A MicroSmart controller is not communicating and the red watchdog timer (WDT) LED is on solid.
  • A MicroSmart controller is not communicating and the red watchdog timer (WDT) LED is on solid.
  • Leo_Tantalo
    Leo_Tantalo
‎2018-09-06 10:16 AM
DMS
Possible hardware issue or power issue
Things to try:
- Power cycle the controller
- Verify it has a good earth ground and 24 Vac
- Hardware clear the controller
- Replace the line driver and disconnect the communications trunk
- If it is a MSC-MPC, remove all modules.  If the WDT LED begins flashing normally, re-connect the modules one at a time until the WDT LED goes solid
On-board hardware issue.  Replace with another controller