Upgrade Conversion Log Warning and Error Analysis

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Upgrade Conversion Log Warning and Error Analysis
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Hernan_Urueña
    Hernan_Urueña
  • Dave_Shore
    Dave_Shore
  • DavidFisher
    DavidFisher
  • DavidChild
    DavidChild
  • Cody_Failinger
    Cody_Failinger
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2334 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Upgrade Conversion Log Warning and Error Analysis

Picard Product_Support
‎2018-09-11 07:03 AM

Last Updated: Administrator CraigEl Administrator ‎2025-11-25 05:51 PM

Issue

During an Automation Server upgrade using Device Administrator, you may see warnings or errors in the Conversion Log.

  • Errors block the upgrade process.
  • Warnings allow the upgrade to complete, but may indicate invalid values or bindings.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server, AS-P, AS-B
  • Building Operation Enterprise Server
  • Building Operation Device Administrator
  • Conversion Log

Cause

Starting with EBO v1.4, new binding rules were introduced:

  1. Public Numeric/Signal bindings removed
  2. Multiple bindings per point prohibited (only the first remains)
  3. Bindings to Local-Node NVIs dropped

Older configurations that violate these rules trigger warnings or errors in the Conversion Log.

Resolution

  • Run the Device Administrator upgrade. Instructions on how to perform the Automation Server upgrade and how to obtain the Conversion Log, see:
    • SmartX Server System Upgrade Workflow - EcoStruxure WebHelp 
    • Opening the Conversion Log - EcoStruxure WebHelp
  • Export and review the Conversion Log:

The file paths given in the Conversion Log entries will direct you to the location of the unresolved or invalid reference. Depending on the type of entry it is, it may require further action to correct the problem.

 

Type of entries found in the Conversion Log

WARNING: ERROR: Invalid_Property_Reference (destination) (source)

Explanation: Either rule 1 or 3 has been broken. If a public numeric/signal is bound programmatically to another object then it violates rule number 1. The public numeric/signal in the program must be changed to an input or output before upgrading the database.

If the destination of the binding is an NVI in the Local Node then it violates rule number 3. A change to the configuration of the local node must be implemented before performing the upgrade. In many cases the substitution of an NVO for the NVI will address this issue.

Explanation: This binding should not have been allowed in SmartStruxure version 1.3. In the StruxureWare Building Operation Technical Reference Guide, you will find on page 2107 that BACnet priority 6 is reserved for future use. This binding needs to be made to a different priority.


WARNING: ERROR: Object_Does_Not_Exist (object).

Explanation: The object that the reference is trying to bind to does not exist. In other cases the binding was already broken in the source database so it will remain broken in the target database. The binding fix can be addressed before or after the upgrade.


WARNING: Property (property) bound to (property), so binding to (property) is dropped. Multiple bindings are not allowed in SmartStruxure version 1.4 and above.

Explanation: The object is being written to by multiple objects and/or programs. This violates rule number 2 and is no longer accepted. After the upgrade, only one of the bindings will be left connected and all others will be dropped. This will require changes to be made to the configuration to maintain the same operation.

Note: In some cases this warning can occur due to a default value of a configuration object that is mistakenly interpreted as a duplicate binding. The binding is in fact preserved by the upgrade and no further action is required.


WARNING: Discarding incomplete binding for (object) -unknown source.

Explanation: Due to a version 1.3 defect, the source version configuration database contains an incomplete binding error. This is not a problem but it may be a sign that someone intended for the property to be bound to something but failed to do so. Therefore, the configuration should be examined after the upgrade has been completed to insure that everything is okay. No information has been lost in the upgrade but check the configuration to rule out any errors in the source version database.


WARNING: Property (property) in (object) is Unit configured but is not configurable in the new.

Explanation: This property has a selected unit configured in the source version database, while in the target version configuring the unit of this property is no longer possible/meaningful. These errors should be investigated to insure that there has been no negative impact on the operation. Generally this error will not be a problem and will require no further action.


WARNING: Property REF in (object) is not defined in the new system, skip REF.

Explanation: The REF property prior to version 1.4 held a back-reference to an object or property that was referring to the property at hand. Starting in version 1.4 and on, the back-references are handled by other means and are no longer represented in the configuration database. This information can not be upgraded but this is not a problem and no further action is required.


WARNING: Invalid value for (property) in the object, (object). The default value has been applied.

Explanation: The value seen in the source version is invalid or can not be found; therefore the upgrade process sets it back to the default value. No further actions needs to be taken.


WARNING: The declared instance (instance) is obsolete but contains non-default data which has been discarded.

Explanation: If the instance is a SavedUserTokens or System/Remote Server warning then the warning can be ignored. No further action is required.


WARNING: Property (property) in (source) is not an acceptable property type and is not configured.

Explanation: This has to do with the lead reference for shadow Alarm Control Panels that cannot be properly upgraded due to changes to the type of system in version 1.4. There is logic in place that automatically sets the lead reference to the ES again. This is a warning that can be ignored.

Explanation: There have been changes made to the type of system. This change prevents the hidden SynchSource property of the Time Zone setting in the source version of the database from being upgraded automatically. If the lead reference was set for Time Zone in the source database, this may have been erased and will have to be done again after the upgrade. This should be followed up manually.

Explanation: The new referencing scheme expects all references to be relative so if there is a full binding path it is perceived as an error. This is not an issue and requires no action.

Explanation: MatchedDevice is a hidden property that can not be seen. This warning refers to old items that have not been cleaned out. This warning can be ignored.

Note: Also keep in mind that the upgrade process considers any empty link "not an acceptable Property". This error can be ignored, no changes need to be made.


INFORMATION: Property "Value" in (location) is Unit configured but is not configurable, default unit is used.

Explanation: This property has a configured unit that is no longer allowed to be configured in the target database, a fixed default value is used. This is unlikely to cause a problem, no further action needs to be taken.

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (3)
  • Find more articles tagged with:
  • 14006
  • DavidShore21
  • HernanUruena25
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore