Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Wiring an STR-150 into a Xenta 121

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Wiring an STR-150 into a Xenta 121
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2379 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Wiring an STR-150 into a Xenta 121

Picard Product_Support
‎2018-09-06 01:44 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:50 PM

Issue

The STR-150 Installation Instructions state that the stat wires into D1, X1, and M of the Xenta 100 series controller. However, this is not applicable to the Xenta 121, which does not have a D1 input.

Product Line

TAC Vista

Environment

  • Xenta 121
  • STR-150

Cause

The correct terminal for the mode input from the STR-121 is labeled differently on the Xenta 121 versus all other Xenta 100 series controllers.

Resolution

Wire the stat as follows:

STR-150 Xenta 121
Label Terminal Label Terminal
Mode 11 Y1 5
Data 12 X1 7
M 13 M 6

 

The Purpose of output Y1

The only function that the STR-150 uses Y1 for is to get an effective occupancy signal from the Xenta 121. When the Xenta 121 is occupied, the man symbol will be displayed on the STR-150. If Y1 is already in use then the Status LED can be moved to a K output as explained inIs it possible to use an analog valve on the TAC Xenta 121-FC/HP and still have the effective occupa.... In order to activate this feature, the Hardwired status LED option must be selected. This can be found under the Configuration tab > Connected devices > Room unit in ZBuilder.

If this feature is not desired then unselect Hardwired status LED and only wire up X1 and M. The STR-150 will still be able to send the controller the temperature, setpoint, bypass signal, and fan speed.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 5422
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore