matrix Hardware & Software Requirements Ensure compatibility with: TimescaleDB PostgreSQL Recommended specs for large systems (e.g., 100 BMS servers): High-performance SSD Minimum 64 GB RAM Additional CPU capacity Refer to: IT System Planning Guide Merging Log Data External Log Storage reduces extended trend logs on BMS servers You can merge extended trend logs into source logs in External Log Storage See: Merging of Trend Log Data Enhanced Reporting (XLSX Templates) EBO servers (v3.2 or higher) support native reporting with: Text and XLSX formats Advanced XLSX features: formulas, conditional formatting, charts, sparklines Historical data pulled from External Log Storage (PostgreSQL/TimescaleDB) Refer to: Examples for Native EBO Notification Reports
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-06-22 01:54 AM

Last Updated: Administrator CraigEl Administrator ‎2025-08-15 06:38 PM

Labels:
  • EcoStruxure Building Operation
6546 Views
  • « Previous
    • 1
    • …
    • 16
    • 17
    • 18
    • …
    • 500
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore