When a PDA is used to calibrate a MN-Sx sensor, the calibration offset value is stored in the controller. How can the value be preserved within the application drawing?
  • When a PDA is used to calibrate a MN-Sx sensor, the calibration offset value is stored in the controller. How can the value b...
  • sesa119747
    sesa119747
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 02:50 PM
  • PDA
  • MN-Sx sensor
The offset is not stored as a nci so a “Read NCI Values” command will not preserve it.
The calibration offset is a plus or minus temperature and / or humidity value. These values must be entered in the hardware wizard - sensor config area. Once entered, the values remain with the application drawing (make sure to re-download the controller).