Issue
When attempting to bind to SNVTs from a LON Field Server device a service_type_error appears.
Environment
- Field Server
- UNC network management tool
Cause
The UNC network management for bindings is set to the "standard" service type (Unacknowledged) by default.
Resolution
The Field Server device requires something other than the "Unacknowledged" service type. Either change the Field Server service type to Unacknowledged or change the default service type in the UNC network management tool to match their type.
Review the Niagara LonWorks Integration Guide for more details.