'Com Addr' does not appear in list of SE7000 parameters

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • 'Com Addr' does not appear in list of SE7000 parameters
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1641 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

'Com Addr' does not appear in list of SE7000 parameters

Picard Product_Support
‎2018-09-06 09:03 AM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:39 AM

Issue

'Com Addr' does not appear in list of SE7000 or SER7000 parameters, even when a BACnet or wireless network card is fitted.

Product Line

EcoStruxure Building Expert

Environment

SmartStruxure

SmartStruxure Lite

Warning

Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.

Cause

'Com Addr' only appears in the list of parameters when the controller recognises that a BACnet or wireless adapter card is fitted.  If the parameter does not appear even when a card is fitted, there is a problem with the card, the connector or the controller motherboard. 

Resolution

Remove the front cover of the controller and check that a BACnet or wireless adapter card of the correct type is fitted (there are several variants - see the table below for details).  The BACnet/wireless card is piggybacked onto the controller motherboard via a plug and socket and two supporting pillars.

If a card is fitted, remove it and check for bent pins on the plug, signs of damage to the motherboard or daughter board (e.g. scorching), or dry solder joints on the plug or connector.

It may be possible to carefully straighten out any bent pins on the plug, but any other form damage is not repairable by the user and the whole comms card/ controller assembly should be returned for repair under warranty

 

Communication Boards

Part Number Description Compatibility
VCM7000V5045W Wireless communication card SE7000 Series room controllers
VCM72000V5045P Wireless ZigBee Pro communication card SE7200 Series room controllers
VCM7300R5045P Wireless ZigBee Pro communication card SE7300 Series room controllers with RH
VCM7300T5045B BACnet communication card SER7300 Series room controllers
VCM7300V5045B BACnet communication card SE7200/SE7300 Series room controllers
VCM7300V5045P Wireless ZigBee Pro communication card SE7300 Series room controllers without RH
VCM7600V5045B BACnet communication card SE7600 Series room controllers
VCM7600V5045P Wireless ZigBee Pro communication card SE7600 Series room controllers without RH
VCM7607V5045B BACnet communication card SE76x7 room controllers (with RH options) 
VCM7607V5045P Wireless ZigBee Pro communication card SE7600 Series room controllers with RH
Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (3)
  • Find more articles tagged with:
  • 17814
  • se7xxx
  • ser7xxx
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore