Issue
In some situations, there is a network connection problem or PC power management issue that causes the b3 firmware update to be interrupted. When retrying the controller update, an error pops up: "The Infinity2 controller is currently being flashed or reloaded."
Resetting the controller and even doing a power cycle with the controller will not fix this problem.
Environment
BCX1
B3
Cyberstation
Warning
Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.
Cause
The update interruption may be because the b3 is busy.
Resolution
- Take the workstation offline
- Delete the b3 controller
- Reset BCX1 from the editor and reload BCX1
- Bring the b3 controller online
- Try to update firmware b3 again. It should be ok.