Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,845
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 104
    • 105
    • 106
    • …
    • 508
  • Next »

"No license for LonWorks communication" in Vista Workstation

Issue Alarm queue in the Vista Workstation states "No license for LonWorks communication" Product Line TAC Vista Environment Vista Workstation Cause The simplest cause of the issue, and the one that should probably be checked first, is that the license for LonWorks communication was not present at the time the server was started.  Oftentimes, this is due to starting server, realizing the engineering or end user dongle was not plugged in (or license server was not started) and then plugging it in.  The server will not actively poll for this license, it must be present at startup. Resolution Stop the Vista Server Ensure the license dongle is plugged in, or the license file is activated and installed on the license server. Restart the Vista Server Related Articles: "No license for LonWorks communication" with TAC Vista Server LE "No license for LonWorks communication" error when using a non LE dongle "No license for LonWorks communication" - LonMaker Recovery Folder "No license for LonWorks communication" error message in Classic Network "No license for LonWorks communication" Error in Windows 2008 Server X64 TACOS startup delay utility
View full article
Picard Product_Support
‎2018-09-07 02:22 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:06 PM

Labels:
  • TAC Vista
2098 Views

Controllers used to get values from a Modbus device into TAC Vista

Issue What kind of controller can be used to get values from a Modbus device into TAC Vista? For example, getting data from a Modbus meter into a BMS system running Vista. Product Line TAC Vista Environment TAC Vista TAC Xbuilder TAC Xenta server 731/913 Cause TAC Vista can not talk Modbus directly so you need to use a gateway controller. Resolution Xenta firmware version 5.1.4 and earlier only two controllers had Modbus communication capabilities: Xenta Server 731  For details see TAC Xenta 711/731 Web Server and Controller Xenta Server 913 For details see TAC Xenta 913 LonWorks Gateway Starting with Xenta firmware version 5.1.5, all Xenta Servers are now capable of communicating on a Modbus network both via TCP/IP and RS-485.  This includes Xenta 511, 527, 701, 711, 721, 731, 913. Note: Older Xenta Server devices built before firmware 5.1.5 have the capability of using Modbus over RS-485 once they have been upgraded even though the terminals are not labeled on the device. For information on how to wire these devices to reference a newer Xenta Server that does have the RS-485 A terminals labeled or see Xenta Server wiring and pinouts.
View full article
Picard Product_Support
‎2018-09-07 04:05 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:05 PM

Labels:
  • TAC Vista
2339 Views

Typical data throughput rates for Modbus XDrivers

Issue When polling data from the Modbus IP and RTU X Drivers, how fast can data be retrieved? Product Line Andover Continuum Environment Modbus RTU, Modbus IP X-Drivers bCX1, Netcontroller II, ACX57xx Cause Polling data too fast particularly with the Modbus RTU XDriver can cause the controller Scan time to rapidly rise to excessive levels. Resolution The Modbus RTU X Driver can typically make 2 polls per second. These polls can be for single values or block reads. As this X Driver operates outside the regular controller scanning process, polling too many points or many points that are offline can cause the scan time to rapidly rise. Use a single Plain English program to schedule the polling of all points. See Helpful Modbus register Information for advice on how to handle offline devices. If 2 off Modbus RTU X Drivers are used on the same controller, then again use a single Plain English program to poll across both ports and do not exceed the recommended overall rate of 2 polls per second.  For the Modbus IP X Driver, only one port can be used to load this driver on any controller. It can typically make 8 polls per second for single or block reads. Also see What should be considered when analyzing the performance of a Modbus TCP/IP implementation?on analyzing the performance of the Modbus IP X Driver.  NOTE:  The ability to enable 2 comm ports using Xdrivers can be done, but is not recommended by the Xdriver developers nor supported by PSS. The RTU Xdriver is poll on demand. This type of driver can request a lot of data and starve the CPU on the controller which then makes the polling irregular. If 2 ports are being used then there are typically more devices being added and therefore more points increasing the requests and demand on the controller's CPU. Use one program to control the polling on both ports. Two programs attempting to control the polling asynchronously will cause communication issues.
View full article
Picard Product_Support
‎2018-09-10 10:20 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:04 PM

Labels:
  • Andover Continuum
2812 Views

Upgrade warning and Error Conversion Log Analysis

Issue Upgrade warning and Error Conversion Log Analysis Additionally upgrading an AS from version 1.3 to 1.4 can create a number of unresolved or invalid references. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server, ASP, ASB Building Operation Enterprise Server Building Operation Device Administrator Conversion Log Cause When upgrading using the Device Administrator various warning and errors can be seen. Errors will prevent the upgrade, but warning will still allow the upgrade to continue. Starting in version 1.4, new rules have been put in place that will invalidate some bindings that had previously been made in older versions. These rules may cause errors to be produced in the Conversion Log found in the Device Administrator. The three new rules are: Public Numeric/Signal bindings will be dropped. Multiple bindings will be restricted to one. Binding to Local Node NVIs will be dropped. For more information regarding the rule changes made in version 1.4 see Reference Guide and References beginning with 1.4.x. Resolution Instructions on how to perform the Automation Server upgrade and how to obtain the Conversion Log, see Upgrading Automation Servers from 1.3 to 1.4. Breakdown of the Conversion Log The file paths given in the Conversion Log entries will direct you to the location of the unresolved or invalid reference. Depending on the type of entry it is, it may require further action to correct the problem.   Type of entries found in the Conversion Log WARNING: ERROR: Invalid_Property_Reference (destination) (source) Explanation: Either rule 1 or 3 has been broken. If a public numeric/signal is bound programmatically to another object then it violates rule number 1. The public numeric/signal in the program must be changed to an input or output before upgrading the database. If the destination of the binding is an NVI in the Local Node then it violates rule number 3. A change to the configuration of the local node must be implemented before performing the upgrade. In many cases the substitution of an NVO for the NVI will address this issue. Explanation: This binding should not have been allowed in SmartStruxure version 1.3. In the StruxureWare Building Operation Technical Reference Guide, you will find on page 2107 that BACnet priority 6 is reserved for future use. This binding needs to be made to a different priority. WARNING: ERROR: Object_Does_Not_Exist (object). Explanation: The object that the reference is trying to bind to does not exist. In other cases the binding was already broken in the source database so it will remain broken in the target database. The binding fix can be addressed before or after the upgrade. WARNING: Property (property) bound to (property), so binding to (property) is dropped. Multiple bindings are not allowed in SmartStruxure version 1.4 and above. Explanation: The object is being written to by multiple objects and/or programs. This violates rule number 2 and is no longer accepted. After the upgrade, only one of the bindings will be left connected and all others will be dropped. This will require changes to be made to the configuration to maintain the same operation. Note: In some cases this warning can occur due to a default value of a configuration object that is mistakenly interpreted as a duplicate binding. The binding is in fact preserved by the upgrade and no further action is required. WARNING: Discarding incomplete binding for (object) -unknown source. Explanation: Due to a version 1.3 defect, the source version configuration database contains an incomplete binding error. This is not a problem but it may be a sign that someone intended for the property to be bound to something but failed to do so. Therefore, the configuration should be examined after the upgrade has been completed to insure that everything is okay. No information has been lost in the upgrade but check the configuration to rule out any errors in the source version database. WARNING: Property (property) in (object) is Unit configured but is not configurable in the new. Explanation: This property has a selected unit configured in the source version database, while in the target version configuring the unit of this property is no longer possible/meaningful. These errors should be investigated to insure that there has been no negative impact on the operation. Generally this error will not be a problem and will require no further action. WARNING: Property REF in (object) is not defined in the new system, skip REF. Explanation: The REF property prior to version 1.4 held a back-reference to an object or property that was referring to the property at hand. Starting in version 1.4 and on, the back-references are handled by other means and are no longer represented in the configuration database. This information can not be upgraded but this is not a problem and no further action is required. WARNING: Invalid value for (property) in the object, (object). The default value has been applied. Explanation: The value seen in the source version is invalid or can not be found; therefore the upgrade process sets it back to the default value. No further actions needs to be taken. WARNING: The declared instance (instance) is obsolete but contains non-default data which has been discarded. Explanation: If the instance is a SavedUserTokens or System/Remote Server warning then the warning can be ignored. No further action is required. WARNING: Property (property) in (source) is not an acceptable property type and is not configured. Explanation: This has to do with the lead reference for shadow Alarm Control Panels that cannot be properly upgraded due to changes to the type of system in version 1.4. There is logic in place that automatically sets the lead reference to the ES again. This is a warning that can be ignored. Explanation: There have been changes made to the type of system. This change prevents the hidden SynchSource property of the Time Zone setting in the source version of the database from being upgraded automatically. If the lead reference was set for Time Zone in the source database, this may have been erased and will have to be done again after the upgrade. This should be followed up manually. Explanation: The new referencing scheme expects all references to be relative so if there is a full binding path it is perceived as an error. This is not an issue and requires no action. Explanation: MatchedDevice is a hidden property that can not be seen. This warning refers to old items that have not been cleaned out. This warning can be ignored. Note: Also keep in mind that the upgrade process considers any empty link "not an acceptable Property". This error can be ignored, no changes need to be made. INFORMATION: Property "Value" in (location) is Unit configured but is not configurable, default unit is used. Explanation: This property has a configured unit that is no longer allowed to be configured in the target database, a fixed default value is used. This is unlikely to cause a problem, no further action needs to be taken.  
View full article
Picard Product_Support
‎2018-09-11 07:03 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:04 PM

Labels:
  • EcoStruxure Building Operation
2141 Views

Ordering more Echelon LonMaker credits

Issue How to order more LonMaker credits in order to commission more devices. Product Line TAC IA Series, TAC Vista Environment LonMaker LNS Cause There are two types of credits: Product specific credits like LonMaker and NL credits LNS credits   LNS LNS credits are assigned to the PC and when they reach zero, the LNS Server license goes into deficit mode. After 14 days the deficit mode will expire, at which time no LNS tools will be able to be used on that PC. To reverse the lockout, enough LNS credits must be ordered to cover the deficit and any additional nodes that need to be commissioned. Backing up, sharing, and restoring LNS databases can sometimes corrupt these LNS credits, which then prohibits you from launching any LNS plug-ins. For more help with corrupt LNS credits see Corrupted LNS Credits. LonMaker LonMaker credits are assigned to the PC. Both LNS and LonMaker credits are required, however when commissioning devices in LonMaker, LonMaker credits are consumed but LNS credits are not. Even though LNS credits are not consumed in LonMaker they are still necessary because certain LNS applications (i.e. TAC Vista System Plug-in) require them to operate. NL220 Each time a node is commissioned in NL220 it requires a NL credit and a LNS credit. NL credits are assigned to the NL220 dongle and can be used on other PCs in "MOVED" mode. LNS credits are also necessary in NL220 to operate certain LNS applications such as the TAC Vista System Plug-in.   To order more Echelon LNS credits see Ordering more LNS credits. To order more Newron NL220 credits see Ordering more Newron NL220 credits. Resolution To order more LonMaker credits: Echelon LonMaker v3.1 Open up a LonMaker database and go to LonMaker menu > LonMaker Credits Info... Here you can view how many LonMaker available credits that you have. Click on Add Credits... In the box named Credit Order, type in how many credits to order, then click Next. Following the instructions at the top of the window, click the Copy to Clipboard button to copy the PC key generated by LonMaker License Wizard. Click Cancel. Compose a new email and paste the PC key into the body of the email. Address the email to credits@echelon.com or your local Schneider Electric Buildings Business order department so they can place the order. Follow the instructions at the top of the email making sure to fill out all required fields. Once Echelon or the local Schneider Electric Buildings Business order department sends back an Application Key, open up the LonMaker License Wizard again. Click Next and paste the application key into the field titled "Application Key". Click Finish. Echelon LonMaker v3.2 Turbo Open up the LonMaker License Wizard by going to Start > All Programs > Echelon LonMaker > LonMaker License Wizard. Here you can view how many LonMaker credits that you have available. In the box named Credit Order, type in how many credits to order, then click Next. Following the instructions at the top of the window, click the Copy to Clipboard button to copy the PC key generated by LonMaker License Wizard. Click Cancel. Compose a new email and paste the PC key into the body of the email. Address the email to credits@echelon.com or your Schneider Electric Buildings Business Order Entry Department (888-444-1311) so they can place the order. Follow the instructions at the top of the email making sure to fill out all required fields. Once Echelon or the local Schneider Electric Buildings Business order department sends back an Application Key, open up the LonMaker License Wizard again. Click Next and paste the application key into the field titled "Application Key". Click Finish.
View full article
Picard Product_Support
‎2018-09-10 11:08 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:02 PM

Labels:
  • TAC IA Series
  • TAC Vista
2970 Views

How to replace a Xenta controller in a LNS network

Issue In the event of a hardware failure on a Xenta controller you may need to perform a proper replacement procedure in the TAC Plug-In to install the new device. Product Line TAC Vista Environment Vista Xenta Programmable Controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause Hardware failure in an LNS network Resolution In the event you have a piece of hardware fail on your LNS network you will want to follow the steps below to properly replace the device. Remove the bad controller and Install the new controller in its place Open your LNS network in LonMaker or NL220 Select to open the TAC System Plug-In in your network management tool In the Plug-In, locate the bad controller in the tree under the LNS Network pane and right click Select Replace... (the Replace TAC Xenta Device Wizard will open) Click Next Select the service pin button and press the service pin on the new controller Then click Next In the next window, click Next to update your Vista Database (NOTE: If you receive a warning during this process, see Warning about application file replacing a programmable controller in Vista System Plug-In) Once this process of updating your Vista Database is complete you will see the screen below confirming that the update was completed successfully Close the TAC Vista Load window Return to the Replace TAC Device Wizard and click Finish. This will complete the replacement process for your new device In some rare cases not all I/O modules will come online after this procedure. If this occurs a power cycle of the Xenta 400/300 will solve this issue.
View full article
Picard Product_Support
‎2018-09-10 05:36 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:01 PM

Labels:
  • TAC Vista
2468 Views

Bacnet and StruxureWare Building Operation Central IO points

Issue Depicting the differences between Bacnet points and Central IO points. Product Line EcoStruxure Building Operation Environment SmartStruxure 1.3 and lower Cause Explanation of difference in points Resolution Creating Central IO points When you create inputs and outputs in a non-BACnet SmartStruxure system, you simply create the inputs and outputs and then provide programming to control the Requested value. Trends, alarms and graphics would monitor the value property. In a BACnet SmartStruxure system, the inputs and outputs are created under the IO Module in the same way; however an additional point is created in the Application folder under the BACnet Interface Device. On the property page of that point is a field designating the “Associated Value”. You should browse to the appropriate CIO point and select it. At this point all monitoring, display and control of the object should be accomplished with the BACnet point. (It is also possible to make the link between the associated value and the IO value by using the binding tool.) There is no other binding necessary to make the link between the CIO point and the BACnet “proxy” that is created in the application folder. For SmartStruxure versions prior to 1.4 please see the attached document for some implications and proper method of operation for using the IO associated value property: PSS Building Operation Attachment 14040rev2.pdf For SmartStruxure 1.4 and above see Associate AS BACnet Interface IO points with points on the IO bus in SmartStruxure 1.4 and above.
View full article
Picard Product_Support
‎2018-09-11 05:53 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:00 PM

Labels:
  • EcoStruxure Building Operation
2735 Views

TAC ToolPack plug-ins are not showing up

Issue TAC ToolPack plug-ins (eg. STR 350 plug-in) do not show up Product Line TAC Vista Environment TAC Vista 5.1.4, 5.1.5, 5.1.6 Windows 7, Windows Server 2008, Visio 2010 TAC System Plug-in TAC Device Plug-in TAC Zbuilder TAC Xenta 100 Plug-in TAC Xenta 102-AX Plug-in STR 350 Plug-in Cause Not all plug-ins in the TAC ToolPack can run on Windows 7, Windows 2008 or Visio 2010. Resolution When installing TAC ToolPack on these operating systems only the supported plug-ins will be installed: TAC System Plug-in TAC Device Plug-in TAC Zbuilder TAC Xenta 100 Plug-in TAC Xenta 102-AX Plug-in If the desired plug-in is missing, configuration of your controller will need to be done manually in NL220, Lonmaker, or Vista. Read details about manually setup STR 350/351 in STR 350/351 manually setup without plug-in (nciOption1 and nciOption2).
View full article
Picard Product_Support
‎2018-09-07 04:09 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:00 PM

Labels:
  • TAC Vista
2185 Views

Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal

Issue Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal Product Line TAC IA Series Environment I/A Series R2 Universal Network Controllers: UNC-410-1 UNC-410-1-N UNC-520-2 UNC-520-2-N Cause There maybe a need to access the UNC via its serial port if the IP address of the UNC is unknown or for troubleshooting purposes when the UNC's Ethernet port is not functioning. Resolution Hardware required for connection to UNC's RS-232 port: 8-conductor flat silver satin stranded cable with standard male (plug) RJ-45 connectors RJ-45 to DB-9 adapter (part number: UNCC-405) or a socket-to-plug type RJ-45 to DB-25 adapter (part number: UNCC-430) A functioning COM port on a computer A 2-pin jumper for connection to the UNC's "Mode" connector Refer to the Installations Instructions for UNC-520 (page 15) for details on the cable and adapter (applies for both UNC-410 and UNC-520). Pinout configuration for a RJ-45 to DB-9 Null Modem Adapter (part number UNCC-405) also refers to these pin outs. Connection to UNC's VxWorks Target Shell using Windows HyperTerminal (for operating systems without HyperTerminal, please refer to Hyperterminal on Microsoft Windows Operating Systems😞 Connect the cable and adapter between the UNC's RS-232 port and the RS-232 COM port used on the computer. Start HyperTerminal (Programs > Accessories > Communications > HyperTerminal). In the 'Connection Description' dialog, type a name for this session. For example, 'Connection to UNC'. Click OK. In the 'Connect to' dialog, use the 'Connect using' drop-down list to select the COM port used on the computer. Click OK. In the Com(n) Properties dialog, choose the following settings: Bits per second: 9600 Data bits: 8 Parity: None Stop bits: 1 Flow control: Hardware Click OK. On the UNC circuit board, locate the 4-pin Mode connector and put a 2-pin jumper on the 2 outer pins. Refer to page 17 UNC-520 Installation Instructions for position of the Mode connector (top right corner). With the HyperTerminal session active, remove power from the UNC, let it cycle down, then reapply power. After some number of seconds, text should appear in the HyperTerminal window similar to: Press any key to stop auto-boot... To enter commands to the UNC, press any key to break out of the boot sequence. A prompt similar to the following is shown: [VxWorks Boot]: To determine the IP address / subnet mask of the UNC, do not break the auto-boot sequence as described in step 7. Allow the UNC to finish booting. When the controller stops displaying new messages, press ENTER to reach the command prompt. The prompt is similar to the following: -> Using the scroll bars on the HyperTerminal window, scroll up until the section that begins with the line 'Press any key to stop auto-boot...'. The IP address of the UNC is listed on the line that begins 'inet on ethernet (e)' The IP address is listed (in dotted decimal), followed by a colon, and then the subnet mask (in hexadecimal). Disconnect from the UNC when complete. Press the 'Disconnect' button on the HyperTerminal toolbar. Exit from the HyperTerminal application, selecting to Save if planning to reuse this HyperTerminal setup for future connection to an UNC. Remove the 2-pin jumper from the Mode connector of the UNC. Reboot the UNC by removing the power connector, waiting for all lights to extinguish, and plugging the power connector back in. * If troubleshooting the UNC, send the HyperTerminal start up messages to Product Support for analysis.
View full article
Picard Product_Support
‎2018-09-10 09:11 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:59 PM

Labels:
  • TAC IA Series
4934 Views

"The time on the workstation is less than the time of one or more controller log entries"

Issue Error displayed: "Extended logging time synchronization problem. The time on the workstation is less than the time of one or more controller log entries," when Workstation tries to download ExtendedLog data from controllers. Product Line Andover Continuum Environment Continuum Workstation (LAN & SU) NetController (CX99xx , BCX9640, BCX4xxx, ACX57xx) InfinetController (i2xxx & First Generation InfinetControllers) Cause Time setting is different between Workstation and Controllers or the time setting is same but the UTC Offset (Time Zone) is wrongfully set between the WS and the Continuum Network object of the controller. Resolution Set the correct UTC offset (time zone) in all of the below locations: Confirm Cyberstation(s) PC time zone (UTC offset) and Windows regional settings are correct. Confirm the SQL Server PC time zone (GMT settings) and Windows regional settings are correct. In Continuum, the Workstations Device objects Time tab has the correct time zone setting (be aware this is in minutes, ex. GMT+10 = +600 minutes). In Continuum, the Network folder has a setting for the time zone, this needs to be configured to the time zone the controllers are located. If GMT+10 then this gets set to +600. Note: See Configure Time Zone and UTC Offset settings so that time is synchronized across your system for more detail on the various locations for UTC settings and what these are required for. Setup Workstation and Controller Time Synchronization: Synchronize the time on all Workstations to a common source. See instructions in Cyberstation Installation Guide under "Workstation Time Synchronization." Synchronize controller time by creating a Program in one of your Cyberstations (only create on one Cyber). This synchronizes the controllers time to the Workstations time once every hour. There are detailed instructions on this in the Cyberstation Installation Guide (with a sample program) under "Controller Time Synchronization." (Also see Time sync controllers to workstations)
View full article
Picard Product_Support
‎2018-09-07 07:04 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:58 PM

Labels:
  • Andover Continuum
2459 Views

How the Enterprise Server determines the offline status of an AS

Issue Communication issues between the Enterprise Server and Automation Servers result in an offline status of the AS. More information is required on how this status is detected.  Product Line EcoStruxure Building Operation Environment Enterprise Server Automation Server Cause An AS behaves as if it is online yet shows up as offline in Workstation.  Resolution As of 1.5.0.10001 there is a new model for detecting online / offline servers. Prior to 1.5.0.10001 When a communication error was detected the Automation Server was marked as offline. As of 1.5.0.10001 and Newer An immediate DetectOnline call is scheduled. Only after three failed DetectOnline with an interval of one second we consider the  server to be offline. When offline an alarm is generated.and set the offline status as normal, and also go back to one minute interval for online detection. In 1.5.0.10001 the number of retries and interval is possible to set in server.properties. From 1.6.0 this is configurable from WorkStation. *** Server Communication folder is hidden in more recent versions of SBO See Also: How BACnet b3 controllers are established as being Online / Offline How the communication status of BACnet devices are verified
View full article
Picard Product_Support
‎2018-09-11 01:23 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:57 PM

Labels:
  • EcoStruxure Building Operation
3232 Views

How to configure the Windows Time Service to use an internal clock

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Time synchronisation is often an issue on large BMS installations. A central time signal is normally required to make sure all controllers, terminals or workstations have the correct time. If there is no internet connection available then the time has to be synchronised from a central source. Product Line Andover Continuum, EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC Vista Environment Sigma Continuum Vista SmartStruxure Windows XP Windows 7 Server 2003 Server 2008 R2 Cause No internet connection available to synchronise the system time. Resolution Important The methods below contain steps that tell you how to modify the registry. However, serious problems might occur if you modify the registry incorrectly. Therefore, make sure that you follow these steps carefully. For added protection, back up the registry before you modify it. Then, you can restore the registry if a problem occurs. If using Windows XP, please use the following link - http://support.microsoft.com/kb/314054 If using Server or Windows 7 OS, please use the following link - http://support.microsoft.com/kb/816042 This has been tested for Time updates to an AS by simply using the PC IP address as the primary NTP Time Server. If the firewall is turned on you also need to make sure UDP 123 is open. Please note that Windows will add a dispersion to the time that may cause issues with time synchronization, please see Automation Servers ignore time sync message sent from Windows NTP server that uses local internal clock for details.
View full article
Picard Product_Support
‎2018-09-11 01:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:56 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
2308 Views

Unable to login to AS directly when using Domain user

Issue Unable to login to AS directly when using Domain user. It is possible to login to AS directly with "Local" Domain and to the ES with same Domain. Receive error "Can not continue because server is offline or temporarily unavailable" even though ES is online. Product Line EcoStruxure Building Operation Environment Enterprise Server Automation Server Domain Cause AS is unable to communicate with the ES to properly authenticate the Domain user.  If the ES is picking up a WiFi IP address instead of the LAN IP address, this can be the cause. All other communications can still function correctly with the ES but the issue occurs when the AS tries to connect directly to query the Domain, it will be using the wrong IP address. Resolution Changed the order of NIC''s in Windows so that the Local Area Connection was first, confirmed the ES had the correct IP address, confirmed the AS saw the change, and was then able to login to the AS directly using the Domain user. See How to set the Enterprise Server IP address for details on how to ensure you are using the correct IP address.  Another thing to look out for is that you are using the correct port number for the ES communications as seen from the AS.
View full article
Picard Product_Support
‎2018-09-11 03:08 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:54 PM

Labels:
  • EcoStruxure Building Operation
2213 Views

Is it possible to run TAC Vista 5.X.X in Windows XP compatibility mode (When TAC Vista Installed on Windows Vista, Windows 7, Server 2003/2008)

Issue Is it possible to run TAC Vista 5.X.X in Windows XP compatibility mode (When TAC Vista Installed on Windows Vista, Windows 7, Server 2003/2008) Product Line TAC Vista Environment TAC Vista 5.X.X Windows XP Windows Vista Windows 7 Windows Server 2003/2008 Cause If TAC Vista 5.x.x is Installed on Windows 7, Windows Vista, or Windows Server 2003/2008, is it possible to run the Vista Workstation on Windows XP using Compatibility mode. Resolution TAC Vista has several other applications that work together with Vista. These applications do not support compatibility mode. Upgrade to Vista 5.1.4 or later which support Windows 7. If the operating system is a 64-bit version, upgrade to Vista 5.1.5 or later. For the compatibility matrix see Software and Firmware compatibility matrix for older versions of the traditional product lines.
View full article
Picard Product_Support
‎2018-09-06 01:27 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:53 PM

Labels:
  • TAC Vista
2314 Views

What card readers and technology can be used with Continuum Access Control Systems

Issue What card readers and technology can be used with Continuum Access Control Systems Product Line Andover Continuum Environment Continuum Cause Need to know what card readers will work with Continuum Access Control Systems Resolution The card reader and card technology is not relevant to the Continuum Controller, as this is used between the card (tag, fob or other) and the reader. This allows the use of the standard technologies available today, including fingerprint and other biometric based access as well as cards, fobs and tags. The signal that comes from the reader must be serial data input type Wiegand or ABA (or Clock & Data) USB, Ethernet, RS485, RS232 inputs are not accepted. NOTES The exact input type and maximum data bits can only be determined by checking the hardware, firmware and Continuum version combination being used. Retina, fingerprint, facial recognition and other biometric based systems that are connected to Continuum Access Controllers will store the biometric information and still be connected via the serial data Wiegand or ABA to the Continuum Controller. The current Continuum access controllers also accept an 8 bit burst for PIN numbers from keypads See Where can I find datasheets, install guides and other information on HID Electronic Access Control products? ABA (or Clock & Data) this was often used with Magnetic Swipe technology which has mostly been phased out Standard Wiegand Formats within Continuum Infinity 37-Bit AC 4+4 32-Bit Wiegand 26-Bit CK 34-Bit G 32-Bit HIDCorp1000 35-Bit - Some restrictions Custom
View full article
Picard Product_Support
‎2018-09-11 09:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:52 PM

Labels:
  • Andover Continuum
2353 Views

Sensor cleaning and maintenance requirements

Issue How and where should sensors be fitted and maintained? Product Line Field Devices Environment Temperature and humidity sensors Cause General advice is required for cleaning and maintaining temperature and humidity sensors. Resolution The most important thing about sensors is to fit them correctly and appropriately during installation as this will reduce the amount of maintenance required. Fit them in locations that are accessible as well as away from dust and dirt to reduce the amount of cleaning required. See Recommended locations for Temperature Sensors, Valves, and Actuators for further advice on sensor location. Check the specific installation instructions for the sensor used and verify they are fitted accordance with this. All sensors should be regularly checked for correct operation as part of a regular building maintenance plan and replaced if they are not operating correctly. Most sensors are sealed units and do not require maintenance, maybe just an occasional dust with a clean cloth to remove surface dust, these include duct and immersion temperature sensors, outdoor sensors and thermostats. Room temperature and humidity sensors usually have vents or gauzes to allow airflow over the elements; these should be regularly dusted and can be cleaned with careful use of a vacuum cleaner or air blower to remove dust or other particles from within the unit. Do not however use equipment that can produce excessive pressures like compressed airlines as this could result in damage to the sensor. If you do need to use cleaning products on the sensors, then first check the materials used on that specific sensor (see datasheet, most sensors use Polycarbonate or ABS plastics) then verify that the cleaning chemicals are safe for use on that type of plastic or metal. Chemical/ material compatibility data is widely available on external websites (e.g. http://www.coleparmer.co.uk/Chemical-Resistance )
View full article
Picard Product_Support
‎2018-09-10 12:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:52 PM

Labels:
  • Field Devices
2601 Views

Error "The Bcpv3 service is not installed under Config/Services" adding a discovered BACnet device to station database

Issue Encountered the error 'The Bcpv3 service is not installed under Config/Services' while trying to add a discovered BACnet device to the station database Product Line TAC IA Series Environment I/A Series G3 Enterprise Network Server / Workbench Cause The default view of the BacnetNetwork is now the 'Bcp Bacnet Device Manager' instead of the standard I/A Series G3 'Bacnet Device Manager'. This happens when the Distech Controls EC-NET-AX Support Package  v3.0.2.8 (I/A Series G3 support files for Proview) is installed on the computer running the station. Refer to BCP Device Manager showing up with the BACnet Device Manager. The Bcp Bacnet Device Manager is used to discover and add Distech devices. Using it to discover and add I/A Series BACnet controllers will result in the 'The Bcpv3 service is not installed under Config/Services' error. Third party non Distech devices may also exhibit the same symptoms. Resolution Discover and add BACnet devices using the 'Bacnet Device Manager' instead of the 'Bcp Bacnet Device Manager'. The 'Bacnet Device Manager' is now the 2nd view of the BacnetNetwork (right-click on the BacnetNetwork and go to 'Views' > ' Bacnet Device Manager').
View full article
Picard Product_Support
‎2018-09-10 05:12 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:51 PM

Labels:
  • TAC IA Series
3294 Views

Wiring an STR-150 into a Xenta 121

Issue The STR-150 Installation Instructions state that the stat wires into D1, X1, and M of the Xenta 100 series controller. However, this is not applicable to the Xenta 121, which does not have a D1 input. Product Line TAC Vista Environment Xenta 121 STR-150 Cause The correct terminal for the mode input from the STR-121 is labeled differently on the Xenta 121 versus all other Xenta 100 series controllers. Resolution Wire the stat as follows: STR-150 Xenta 121 Label Terminal Label Terminal Mode 11 Y1 5 Data 12 X1 7 M 13 M 6   The Purpose of output Y1 The only function that the STR-150 uses Y1 for is to get an effective occupancy signal from the Xenta 121. When the Xenta 121 is occupied, the man symbol will be displayed on the STR-150. If Y1 is already in use then the Status LED can be moved to a K output as explained inIs it possible to use an analog valve on the TAC Xenta 121-FC/HP and still have the effective occupancy active on the STR-150?. In order to activate this feature, the Hardwired status LED option must be selected. This can be found under the Configuration tab > Connected devices > Room unit in ZBuilder. If this feature is not desired then unselect Hardwired status LED and only wire up X1 and M. The STR-150 will still be able to send the controller the temperature, setpoint, bypass signal, and fan speed.
View full article
Picard Product_Support
‎2018-09-06 01:44 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:50 PM

Labels:
  • TAC Vista
2282 Views

Smart Heap error when starting Cyberstation or not all processes start and Cyber doesn't open

Issue When starting up the Continuum Workstation an error "SmartHeap library out of memory" error is displayed and Continuum does not startup. Product Line Andover Continuum Environment Continuum Cyberstation Microsoft Windows Cause The PC memory allocated for Cyberstation to use is insufficient for the application and the site's configuration. There are three known items that can require more memory to be required on Workstation startup. EventNotifications. If a very large number of them. The Workstation reads all of them and may require more memory at startup. Workstation Programs. Check in the Workstation for many or large Programs. Objects in the Root of Continuum. The startup of WS can be very long with a large number of objects in the Root. Resolution Verify that the PC being used for the workstation meets the minimum requirements as defined in the Install.pdf document for the specific Cyberstation version being used. If other applications are to be run on the PC then the RAM size should be increased accordingly. If the system StandAlone (Single User) 1.81 or before then verify the database size is below 2Gb, For Version 1.82 and above it can not exceed 4Gb. Verify that you have sufficient available memory you have when seeing the error, using task manager. If the above checks confirm that the basic PC memory is sufficient then the following changes can be made to allow the Cyberstation application further resources, this is often required when a number of Plain English programs are running in a Workstation. Shut down Continuum and set the Virtual Memory size Initial to 2048 and Maximum to 4096. Using Regedit go to the registry key HKEY_CURRENT_USER\Software\Andover Controls\Continuum\Settings and increase the setting for omscachesize to 5000 decimal. For systems where the Workstation is known to have an extremely heavy workload, this number may be increased up to 9000 in decimals. If using the Elevator Control Module add-on, it may be necessary to set the size to 5000. Note: For new Continuum or WebClient Workstations, the omscachesize registry key is not created until after the Workstation has first logged in at least once. If you are adding a Workstation to an existing LAN installation with a large ContinuumDB, then the omscachesize may need to be increased right from the start. One way to do this is to: Create  a new "test" database, see Creating a test database for troubleshooting for more information. Connect this Workstation to that test database so that the correct registry keys are created Change the omscachesize value as described above Restart the PC Reconnect to the original production database and start-up Continuum.
View full article
Picard Product_Support
‎2018-09-07 08:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:49 PM

Labels:
  • Andover Continuum
2326 Views

Incompatible SQL Server Version error when Restoring I/NET Database in DBCreate

Issue When restoring database, an error will show up, saying that version is incompatible with this server. Product Line EcoStruxure Building Operation, TAC INET Environment I/NET Cause This is usually caused by restoring new SQL database to older version or under different kind of Operation Systems (like restoring a 64 bit database to a 32bit SQL server). Microsoft doesn't like to do this. Resolution There is build number matrix for each SQL server version:     RTM (Gold, no SP) SP1 SP2 SP3 SP4 SQL Server 2012 11.00.2100.60 11.00.3000       SQL Server 2008 R2 10.50.1600.1 10.50.2500 10.50.4000     SQL Server 2008 10.00.1600.22 10.00.2531 10.00.4000 10.00.5500   SQL Server 2005 9.00.1399.06 9.00.2047 9.00.3042 9.00.4035 9.00.5000 So check the build number in the error message and download the corresponding version of SQL to restore and be used for I/NET.  Refer to How to Troubleshoot on DBCreate for more issues about DBCreate.
View full article
Picard Product_Support
‎2018-09-11 07:04 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:47 PM

Labels:
  • EcoStruxure Building Operation
  • TAC INET
2454 Views
  • « Previous
    • 1
    • …
    • 104
    • 105
    • 106
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of