Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 81
    • 82
    • 83
    • …
    • 509
  • Next »

Satchwell MEU 3-port Unit Control Valve replacement.

Issue Satchwell MEU 3-port Unit Control Valve is obsolete. Product Line Field Devices Environment Satchwell MEU 3-port Unit Control Valve installations Cause Satchwell MEU 3-port Unit Control Valve requires replacement due to failure. Resolution Satchwell MEU 3-port Unit Control Valve may be replaced by Schneider Electric VZ319 series Unit Control Valve, although dimensional differences may apply. It should be noted that VZ319 series Unit Control Valves are available in both Flat Face and Compression fitting specifications. The latest issue of the Schneider Electric Valves and Actuators Catalogue should therefore be consulted in order to determine the availability of the particular size / kv / fitting combination required. It should also be noted that any Actuator installed on the Satchwell MEU 3-port Unit Control Valve will not be compatible with the replacement Schneider Electric VZ319 3-port Unit Control Valve and that a Schneider Electric MZ20 series Actuator of the appropriate operating voltage / signal type will also be required.
View full article
Picard Product_Support
‎2018-09-07 01:32 PM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-19 05:39 AM

Labels:
  • Field Devices
11284 Views

Failed to import backup set file.

Issue Backup set file cannot be imported.   Product Line EcoStruxure Building Operation Environment Building Operation Workstation Automation Server Enterprise Server Backup set file Cause Backup set file is very large so import of backup set file fails.   Resolution A current workaround is to manually copy the backup file set to the default backup location. Browse to C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db_backup or C:\ProgramData\Schneider Electric EcoStruxure\Building Operation x.x\Enterprise Server\db_backup By default the ProgramData folder is hidden. To view the ProgramData folder follow the below steps: Select Organize>>Folder and Search options. In Folder options under view tab select "Show hidden files,folders and drives". Manually copy the Enterprise Server Backup set file and paste to the below location: C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db_backup\LocalBackup   Manually copy the Automation Server Backup set file and paste to the below location: C:\ProgramData\Schneider Electric StruxureWare\Building Operation 1.x\Enterprise Server\db_backup\ASArchives
View full article
Picard Product_Support
‎2018-09-07 08:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 08:01 PM

Labels:
  • EcoStruxure Building Operation
2760 Views

.NET Framework errors in general

Issue When launching a program or when working with a program, you get an error from "Microsoft .NET Framework".   Product Line EcoStruxure Building Operation, Satchwell MicroNet, TAC INET, TAC Vista Environment Windows .NET Framework Cause Microsoft .NET Framework is used in almost all larger applications, and there can be various reasons why you see an error. One reason can be application specific, meaning that there is an actual issue with the software and the way the software is using .NET Framework, but another reason can be that the .NET Framework installation itself is corrupted. If it's an application specific issue, you need to contact product support, but in many cases simply repairing the .NET Framework installation has proven to solve the issue. Resolution 1: Close all applications 2: Make sure you have the correct version of .NET Framework installed for the software you use referencing the product's data sheet. You can use this tool to check what versions you have. Here is a direct download link. 3: Install versions that might be missing. You can download the various versions from the tool linked above. 4: Download Microsoft's .NET Framework repair tool and run it applying all fixes the tool suggests. Here is a direct download link.
View full article
Picard Product_Support
‎2018-09-11 09:47 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:58 PM

Labels:
  • EcoStruxure Building Operation
  • Satchwell MicroNet
  • TAC INET
  • TAC Vista
3113 Views

Sigma - Remote Alarm Manager - Commonly used GSM modems.

Issue GSM modems that can be used with the Remote Alarm Manager. Product Line Satchwell BAS & Sigma,Satchwell MicroNet,TAC Vista Environment Remote Alarm Manager. BAS Sigma Micronet Vista  GSM RAM Siemens TC35i Siemens MC52i Multi-Tech MTCBA-G-F4-GB/IE Cinterion MTX-65+G-V53 Cause Not all GSM modems will allow the full functionality of message acceptance in the Remote Alarm Manager. Resolution The following GSM modems are known to provide the full message acceptance of the Remote Alarm Manager. Siemens TC35i GSM modem terminal. In the Remote Alarm Manager configuration select the C35i driver. This modem is now being replaced be the Cinterion (Siemens) MC52i GSM/GPRS Dual band modem terminal, which has not been tested, but appears to be a direct replacement with added functionality. TC35i GSM/GPRS modem terminal data sheet MC52i GSM/GPRS modem terminal data sheet Multi-Tech MultiModem MTCBA-G-F4-GB/IE modem terminal. In the Remote Alarm Manager configuration select the Brodersen UCM 91/92. This modem is still available, but seems expensive and difficult to source. MultiTech MultiModems MTCBA-G-F4 data sheet Cinterion MTX-65+G-V53 modem terminal.In the Remote Alarm Manager configuration, allow the software to locate the modem and use a generic driver. Cinterion MTX-65+G-V53 modem terminal data sheet   Remote Alarm Manger is no longer a support solution, it is recommended transitioning or upgrading to EcoStruxure Building Operation.
View full article
Picard Product_Support
‎2018-09-07 08:44 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:54 PM

Labels:
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC Vista
5580 Views

What is the replacement for a Drayton Theta YBM2A Valve Body / Actuator assembly?

Issue The Drayton Theta YBM2A Valve Body / Actuator assembly is to be replaced. Product Line Field Devices Environment Replacement Drayton Actuator Valve YBM2A Cause The Drayton Theta YBM2A Valve Body / Actuator assembly is obsolete. Resolution OVERVIEW The Drayton Theta YBM2A Valve Body / Actuator assembly is obsolete, and there is no purpose built replacement. The Valve Body was available in 1.1/4", 1.1/2" and 2" B.S.P. sizes and was normally installed as a mixing valve in variable temperature, constant volume, compensated heating circuits. No Valve Body / Actuator assemblies are currently available in these sizes. Details of the YB Valve Body may be viewed here.   VALVE BODY REPLACEMENT To replace the YBM2A Valve Body the following is required:- S-E Satchwell MB Valve Body of appropriate size - MB1552 (1.1/4"), MB1602 (1.1/2"), MB1652 (2") Details of the MB Valve Body may be viewed here.   ACTUATOR REPLACEMENT The YBM2A Actuator comprised a 3-wire electrical connection enabling it to be operated by a Mains Voltage changeover contact device as follows :- Terminal M1 – Open signal Terminal M2 – Close signal Terminal M3 – Common The YBM2A Actuator may be replaced by one or other of the following S-E Actuators :- MD10B-230 MD20B-230 (if MD10B-230 not available) Details of the MD10B-230 Actuator may be viewed here. Details of the MD20B-230 Actuator may be viewed here. N.B. The YBM2A Actuator also included an additional 3-wire electrical connection associated with an integral S.P.C.O. Auxiliary Switch wired as follows :- Terminal S1 – Normally Closed Contact Terminal S2 – Common Terminal S3 – Normally Open Contact Where external wiring is connected to the YBM2A Actuator Auxiliary Switch then an Auxiliary Switch Kit containing a S.P.C.O. Auxiliary Switch should be installed on the MD Actuator. Auxiliary Switch Kit MD-S1 (914-1060-000) Details of the MD-S1 Auxiliary Switch Kit may be viewed here. The MD-S1 Auxiliary Switch Kit should be wired as follows :-. Terminal S1 – Common Terminal S2 – Normally Closed Contact Terminal S3 – Normally Open Contact   LINKAGE KIT A Linkage Kit will also be required in order to enable the MD Actuator to be mounted on the MB Valve Body. Linkage Kit LMD/AR-MB (914-1071-000) Details of the LMD/AR-MB Linkage Kit may be viewed here In such 3-wire installations the YBM2A Valve / Actuator assembly only will need to be replaced, while any associated Controller and Sensors may be retained.
View full article
Picard Product_Support
‎2018-09-09 11:51 PM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-19 05:50 AM

Labels:
  • Field Devices
6657 Views

What is valve authority?

Issue What is valve authority? Product Line Field Devices Environment Any valve Cause Information on Valve Authority to obtain good control. Resolution Valve Authority = (Pressure drop across fully open control valve) / (pressure drop across the remainder of the circuit) + (pressure drop across fully open valve) In other words, valve authority within a system indicates how much of the system's total pressure drop comes from the control valve. It is common practice to consider the range between .2 to .5 as "acceptable" authority for proportional valve.
View full article
Picard Product_Support
‎2018-09-06 02:30 PM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-19 05:51 AM

Labels:
  • Field Devices
2175 Views

What is the replacement for a Drayton CRL 240 Actuator / Valve assembly.

Issue The Drayton CRL 240 Actuator / Valve assembly is to be replaced. Product Line Field Devices Environment Replacement Drayton Actuator Valve CRL 240 Cause The Drayton CRL 240 Actuator / Valve is obsolete Resolution The Drayton CRL 240 Actuator / Valve assembly is obsolete and there is no purpose built replacement. The associated Drayton Valve Body was available in numerous sizes.  These sizes are not available in current combined Actuator / Valve designs. To replace one of the above Actuator / Valve Body combinations the following are required :- Valve sizes ½” – 2” Valve – MB(1/2" - 2") Actuator -  MD10B-230 (  MD20B-230 could  be used if MD10B-230 is not available) Auxiliary Switch - MD-S1 ( MD-S2 could be used if MD-S1 is not available) Linkage Kit - LMD/AR-MB or the RM3601 actuator without the need for a linkage kit Linkage Kit Select S-E LMD/AR-MB Linkage Kit. (914-1071-000) MBF Valve sizes 65mm – 100mm Could be replaced by the VTRE range To view the MB Valve Data Sheet, please click here. To view the MD10B Actuator Data Sheet, please click here. To view the MD-S1 Auxiliary Switch Data Sheet, please click here. To view the LMD/AR-MB Linkage Kit Data Sheet, please click here. To view the LMD/AR-MBF Linkage Kit Data Sheet, please click here. To view the RM 360 data sheet please click here
View full article
Picard Product_Support
‎2018-09-10 12:21 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-19 05:52 AM

Labels:
  • Field Devices
6611 Views

Sigma will not launch displaying no error message or HTTP error.

Issue Schneider Electric domain firewall policy Product Line Satchwell BAS & Sigma Environment Engineer's laptops Cause Schneider computer/domain updates include McAfee firewall updates. It has been seen on some laptops with a fully working Sigma system, after a  Schneider policy update, the Sigma client fails to connect to the server.   Resolution Access to the firewall setting, on most Schneider Electric engineer's  laptops is not possible. Disabling the McAfee firewall should allow Sigma to load. Locate and, with a right mouse click, select the McAfee Icon  (found on the taskbar near the clock). From the list provided select "Quick Settings" Then select "Enable Firewall Timed Groups", You will need to enter a reason. The firewall will be disabled for a one hour period. 
View full article
Picard Product_Support
‎2018-09-11 06:28 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:44 PM

Labels:
  • Satchwell BAS & Sigma
2252 Views

Automation Server - Warm and Cold Start differences

Issue Automation Server - Warm and Cold Start differences Product Line EcoStruxure Building Operation Environment Building Operation Automation server Cause The explanation on the differences between a warm start and a cold start in the documentation and web help may not be clear to some.  Resolution Warm Start: Restarts the controller's application Cold Start: Restarts the controller's operating system An Automation Server can be warm/cold started from Workstation or by using the reset button on the Automation Server. Refer to Reset Functions on Web Help for an explanation of the differences between warm and cold starting the AS.  Basically, you can set the Retain Levels for variables in Building Operation to 'No', 'warm start' or 'cold start'. To change the retain level of a variable and go to its properties.  - Click on the gear icon. - Set the retain level of the variable. 1. Retain level set to 'No' - The variable is reset to the value set when the object was created. When you create an Analog Value object, the value of the newly created object is '0'. A user can set this to another value. When retain level is set for this Analog Value object, after a warm or cold start, the value of this object will default back to '0'. 2. Retain level set to 'Warm start' - The value is set back to the last value set by the user. If a user change the value of an Analog Value object to another value and save, after a warm start, the object will return to the last value set by the user.  3. Retain level set to 'Cold start' - The value is set back to the last value set by either the user or the system (for instance by a program). The operation is similar to the warm start but in this case, the last value set by the system will also be retained. 
View full article
Picard Product_Support
‎2018-09-11 07:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 07:25 PM

Labels:
  • EcoStruxure Building Operation
7819 Views

Replacement of AVUE 2. 3 or 4 Series Actuator with AVUE 5 Series Actuator results in poor actuation of Control Valve.

