Issue
Documentation supplied with new UNC, ENC, or Jace 8000 was discarded. Is there a way to determine the default, the factory-defined IP address, for the Ethernet port on the controller?
Product Line
TAC IA Series
Environment
- I/A Series (Niagara) R2 UNC
- I/A Series (Niagara) G3 ENC
- Niagara N4 or G3 Jace 8000
Cause
Lost or discarded document, shipped with the controller, that contained the configured IP address.
Resolution
- The default Ethernet IP address for an I/A Series (Niagara) UNC or ENC is based on the serial number and type of device. For a UNC or ENC, the default address is 192.168.1.14X where X is the last digit of the device serial number. The default serial number is found on a sticker on the controller circuit board. This sticker has the full model number, date code, and the serial number of the controller. The serial number is preceded with S/N:.The subnet mask is 255.255.255.0 in all UNCs, ENCs, and Jace 8000
- The default address base address (192.168.1.140) is the same for all UNC-410, UNC-510, UNC-520, ENC-410, and ENC-520 controllers.
- The default IP address of a Jace 8000 for PRI (LAN1) is 192.168.1.140. SEC (LAN2) is by default disabled.