Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 467
    • 468
    • 469
    • …
    • 509
  • Next »

Can the I/A Series R2 ModbusAsync driver be configured to control minimum send time between Modbus messages to the bus?

Issue Can the I/A Series R2 ModbusAsync driver be configured to control minimum send time between Modbus messages to the bus? Environment I/A Series R2, Modbus Cause The Modbus device under control is unable to process messages at normal rates and requires a delay between messages received. Resolution The minimum send time between Modbus messages can be controlled by adding a parameter into the drivers.properties file. Note: Requires modbusAsync-2.302.514.v1 or higher. Open the UNC with the admin tool and go to the Installation tab. Edit the drivers.properties file. Add the property (shown below) on its own line within the file. Set the value the number of mSec of delay between messages. Save the file and reboot the station (remember to backup the station when requested). modbusAsync.minSendInterval=1000
View full article
Picard Product_Support
‎2018-09-06 10:24 AM

Labels:
  • TAC IA Series
934 Views

Importing a Menta application for a Xenta 301 controller into StruxureWare Building Operation for a second time, cannot be saved.

Issue Importing a Menta application for a Xenta 301 controller cannot be saved. Environment Xenta 301 importing Save Saving Cause Importing a Menta application for a Xenta 301 controller, and then saving it, works correctly. If the application is modified in some way, requiring a second import, then this import cannot be saved. Resolution This issue has been assigned to defect 22178, which is due to be fixed in release 1.5. Work around. Delete the existing controller object, and then create a new controller object before importing the modified Menta application.
View full article
Picard Product_Support
‎2018-09-06 10:16 AM

Labels:
  • EcoStruxure Building Operation
940 Views

If a 7716 is taken off the LAN what status light indicates LAN Reconfiguration

Issue If the 7716 is taken off the LAN what status light indicates LAN Reconfiguration? Environment I/NET Site Cause If the 7716 is taken off the LAN what status light indicates LAN Reconfiguration? Resolution Assuming the unit has not lost power, LED #7. It is Labeled "RECON"
View full article
Picard Product_Support
‎2018-09-06 03:17 PM

Labels:
  • TAC INET
941 Views

When a PDA is used to calibrate a MN-Sx sensor, the calibration offset value is stored in the controller. How can the value be preserved within the application drawing?

Issue When a PDA is used to calibrate a MN-Sx sensor, the calibration offset value is stored in the controller. How can the value be preserved within the application drawing? Environment PDA MN-Sx sensor Cause The offset is not stored as a nci so a “Read NCI Values” command will not preserve it. Resolution The calibration offset is a plus or minus temperature and / or humidity value. These values must be entered in the hardware wizard - sensor config area. Once entered, the values remain with the application drawing (make sure to re-download the controller).
View full article
Picard Product_Support
‎2018-09-06 02:50 PM

Labels:
  • TAC IA Series
958 Views

Error: LNS #81 lcaErrDbInvalidVersion

Issue The database has an invalid version. Note that LNS databases can be upgraded using the CompactDb method, but also note that LNS databases are not backwards compatible. Once updated to version N+1, the database will not be accessible for a version N client any more. Environment LonMaker NL220 Vista LNS Cause Invalid database version.  If you are running LonMaker 3.1 with a non-Turbo LNS Server and somebody who is running LonMaker 3.1 with a Turbo LNS Server has edited the database and sent you a backup, you will not be able to open the database until your PC has been upgraded. The global database is not open. (Subsystem: LNS, #64) and Invalid database version. (Subsystem: LNS, #81)[DB #-2038] errors occur if you try to open a database with an older version of LNS. Resolution Right click on the title bar of the design window and select About. This will tell you your LNS server version on the machine in question has. It must be the same or greater than the database you attempt to open.
View full article
Picard Product_Support
‎2018-09-06 02:21 PM

Labels:
  • TAC Vista
936 Views

Access Expert Extending Expiry Date

  Issue Extending a User/Cardholder Expiry Date Product Line EcoStruxure Access Expert Environment Access Expert Hosted V3 Cause Steps needed to Extend an Expiry date for a cardholder Resolution In Access Expert, there needs to be a way to extend cards that are about to expire after the default time has been entered initially. This can be done for single users or badge types depending on the circumstances. The following steps describe how this can be accomplished:   Open and log on to the Users instance Once opened, select Access Control and click on the List Tab then select View Expiring Cards A list will appear that shows all the cards that are about to expire based on the parameters entered When this list comes up, Select the Extend All button to bring up the Editor that will extend the time Enter the New Expiry Date that allows the card to function accordingly Click OK and the cards listed will then have the New Expiry Date listed    
View full article
Admiral Alan_Wood Admiral
‎2022-11-21 02:03 PM

on ‎2022-11-21 02:03 PM

Labels:
  • EcoStruxure Access Expert
997 Views

Unable to add a new user in a G3 (Niagara) ENC station accessed via web browser. There is no "New" tab displayed under the Services / UserService / right-click, User Ma...

Issue Unable to add a new user in a G3 (Niagara) ENC station accessed via web browser. There is no "New" tab displayed under the Services / UserService / right-click, User Manager page. Environment I/A Series ENC-520, ENC-410 Embedded Workbench feature, part number ENC-WB Cause The ability to add a user to the ENC via web browser requires the Embedded Workbench feature be enabled. Resolution To determine if the ENC has the Embedded Workbench feature enabled, open the Platform, License Manager, view the license, and the feature name = "web" ... ui.wb.admin = true indicates that the feature is enabled.  See the high-lighted lines in the screen capture below. If the feature is not enabled, it can be ordered and added to the ENC license.  
View full article
Picard Product_Support
‎2018-09-10 10:35 PM

Labels:
  • TAC IA Series
959 Views

Auxiliary switch for Forta series actuators

Issue Which aux switch is the correct for the Forta actuators? Environment Forta Auxiliary switch S2 8800104000 Cause The correct aux switch for Forta Resolution The correct auxiliary switch to be used with the Forta series actuators is the S2. Part no 8800104000.
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Labels:
  • Field Devices
944 Views

Why aren't the MSTP Devices coming in to SBO when upgrading site from Continuum?

Issue Some MSTP Devices show up when learned but other are not coming in. They worked fine on the Continuum install with the same MSTP network. Environment Automation Server Cause The AS has a maximum of 50 MSTP nodes and the b3 controllers that are not coming in are above this NodeId. Resolution Change the b3's NodeId's to a value below 50. 1. Use the Continuum system to change the Id by deleting the device object from the database, recreating it with the new NodeId. 2. Clear the controller to factory default.
View full article
Picard Product_Support
‎2018-09-06 09:54 AM

Labels:
  • EcoStruxure Building Operation
943 Views

ADAA problems: can not dial in or out of the site

Issue ADAA problems: can not dial in or out of the site A PCU is set up as a 06 TAP. The RX and TX LEDs are flashing on the RS-232 card. A CBL048 cable is connected from the RS-232 card to the modem. The RD and SD lights are flashing. Environment ADAA Cause The wrong BIN file is in the PCU. Resolution You have the wrong BIN file in the PCU. If the PCU is at the “Boot State”, you may have the wrong EPROM too. Install the correct BIN file; and it is strongly recommend to put in a compatible Asynchronous EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
951 Views

Where should I find the preprogrammed number for a key or card?

Issue Where should I find the preprogrammed number for a key or card? Environment I/NET Site with Access Control Cause Where should I find the preprogrammed number for a key or card? Resolution Typically it is printed or stamped on the device. However you may have to convert the listed value into a number the can be entered into INET. Refer to TCON 237.
View full article
Picard Product_Support
‎2018-09-06 11:10 PM

Labels:
  • TAC INET
934 Views

Convert the hexadecimal value of a key/card for an older I/NET system

Issue I need to convert the hexadecimal value of a key/card for an older I/NET system. Is there a TCON or any documentation on how to do this? Environment I/NET Site Cause I need to convert the hexadecimal value of a key/card for an older I/NET system. Is there a TCON or any documentation on how to do this? Resolution Refer to TCON 237. Most calculators can convert decimal and hexadecimal. Windows also has this feature in the on-screen calculator.
View full article
Picard Product_Support
‎2018-09-06 11:59 PM

Labels:
  • TAC INET
960 Views

Send out the system date and time as a SNVT_Time_stamp

Issue Send out the system date and time as a SNVT_Time_stamp Environment Time Stamp SNVT type Xenta 511 Cause Send out the system time properties to monitor externally and make sure the time is synchronized. Resolution You can do this by creating signals in the system window for the system variable year, month, day, hour, minute and second. Create an nvo SNVT_time_stamp in the Xenta 511. Create connection objects and connect the signals with the members of the SNVT. Note, you have to change the category and the unit for hour, minute and second to match the SNVT.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Labels:
  • TAC Vista
932 Views

Equalization not working on a File Master and Client

Issue Equalization not working on a File Master and Client Are you having an issue where you have a File Master and several Clients but cannot get Equalization to work? It looks like the snapshot gets delivered but the File Master’s Icon stays red and the client never gets the database.  Environment I/NET Cause SQL services may not be running properly. Resolution There are a few possibilities that could be the cause of this not working. Verify that MSSQLSERVER and SQLSERVERAGENT are set for Automatic and Local Machine in Services. Verify that the file C:\Program Files\Microsoft SQL Server\MSSQL\Data\InetDbSnapshot.mdf already exists but is not a registered database on the file master. See note below. Go to the FM; delete C:\Program Files\Microsoft SQL Server\MSSQL\Data\InetDbSnapshot.mdf and InetDbSnapshot_Log.ldf. Set all PCs to Stand Alone; re-promote the File Master and then the clients again. Note: This is an existing file that SQL uses, if you can rename it, it means that the existing one is not being used and therefore cannot be created by SQL again. If you cannot rename this file then this is not your issue.
View full article
Picard Product_Support
‎2018-09-06 03:04 PM

Labels:
  • TAC INET
959 Views

How do you reset the passwords in a MicroNet View project

Issue Lost or unknown access password for Micronet View.  Environment Global  Cause Lost user password for Micronet View Resolution Back up the MicroNet View project before carrying out the following: Take a copy of the default password file from MicroNet View default project1 Copy the password file from C:\MicroNet\Projects\Project1\View\password.bin Paste this file into Your project. C:\MicroNet\Projects\YourProjectName\View\password.bin
View full article
Picard Product_Support
‎2018-09-06 01:18 PM

Labels:
  • Satchwell MicroNet
939 Views

Sigma - Short Text not displaying correctly

Issue Sigma - Short Text displaying correctly on local client but not displaying on the remote client Environment Sigma Version 4 releases Cause In version 4 Sigma the short text file is located in C:/Sigma/Data/Locality/English United_Kingdom (IF UK)/ This folder location is set by the regional settings of the PC. If there is a difference between the Sigma Client and Sigma Server then if new short text entries are added they can display on some clients but not on others. An example of this would be if the server is set to UK locale then any short text added via the local client would appear in the UK short text folder. If you then have a remote client with the locale set to US then it will read the short text from the US short text folder which will not have the correct entry. Result will be an incorrect object display. Resolution Check the Regional Settings for all Sigma PC's installed on the system. For Windows XP and Server 2003 go to Control Panel>Regional and Language Options. On the first tab make sure the Standards and Formats and Location are set to the correct location. On the third tab Advanced make sure the Language for non-Unicode programs is set to the correct location. For Windows 7 and Server 2008 go to Control Panel>Region and Language. On the first tab Formats make sure the Format is set to the correct location. On the second tab Location check the location is set to the correct location. On the last tab Administrative make sure the current language for non-Unicode programs is set to the correct location. In summary all Sigma machines connected to each other need to be set using the same regional settings
View full article
Picard Product_Support
‎2018-09-06 12:37 PM

Labels:
  • Satchwell BAS & Sigma
949 Views

Schedule Import will not update.

Issue Schedule Import will not update. Environment G3 Niagara Cause Schedule import defaults to Manual update this will prevent the schedule from automatically.. Resolution Schedule execution time can be set to daily, days of week, interval and manual.  Please consult Doc Drivers document.  
View full article
Picard Product_Support
‎2018-09-06 12:17 PM

Labels:
  • TAC IA Series
936 Views

Do I need a HHC to set up a 7798 (SLI) (ISITE)?

Issue Do I need a Handheld Console (HHC) to set up a 7798 (SLI) (ISITE)? Environment 7798 SLI ISITE Cause The 7798 does not have ports for a HHC. Resolution No. In fact, the 7798 does not have ports for a HHC. The 7798 is setup using its touch pad. Refer to 7798 TCONs for more details.
View full article
Picard Product_Support
‎2018-09-06 09:22 PM

Labels:
  • TAC INET
961 Views

How can BACnet objects be learned as "full" objects and not "lite" objects in a Niagara R2?

Issue How can BACnet objects be learned as "full" objects and not "lite" objects in Niagara R2? Environment Niagara R2 Cause "Use lite objects" is enabled and need to be disable (uncheck the box) "Use Lite Objects" setting using BACnet Utilities. Resolution From the BACnet Utilities window, when performing either a "network - learnNetwork" or "device - learnDevice" command, clicking the Execute button will generate a pop-up window. In this window, uncheck "Use lite objects", and click OK to proceed.
View full article
Picard Product_Support
‎2018-09-06 02:53 PM

Labels:
  • TAC IA Series
937 Views

Resolve duplicate node addresses in a Niagara R2 UNC station running the LonWorks Service

Issue In a Niagara R2 UNC station, running the LonWorks Service, there are duplicate node addresses. How can they be resolved? Environment Niagara R2 UNC Cause Duplicate subnet-node address conflicts abort the learn process. Follow the instruction in the resolution to apply unique addressing to learned devices. Resolution There are two ways: Change the subnet/node address(es) of the "duplicate" device(s) already in the station. Now, when a Learn function is performed, the newly learned node(s) addresses will not conflict with existing ones. Set the "duplicate" node(s) in the station to unconfigured. Then do a Learn function and ignore unconfigured devices. The unconfigured node(s) need their shadow object(s) copied manually into the station and then Matched / Commissioned using the Device Manager. For more details, see the Niagara LonWorks Integration Guide, page A-1 to A-3.
View full article
Picard Product_Support
‎2018-09-06 02:50 PM

Labels:
  • TAC IA Series
954 Views
  • « Previous
    • 1
    • …
    • 467
    • 468
    • 469
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of