Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Smart Heap error when starting Cyberstation or not all processes start and Cyber doesn't open

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Smart Heap error when starting Cyberstation or not all processes start and Cyber doesn't open
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • AdamSteele
    AdamSteele
  • PaulFr
    PaulFr
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2260 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Smart Heap error when starting Cyberstation or not all processes start and Cyber doesn't open

Picard Product_Support
‎2018-09-07 08:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:49 PM

Issue

When starting up the Continuum Workstation an error "SmartHeap library out of memory" error is displayed and Continuum does not startup.

Product Line

Andover Continuum

Environment

Continuum Cyberstation

Microsoft Windows

Cause

The PC memory allocated for Cyberstation to use is insufficient for the application and the site's configuration.

There are three known items that can require more memory to be required on Workstation startup.

  1. EventNotifications. If a very large number of them. The Workstation reads all of them and may require more memory at startup.
  2. Workstation Programs. Check in the Workstation for many or large Programs.
  3. Objects in the Root of Continuum. The startup of WS can be very long with a large number of objects in the Root.

Resolution

  1. Verify that the PC being used for the workstation meets the minimum requirements as defined in the Install.pdf document for the specific Cyberstation version being used. If other applications are to be run on the PC then the RAM size should be increased accordingly.
  2. If the system StandAlone (Single User) 1.81 or before then verify the database size is below 2Gb, For Version 1.82 and above it can not exceed 4Gb.
  3. Verify that you have sufficient available memory you have when seeing the error, using task manager.

If the above checks confirm that the basic PC memory is sufficient then the following changes can be made to allow the Cyberstation application further resources, this is often required when a number of Plain English programs are running in a Workstation.

  1. Shut down Continuum and set the Virtual Memory size Initial to 2048 and Maximum to 4096.
  2. Using Regedit go to the registry key HKEY_CURRENT_USER\Software\Andover Controls\Continuum\Settings and increase the setting for omscachesize to 5000 decimal. For systems where the Workstation is known to have an extremely heavy workload, this number may be increased up to 9000 in decimals. If using the Elevator Control Module add-on, it may be necessary to set the size to 5000.

Note: For new Continuum or WebClient Workstations, the omscachesize registry key is not created until after the Workstation has first logged in at least once. If you are adding a Workstation to an existing LAN installation with a large ContinuumDB, then the omscachesize may need to be increased right from the start. One way to do this is to:

  1. Create  a new "test" database, see Creating a test database for troubleshooting for more information.
  2. Connect this Workstation to that test database so that the correct registry keys are created
  3. Change the omscachesize value as described above
  4. Restart the PC
  5. Reconnect to the original production database and start-up Continuum.
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4864
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of