Issue
Difficulty getting b3 controller online in order to replace a failed one
Product Line
EcoStruxure Building Operation
Environment
- EcoStruxure Building Operation
- Continuum b3 Controller
Warning
Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.
Cause
A b3 controller has failed and needs to replace with the same model.
Resolution
- Remove the failed b3 controller.
- In EcoStruxure Building Operation Workstation change the serial number of the failed b3 to that of the replacement b3.
- Install the replacement b3 and ensure the MSTP bus is connected so it autobauds to the correct rate. Then power it up.
- Remove the battery tab from the replacement b3 (if applicable).
- In Workstation right-click on the replacement b3 and select Device -> Commission. A green progress bar should appear with a success status message.
- In Workstation right-click on the replacement b3 and select Download all objects. A green progress bar should appear with a success status message.
- In Workstation right-click on the replacement b3 and select Device -> Backup to flash.