Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 468
    • 469
    • 470
    • …
    • 509
  • Next »

When using the PSI software, the Current Status Screen, All Points History and the graphic data display screens do not properly display the text shown on that screen.

Issue When using the PSI software, the Current Status Screen, All Points History and the graphic data display screens do not properly display the text shown on that screen. Environment PSI software Computer Cause The video bios in the computer does not support the graphics mode used by the graphic displays of the PSI software products. Resolution This problem was first identified several years ago on some models of Gateway brand laptop computers. The problem has been observed from time to time, since then, on various computer makes and models. The problem affects both the "Current Status" screen, the "All Points History" screen and the graphic display screens for analog I/O points. There is no software workaround for the problem. The best solution for this problem is to evaluate the computer model before purchasing any quantity of them. Download test program vga_test on The Exchange Download Center, which allows testing of the computer without having to load the PSI software. The test program can be run from any removable media (diskette, CD, memory-stick, etc.) so the computer can be tested at the computer dealer's store or sales office. The text file included in the zip file explains how to run the test and how to interpret the results.
View full article
Picard Product_Support
‎2018-09-07 01:56 AM

Labels:
  • TAC IA Series
958 Views

Bacnet Schedules stopped working due to "Effective To Date"

Issue Bacnet Schedules stopped working due to "Effective To Date" Environment Bacnet Schedules Cause When creating a bacnet schedule on a bacnet controller the default "Effective To Date" is one year from the creation time. Bacnet schedules will stop working if the bacnet schedule exceeds the "Effective To Date." Resolution Always consider the "Effective To Date" when creating Bacnet schedules.
View full article
Picard Product_Support
‎2018-09-06 02:43 PM

Labels:
  • Andover Continuum
947 Views

Interpreting the Device Alarms from a b0warlog.log file

Issue How can I tell what device the alarm is coming from in the b0warlog.log file? The  b0warlog.log or "Warning Log" file does not reference individual devices therefore is difficult to see where the alarm happened. Environment Vista Alarms Cause A lot of  warnings are due to a mismatch in the Vista database and a device on the field. For instance, if you have a Xenta Server alarm that doesn't exist in the Vista database. Resolution You could see if the Xenta/Xenta Server is marked in Vista, look for the asterisk (*), to give you a clue where it came from.   An alternative way to do it is to use testclt program: Start testclt.exe from the root directory of you Vista installation. Login Go to File-Dbg Write alrproc Click Add Choose the Time radio button Click Poke Click Close Wait for the warning to happen in the b0warlog.log Open b0dbglog.logfile in notepad and search for "your error" Just above the line found you should see which alarm object that sent the alarm Example: (Searching for Error:81) Tue Nov 23 13:26:02 2010 :alrproc  >> ProcessAlarmEvent EventId:TGML_test-731-Lon-XG-Xenta401-$NETMON.offline EventType:1 Pri:9 Txt:Xenta group offline Tue Nov 23 13:26:02 2010 :alrproc  >> ValidateDataSpec Id:TGML_test-731-Lon-XG-Xenta401-$NETMON ObjType:EE_MESS Tue Nov 23 13:26:02 2010 :alrproc  >> Processed Error:81  
View full article
Picard Product_Support
‎2018-09-06 02:22 PM

Labels:
  • TAC Vista
940 Views

Current consumption specification SLO320/SLR320

Issue Unclear information in data sheet Environment SLO320 006920640 SLR320 006920630 Cause During the Schneider Electric data sheet rebranding process, the Current consumption information got unclear. Resolution Current consumption should say: Typical: 0-400lx: 8mA 0-20klx: 13mA
View full article
Picard Product_Support
‎2018-09-06 12:29 PM

Labels:
  • Field Devices
940 Views

Issue showing all BACnet devices in a Search

Issue The "BACnet device proxy base" type is missing in the Search type after EBO 4.0 Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Workstation Building Operation Enterprise Server Building Operation Automation Server Building Operation SmartX Living Space Sensor BACnet B3 IA SE8000 VT8000 Cause The "BACnet device proxy base" was removed from EBO 5.x and later. Resolution To search for a specific type, add individual type to "Include types" For example 'BACnet device' will return all 3rd party (generic) BACnet devices. 'SpaceLogic Series Device' will return all MP and RP devices. Sample Search all BACnet devices(excluding AS/ES) XML attached
View full article
Admiral StephenYang Admiral
‎2024-06-19 11:42 AM

on ‎2024-06-19 11:42 AM

Labels:
  • EcoStruxure Building Operation
1060 Views

In what positions can Continuum controllers be mounted?

Issue In what positions can Continuum controllers be mounted? Environment Continuum Product Line Cause Not sure if the controllers can be mounted on both the vertical and horizontal plane. Resolution There may be some specific mounting instructions for some of the controllers, but for the most part they can be mounted in any direction in the vertical plane. Controllers with relays should not be mounted with the edge the outputs are on facing down. Consult the installation instructions (found here) for each controller for any specific mounting requirements.
View full article
Picard Product_Support
‎2018-09-11 08:33 AM

Labels:
  • Andover Continuum
945 Views

Site has I/NET 2000 PCU set as an 06 TAP for ADAA, and PCU has a synchronous EPROM and ASYNCHRONOUS BIN file loaded

Issue Site has I/NET 2000 PCU set as an 06 TAP for ADAA, and PCU has a synchronous EPROM and ASYNCHRONOUS BIN file loaded Environment I/NET site Cause Should the site change the EPROM? Resolution We strongly recommend you do. If the PCU goes to “Boot-State”, the SYNCHRONOUS EPROM in the PCU will not reset the asynchronous ADAA modem correctly. You won’t be able to dial into the ADAA port of this controller until this is corrected by doing a download or changing the EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
950 Views

How many messages are buffered on a 7801?

Issue How many messages are buffered on a 7801? Environment I/NET Seven 7801x, 7803x, 7804x External or Embedded TAPs. Cause Even though every device in the system contains a message queue, only a few of the devices will successfully buffer the queued messages for later distribution. All controllers and Taps distribute messages out of their RS485 port even with the absence of any LAN communication. This is due to the fact that there is no requirement for an acknowledgment to be received at the generating device. The RS485 LAN is for both solicited and unsolicited message traffic. The only devices that perform extended buffering are the ones which directly communicate to polling devices such as the 7801 Taps, 7803 Taps, 7804 Taps, and all DPUs/SCUs. The MRs, ASCs, and UCs do not generate messages; messages relating to these devices are generated by the relevant MRI, MCI, etc. Resolution A 78-01/03/04/06 EPROM tap can buffer approximately 1000 messages. A 78-01/03/04/06 MIP tap can buffer approximately 1200 messages.
View full article
Picard Product_Support
‎2018-09-06 03:16 PM

Labels:
  • TAC INET
944 Views

Using Russian language with I/NET

Issue Using Russian language with I/NET Environment I/NET foreign language translations Cause I/NET (with SQL) that is installed on an English operating system will not be able to display Russian alphabet characters if regional settings are later changed to Russian. Resolution To avoid this problem, change the regional settings before the installation I/NET and SQL.
View full article
Picard Product_Support
‎2018-09-06 02:34 PM

Labels:
  • TAC INET
935 Views

DPU & SCU Memory Failure Message

Issue A memory failure message in AMT for a DPU or SCU Controller When presenting a valid key card to a door reader, the LED on the SCU turns Green but the relay does not fire.  The relay can be controlled manually via the workstation in some instances. Environment I/NET Door Controllers  Cause This memory failure message is generated when the DPUs or SCUs do not have sufficient voltage supplied to the board. This can either be a bad 24 VAC Transformer or from a gel cell battery. In most cases if there is a battery backup of the controller, the gel cell battery has had a deep discharge applied to it. The charging circuit on the controller cannot recover the battery to its proper charge value. Even if there is a good voltage value from the transformer, the charging circuit load is so great, it restricts the main board of the necessary voltage to keep the RAM alive. Resolution Remove the two wires from the controller that go to the gel cell battery. Get a replacement battery as soon as possible.
View full article
Picard Product_Support
‎2018-09-06 12:54 PM

Labels:
  • TAC INET
959 Views

How can the default graphic for the Monitor Screens be modified in SIGNAL?

Issue How can the default graphic for the Monitor Screens be modified in SIGNAL? Environment SIGNAL (all versions) Cause A re-installation of SIGNAL from floppy restores a default graphic called _MAINMAP.SSF when clicking on the Monitor Screens. Resolution Sign onto SIGNAL with administrative privileges and click on the Edit drop-down menu.  Select Edit Button. The mouse changes to a hand with an index finger pointer.  Select the Monitor button.  The pop-up below will appear:   Change the filename _MAINMAP.SSF to the desired ssf file and click Save/Done.
View full article
Picard Product_Support
‎2018-09-06 12:57 PM

Labels:
  • TAC IA Series
938 Views

How to filter a list view to only show certain entries?

Issue When opening one of the pre defined list views there are many entries and can not find text required. Environment List views Filter, Qualifier, Query Wizard, Wildcard. Cause Default list views show all entries, how to define a qualifier to only show required data? Resolution Create a new list view and define the Class and path, add in the required columns. In the Qualifier tab select the "Query Wizard", for text comparisons use the required attribute e.g. Description, and "Is Like" as the Operator, enter the comparison text between wild card * characters (e.g. *Test* for the objects which contain the word Test) and it will filter only on objects whose attribute contain that text.
View full article
Picard Product_Support
‎2018-09-06 12:41 PM

Labels:
  • Andover Continuum
936 Views

Sigma IC's - Is it possible to convert a Sigma IC-Unifact IC to an IC-SNP?

Issue Converting a IC type. Environment IC IC3 Type Converting Cause The customer has purchased the incorrect type of IC and wishes to convert it. Resolution An IC / IC3 has a personality built into it, therefore if you were to change the IC / IC3 firmware, it would still not work, as the personality and firmware would not match.  
View full article
Picard Product_Support
‎2018-09-06 11:13 AM

Labels:
  • Satchwell BAS & Sigma
953 Views

Can ClimateMaster Controllers be integrated with StruxureWare Building Operation?

Issue ClimateMaster controllers are an OEM version(s) of the I/A MNL LON controllers and can only be added as third party devices in SmartStruxure.   Environment ClimateMaster controllers SmartStruxure Cause ClimateMaster is a channel locked product and will not permit  WorkPlaceTech or WorkPlace Tech Editor to have access to the application via upload or download. Resolution ClimateMaster controllers can only be added as third party devices. For help on adding third party devices consult the StruxureWare Building Operation Web Help. There are three web help topics on adding third party devices: Enterprise Server Automation Server Third-Party Licenses
View full article
Picard Product_Support
‎2018-09-06 12:02 PM

Labels:
  • EcoStruxure Building Operation
963 Views

How to monitor if equipment is running without running cables to additional sensors

Issue How to monitor if equipment is running without running cables to additional sensors Environment Current Sensor switch Cause Running cables to and fitting sensors can be time consuming and expensive, are there other ways to monitor equipment? Resolution The current drawn by equipment can be monitored within a control panel using the Current Sensor devices.   This method of monitoring equipment will not replace other monitor methods, but will be suitable for some projects - Detecting belt loss, coupling shear and mechanical failures - Evaluating lighting circuit and other electrical service run times - Monitoring status of critical electrical equipment - Choose from Switch, 0-5VDC, 0-10VDC and 4-20mA     Information on current sensos can be downloaded from the Schneider Electric Exchange Extranet. Click here to be linked to applicable area.
View full article
Picard Product_Support
‎2018-09-11 04:04 AM

Labels:
  • Field Devices
935 Views

A MicroSmart controller is not communicating and the red watchdog timer (WDT) LED is on solid.

Issue A MicroSmart controller is not communicating and the red watchdog timer (WDT) LED is on solid. Environment DMS Cause Possible hardware issue or power issue Resolution Things to try: - Power cycle the controller - Verify it has a good earth ground and 24 Vac - Hardware clear the controller - Replace the line driver and disconnect the communications trunk - If it is a MSC-MPC, remove all modules.  If the WDT LED begins flashing normally, re-connect the modules one at a time until the WDT LED goes solid   On-board hardware issue.  Replace with another controller
View full article
Picard Product_Support
‎2018-09-06 10:16 AM

Labels:
  • TAC IA Series
957 Views

Output relays on a 7780 will not energize

Issue Why won't the output relays on a 7780 energize? Environment 7780 Output Relays Cause If the fuse in F2 has blown, the output relays will not energize. Resolution Verify that fuse F2 is not open.
View full article
Picard Product_Support
‎2018-09-06 03:14 PM

Labels:
  • TAC INET
937 Views

When attempting to bind to SNVTs from a LON Field Server device a service_type_error appears.

Issue When attempting to bind to SNVTs from a LON Field Server device a service_type_error appears. Environment Field Server UNC network management tool Cause The UNC network management for bindings is set to the "standard" service type (Unacknowledged) by default. Resolution The Field Server device requires something other than the "Unacknowledged" service type. Either change the Field Server service type to Unacknowledged or change the default service type in the UNC network management tool to match their type. Review the Niagara LonWorks Integration Guide for more details.
View full article
Picard Product_Support
‎2018-09-06 02:48 PM

Labels:
  • TAC IA Series
934 Views

How to open a graphic panel from a Plain English program?

Issue A Graphic panel or other object needs to be opened by a Plain English program on Cyberstation, what command can be used? Environment Cyberstation Plain English Programs Cause It is often not clear what Plain English keyword can be used to open a Graphic Panel, or other object. Resolution The "Show" command can be used to open a graphic from Plain English For example: Show AirHandler1 This will open a graphic called AirHandler1, enter Show in the online help search for further examples.  
View full article
Picard Product_Support
‎2018-09-06 12:53 PM

Labels:
  • Andover Continuum
946 Views

Vista - No right to create or modify root object as admin

Issue Access denied Environment Vista Admin Root Cause If Vista user Everyone has no rights no user in the system will be able to add or modify root objects. Also, if the Vista server (or one of the Vista servers) is owned by someone else (eg. not $Administrators) you will get the same error. Resolution Change the user Everyone's rights to at least "read" In Vista right click Vista database Right click and choose authority Make sure the user Everyone at least have read right    If the Vista server is owned by someone else then $Administrator       1. Login as a user that belongs to the group $Administrator        2. Right click on the Vista database and choose authority       3. Click on take ownership
View full article
Picard Product_Support
‎2018-09-06 12:25 PM

Labels:
  • TAC Vista
937 Views
  • « Previous
    • 1
    • …
    • 468
    • 469
    • 470
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of