Issue AVUE 5 Series Actuator does not actuate Control Valve correctly when installed in place of AVUE 2, 3 or 4 Series Actuator. Product Line Field Devices Environment AVUE 5304, AVUE5305, AVUE5354 and AVUE5355 Actuators installed on FEU, MEU, VEU Unit Control Valves. AVUE 5304, AVUE5305, AVUE5354 and AVUE5355 Actuators installed on MZX, VZX Plant Control Valves. Cause AVUE 5 Series Actuators are available with stoke lengths of 9.5mm and 12.7mm AVUE 5304 and AVUE 5354 Actuators provide a stroke length of 12.7mm AVUE 5305 and AVUE 5355 Actuators provide a stroke length of 9.5mm   AVUE 2, 3 and 4 Series Actuators provided universal stroke compatibility. Control Valves having either 9.5mm or 12.7mm stroke could be actuated.  Resolution Select AVUE 5304 (Direct Acting) or AVUE 5354 (Reverse Acting) to actuate MZX or VZX Plant Control Valves. Select AVUE 5305 (Direct Acting) or AVUE 5355 (Reverse Acting) to actuate FEU, MEU or VEU Unit Control Valves.   For further AVUE 5 Series Actuator information please refer to Data Sheet DS 3.002  11/06   The AVUE is no longer available, check the 2022 Valves & Actuators Catalog - EMEA & APAC for a replacement. Note: The valve would need to be replaced to accommodate the replacement actuator.
View full article
Picard Product_Support
‎2018-09-07 12:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 02:16 AM

Labels:
  • Field Devices
3240 Views

Replacement of Satchwell AR Series 7 Rotary Actuator by Schneider Electric MD Series Rotary Actuator due to obsolescence. (Actuator Selection)

Issue Satchwell AR Series 7 Rotary Actuator requires replacement Product Line Field Devices Environment Satchwell AR Series 7 Rotary Actuators installed on Air Dampers, Satchwell MB Series or MBF Series Rotary Shoe Valve Bodies. Actuator types :- ARE ARM ARX Cause Obsolescence of Satchwell AR Series 7 Rotary Actuators Resolution Replace Satchwell AR Series 7 Rotary Actuators with appropriate Schneider Electric MD Series Rotary Actuators and Linkage Kits selected from the following :- Satchwell AR Series 7 Rotary Actuators installed on Air Dampers. ARE Series 7 = MD20A-24 ARM Series 7 = MD20B-230 ARX Series 7 = MD20B-24 N.B. Schneider Electric MD20 Series Actuators are supplied with a Direct Damper Mounting Kit enabling the Actuator to be installed direct on to an Air Damper Spindle. Should the Actuator be required to operate an Air Damper remotely by means of a Damper Crank Arm and associated Connecting Rod and Universal Connectors, then this may be achieved through the installation of the following Linkage Kit :- ZG-MD20 Damper Linkage Kit (914-1063-000) Should the Satchwell AR Series 7 Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the Schneider Electric MD Series Actuator as appropriate :- MD – S1 One independent Mains Voltage rated changeover contact Auxiliary Switch MD – S2 Two independent Mains Voltage rated changeover contact Auxiliary Switches   Satchwell AR Series 7 Rotary Actuators installed on Satchwell MB Series Screwed Rotary Shoe Valve Bodies. ARE Series 7 = MD10A-24 + Linkage Kit 914-1071-000 ARM Series 7 = MD10B-230 + Linkage Kit 914-1071-000 ARX Series 7 = MD10B-24 + Linkage Kit 914-1071-000 N.B. Should the Satchwell AR Series 7 Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the Schneider Electric MD Series Actuator as appropriate :- MD – S1 One independent Mains Voltage rated changeover contact Auxiliary Switch MD – S2 Two independent Mains Voltage rated changeover contact Auxiliary Switches   Satchwell AR Series 7 Rotary Actuators installed on Satchwell MBF Series Flanged Rotary Shoe Valve Bodies ARE Series 7 = MD20A-24 + Linkage Kit 914-1070-000 ARM Series 7 = MD20B-230 + Linkage Kit 914-1070-000 ARX Series 7 = MD20B-24 + Linkage Kit 914-1070-000 N.B. Should the Satchwell AR Series 7 Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the Schneider Electric MD Series Actuator as appropriate :- MD – S1 One independent Mains Voltage rated changeover contact Auxiliary Switch MD – S2 Two independent Mains Voltage rated changeover contact Auxiliary Switches   Product information. For details of MD10A please see here For details of MD10B please see here For details of MD20A please see here For details of MD20B please see here For details of MD-S1 please see here For details of MD-S2 please see here For details of Linkage Kit ZG-MD20 please see here For details of Linkage Kit 914-1070-000 please see here For details of Linkage Kit 914-1071-000 please see here
View full article
Picard Product_Support
‎2018-09-10 12:22 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 02:01 AM

Labels:
  • Field Devices
5093 Views

Vista Server Fails to Start

Issue TAC Vista Server fails to start or "hangs" during startup. "Ensure TAC Vista Server is started" error, after having just started Vista Server and attempting to open Workstation. Product Line TAC Vista Environment Vista Server Cause Corrupt Vista database Bad installation of TAC Vista Resolution Troubleshooting technique to determine if you have corruption of the TAC Vista Database or TAC Vista Software. Determine if the TAC Vista Server is starting by observing the Tacos.exe process in Windows Task Manager. Server is crashing if Tacos.exe is not present or disappears after starting the Server. From the Start Menu, navigate to TAC Vista Server Setup and browse the Vista Server database location to a test location, i.e. :\DBTest. This will create a new "blank" database at that location. Attempt to start TAC Vista Server and observe results in Windows Task Manager. You should get one of two results: If TACOS.exe process is running and the Server seems to start correctly, you may have a corrupted Vista Database. You may further investigate by copying the site Vista Database folder structure and placing it on another computer (with the same Vista Software version) to see if the Server will start. In some cases, it may be successful, a backup can be made and restored to site machine. In most cases, it will also fail. Restoring to a known good backup is the only recourse.   If TACOS.exe process is not running and the Server seems to start incorrectly, you may have corrupted Vista Software. It is recommended to follow the uninstall/ reinstallation procedure for your version of Vista. You may further investigate by copying the site Vista Database folder structure and placing it on another computer (with the same Vista Software version) to see if the Server will start. In this case, it should be successful.
View full article
Picard Product_Support
‎2018-09-06 10:40 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:59 AM

Labels:
  • TAC Vista
2396 Views

.xif files for SE7200 / SE7300 / SE7600

Issue Where can we find the LON xif files for SE72xx, SE73xx, SE76xx controllers? Product Line EcoStruxure Building Expert,EcoStruxure Building Operation,Field Devices Environment SE7200 / SE7300 / SE76000 Room Controllers Cause xif files are needed for LON applications. Resolution All LON related files for these controllers are available for download on The Exchange Download Center:   XIF files and plug-ins Resource files (DRF kit)
View full article
Picard Product_Support
‎2018-09-11 06:42 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:57 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
3143 Views

Sensor Calibration Certificate

Issue A calibration certificate is sometimes requested by the end customer Product Line Field Devices Environment Schneider Electric sensor portfolio Cause To ensure that a sensor is keeping measurement values within specification, a certificate is sometimes requested by the end customer. Resolution If a calibration certificate is requested, this must be notified to the Orders dept when the order is placed. The ordered sensors are then tested again according to the specifications and delivered with a calibration certificate. This process may lead to additional costs and a slightly longer delivery time. Calibration certificates cannot be produced after the products are delivered. Download the Sensor Calibration Certificate Order Form
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:50 AM

Labels:
  • Field Devices
2774 Views

WorkStation licenses

Issue Site looking to add some WorkStations with the ability to show Graphics but without the Graphic editor. Not sure which part number to order. Product Line EcoStruxure Building Operation Environment Building Operation WorkStation Cause Documentation Resolution V2 or higher, Enterprise Server or Enterprise Central license includes three concurrent client licenses (WebSation or WorkStation). For additional clients, order one or more of the licenses below. These licenses do not include any editors, the WorkStation will show the graphics but will not allow editing, order below part numbers:   If graphic or programming editing is required, you can order professional WorkStation license, which will add extra WorkStation with editors, or order Programming & Graphics Editor licensing, which will add editors to existing WorkStation Standard license.  
View full article
Picard Product_Support
‎2018-09-11 03:58 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2022-08-18 06:56 AM

