Trend logs are not being saved to SQL after upgrading the SQL database

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Trend logs are not being saved to SQL after upgrading the SQL database
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1593 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Trend logs are not being saved to SQL after upgrading the SQL database

Picard Product_Support
‎2018-09-06 10:35 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:39 AM

Issue

Trend logs are not being saved to SQL after upgrading the SQL database. There are no error messages and Vista can read old (pre upgrade) values from the taclogdata database. The insertlogvalues keeps growing.

Product Line

TAC Vista

Environment

  • Vista 5.1.X
  • SQL 2005 or 2008 server with a database that has been upgraded to layout 2 (the new schema used from version 5.1.7).

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance.

Cause

The database schema is out of date. The database schema is a blueprint of how a database will be constructed.

Resolution

  1. Shut down Vista.
  2. Go to services and stop the TAC DSS writer service.
    1. Right-click on My Computer (Computer in Win 7 and Win Server 2008) and select manage.
    2. Locate services in the console that opens up.
    3. Locate the TAC DSS Writer service, select and then click on stop. This service is responsible for writing events and trend log data to the SQL database.
  3. Update the database schema.
    1. Open Vista sever setup and locate the SQL server tab.
    2. Click on the Custom radio button (if not already selected) and then change the name (e.g. add "_1" to the end of the current name) of the database in the SQL Server Name field.
    3. Click on Apply, OK and  then Yes to create the new database.
    4. Once complete, change the name of the database back to the original name (or click on the Typical radio button if using default settings) and click on Apply.
    5. A message will appear "Log database found but needs to be reconfigured. Reconfigure Log database?".
    6. Click on Yes.
  4. The database schema should now be updated.
    1. Right-click on My Computer (Computer in Win 7 and Win Server 2008) and select manage.
    2. Locate services in the console that opens up.
    3. Locate the TAC DSS Writer service, select and then click on Start. This service is responsible for writing events and trend log data to the SQL database.

Check to see that the logs are now being written to the log database. It may take some time to process the backlog.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 12719
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore