Can the I/A Series R2 ModbusAsync driver be configured to control minimum send time between Modbus messages to the bus?
  • Can the I/A Series R2 ModbusAsync driver be configured to control minimum send time between Modbus messages to the bus?
  • WaynePeters
    WaynePeters
‎2018-09-06 10:24 AM
I/A Series R2, Modbus
The Modbus device under control is unable to process messages at normal rates and requires a delay between messages received.
The minimum send time between Modbus messages can be controlled by adding a parameter into the drivers.properties file. Note: Requires modbusAsync-2.302.514.v1 or higher.
  1. Open the UNC with the admin tool and go to the Installation tab.
  2. Edit the drivers.properties file.
  3. Add the property (shown below) on its own line within the file.
  4. Set the value the number of mSec of delay between messages.
  5. Save the file and reboot the station (remember to backup the station when requested).
modbusAsync.minSendInterval=1000