Labels:
  • EcoStruxure Building Operation
4908 Views

Capturing MSTP network bus activity

Issue How to get an MSTP capture file so it can be analyzed for comm activity on an MSTP bus How to determine if a site is using bad COV management How to determine if a controller has poor bus design or installation How to determine if a site has multiple BBMD's on the same subnet Product Line Andover Continuum, EcoStruxure Building Operation Environment bCX4000, bCX4040, ASP, ASB b3 controllers Third party BACnet MSTP devices Wireshark Cause Analyze MSTP traffic via capture. Resolution To capture MSTP communication activity to a capture file that can be analyzed using a network sniffer application such as WireShark you will need the following.   Hardware One is required to have an RS-485 Adapter to connect to the MS/TP trunk USB to RS-485 Adapter USB-RS485-WE-1800-BT FTDI, Future Technology Devices International Ltd | 768-1041-ND | DigiKey  RoamIA or RoamIO Any other RS-485 adapter compatible with BACnet MS/TP and baud rates used Software Download and install the following applications: BACnet MSTP Capture Application WireShark Configuration If using the USB to RS-485 Adapter Connect the USB adapter cable to the USB port on a laptop PC Connect the RS232/RS485 adapter to the 9-pin end of the USB adapter cable. Attach a length of MSTP bus cable to the wire terminal on the RS485 adapter. If using the FTDI Connect the TDI RS-485 adapter to the USB port on a laptop PC Connect the cables to the MSTP trunk where Orange = Data+ (A) and Yellow = Data- (B) Ensure the RS-485 adapter driver is installed in Windows by opening Device Manager and ensuring that it is listed as expected under Ports (COM and LPT). Record the COMx being reserved by the adapter.  If using Wireshark with MSTPcap.exe to capture Ensure MSTPcap.exe is installed in the Wireshark Extcap folder per MSTP Capture Application link above NOTE: Wireshark may need to be rebooted if MSTPcap.exe was added while it was open Launch Wireshark Select gear next to BACnet MS/TP on COMx Set known baud rate Click to start a capture.  If using MSTPcap.exe via Command Prompt to capture Copy the MSTP Capture application to C:\ Open a command window. Launch the application by entering C:\> Mstpcap com# ###### where com# is the PC's serial port (Com1, Com2, etc.) and ##### is the current baud rate the bCX/AS MSTP bus is configured for (19200, 38400, etc.). The command window will indicate the name of the file the activity is being captured to. Once done, close the command line window The capture data can be viewed by running Wireshark. Select File > Open and navigate to the folder the capture file was saved to and select the capture file. With the higher-end MSTP capture tools such as tools developed by PolarSoft and Cimetrix, MSTP captures at 76.8K baud are possible. Lower-end capture applications like MSTPCap typically are only able to capture MSTP packets from networks running at bus speeds at or below 38.4K baud. Also, check out the BACnet-Capturing MS/TP Traffic Quick-Help video on the Exchange. This video uses the older pipe method that was used before Extcap was available in Wireshark.
View full article
Picard Product_Support
‎2018-09-07 06:16 AM

Last Updated: Picard David_Purser Picard ‎2022-08-18 08:30 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
4630 Views

Unable to download controller operating files (pntfle.rec, lookup.rec etc) into a BAS outstation.

Issue Controller Download fails when downloading files into a BAS outstation. Product Line Satchwell BAS & Sigma Environment Satchwell BAS2000 Satchwell BAS2800 Satchwell BAS2800+ Cause File downloads (only outstation files, not node files) fail from a terminal connected to port 2 of an outstation e.g an engineers laptop.  Resolution Either perform a commstats (F3) of the node and a list of what devices and their number attached to each port is displayed. Or check the site node file to see what terminal number is configured to the outstation on Port 2. In either case the letter "T" with a device number will indicate a terminal has been set. In the BAS setup page, change the terminal number to match that found in item 1. Save and exit BAS. Re-open BAS, now download files to the controller.
View full article
Picard Product_Support
‎2021-01-31 08:35 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:18 AM

Labels:
  • Satchwell BAS & Sigma
1930 Views

MPM controller stuck in Bootloader

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue Upgrading the MPMs firmware through the boot loader was unsuccessful. 10.50.80.2 is pingable, but not the default IP 10.50.80.3. The LED's keep blinking in tandem (alternating one after the other), even after having the MPM powered over 10 seconds. Product Line EcoStruxure Building Expert Environment SmartStruxure Lite Multi-Purpose Manager Cause This can be triggered by multiple events: - MPM was interrupted (powered off) while the firmware was still being upgraded. - Database does not exist; MPM was formatted and does not have firmware installed. - Database is corrupt (for any reason) Resolution It is strongly recommended that a firmware upgrade be done via the "File Manager" tab in Building Expert. However, if this is not possible, an upgrade can be performed through the bootloader using the following steps: 1 - At the top left part of the screen, make sure "Status" says "Connected". 2 - Format the SD card clicking on the "Submit" button next to "File System Format". "Format Done" will be displayed next to the button once the format has been completed 3 - Click on the "Browse" button and Navigate to the Firmware_update_V2.XX.bp" on your computer then click on "Submit Query". 4 - The previous step will upload the firmware file to the MPM's SD card. Once the file has been transferred, the following message will appear: or 5 - The MPM Must be kept powered-up for at least 15 minutes in order to allow the MPM some time to unpack the firmware file. The best way to determine whether the MPM is back online is to ping its IP address using a "Command Prompt" window. 6 - Once the MPM replies to the ping, Building Expert can be accessible though 10.50.80.3   If the above solution does not work; meaning that every time a new firmware is pushed to the MPM, the MPM keeps coming back to the bootloader, contact technical support
View full article
Picard Product_Support
‎2018-09-11 08:54 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:10 AM

Labels:
  • EcoStruxure Building Expert
3728 Views

What is the maximum number of nodes and points allowed while using a Modbus TCP/IP or RTU xdriver on a BCX?

Issue Definition of number of nodes and points allowed using Modbus TCP/IP or RTU xdriver. Product Line Andover Continuum Environment Modbus Protocol Cause Definition of number of nodes and points allowed using Modbus TCP/IP or RTU xdriver according to the modbus protocol. Resolution The maximum number of nodes is 254. The address range for points is 1 through to 65535. The number of addresses is limited by the controller memory. We have had ~6000 points but please note the Modbus is a polled protocol so the more points you have the longer the poll rate.   Specific Modbus RTU Details Our Modbus RTU XDriver supports the node range from 0-255. According to the Modbus specification, the node range is from 0 – 255, with 0 being the master, 1-247 being the slaves, and 248-255 being reserved addresses. After 32 nodes (1 master + 31 slaves), you may need RS-485 repeaters to ensure proper communications. This depends on a number of different items, including if the RS485 transceivers are full or quarter load. You can find the Modbus serial standard at the link below for further details. http://www.modbus.org/docs/Modbus_over_serial_line_V1.pdf
View full article
Picard Product_Support
‎2018-09-07 04:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 12:30 AM

Labels:
  • Andover Continuum
7087 Views

Retrieve MPM IP Address

Issue Lost MPM IP address Product Line EcoStruxure Building Expert Environment SmartStruxure Lite MPM Cause Forgotten IP address Resolution 1. Connect your PC directly to your MPMs Ethernet port and set your computer network configuration to access the MPM at the default address of 10.50.80.3 (example, set your PC to use address 10.50.80.99). 2. Disconnect and re-connect power to MPM. 3. The MPM goes to Bootloader mode for approximately 10 seconds at start-up. You will see Blue and Green indicators (UN2/VA2 MPMs) alternate steadily during that time according to the following. a. While the MPM is in Bootloader mode, you can access your config.db file at 10.50.80.2/root/ config.db. b. Enter address in browser window before you restore power to not to miss the 10 second window. It may require more than one refresh attempt before you enter Bootloader. 4. The browser prompts you to open or save config.db file once successful connection is made. 5. Open file using text editor. 6. Search “ETH1_ip” field for IP address of your MPM to right side of “ETH1_ip”. 7. Enter IP address to browser address bar to access your MPM.
View full article
Picard Product_Support
‎2018-09-11 12:58 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 12:26 AM

Labels:
  • EcoStruxure Building Expert
3688 Views
  • « Previous
    • 1
    • …
    • 81
    • 82
    • 83
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of