Managing Licensing distribution using the Option's file

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Managing Licensing distribution using the Option's file
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
6613 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Managing Licensing distribution using the Option's file

Picard Product_Support
‎2018-09-11 04:39 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:51 AM

Issue

How can we exclude Hosts or Users from accessing the Workstation Professional license i.e. Script, Function Block and Graphic editors from another Workstation?

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation License Server
  • FLEXnet

Cause

When accessing various editors from within Workstation a particular license does not differentiate host or user who should have access to which editors. Using the option file taclic.opt allows you to exclude certain Host / Users of StruxureWare Building Operation from accessing these Workstation clients.

The Workstation clients referenced are as follows:

  • client.station (Workstation)
  • client.script (Script Editor)
  • client.functionblock.view (Function Block Editor)
  • client.graphiceditor (Graphic Editor)

Resolution

FLEXnet Licensing provides the options file to be included in the License Server directory. Each time the License Server service is started this file is checked. Syntax and use can be found in the attached document - Chapter 13

The following option file must reside on the License Server in the following path:

Building Operation 1.9 and below:

  • C:\Program Files(x86)\Schneider Electric StruxureWare\Building Operation 1.x\License Server

Building Operation 2.0 and above:

  • C:\Program Files(x86)\Schneider Electric EcoStruxure\Building Operation x.x\License Server

Once this file is copied into the License Server folder, you must restart the license service (via the Windows Control Panel, Administrative Tools, Services).


Examples:

# The following text excludes the features from Workstation Professional
#
# Use the following 3 Exclude statements if you wish to exclude an entire Workstation from accessing editors
#
EXCLUDE client.script HOST enter_host_name
EXCLUDE client.functionblock.view HOST enter_host_name
EXCLUDE client.graphiceditor HOST enter_host_name
#
# Use the following 3 Exclude statements if you wish to exclude a Building Operation User from accessing editors
# (remove #'s below as required)
#
# EXCLUDE client.script USER enter_user_name
# EXCLUDE client.functionblock.view USER enter_user_name
# EXCLUDE client.graphiceditor USER enter_user_name
#

Notes:

The HOST can be defined by either DNS or IP Address

The USER is the user name as defined in Building Operation, this may be the same as the Windows username if using Windows Domain.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Attachments
taclic.zip
Tags (2)
  • Find more articles tagged with:
  • 14002
  • RobertAndriolo19
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore