Interpreting the Device Alarms from a b0warlog.log file

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Interpreting the Device Alarms from a b0warlog.log file
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1115 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Interpreting the Device Alarms from a b0warlog.log file

Picard Product_Support
‎2018-09-06 02:22 PM

Issue

How can I tell what device the alarm is coming from in the b0warlog.log file?

The  b0warlog.log or "Warning Log" file does not reference individual devices therefore is difficult to see where the alarm happened.

Environment

Vista

Alarms

Cause

A lot of  warnings are due to a mismatch in the Vista database and a device on the field. For instance, if you have a Xenta Server alarm that doesn't exist in the Vista database.

Resolution

You could see if the Xenta/Xenta Server is marked in Vista, look for the asterisk (*), to give you a clue where it came from.
 
An alternative way to do it is to use testclt program:

  1. Start testclt.exe from the root directory of you Vista installation.
  2. Login
  3. Go to File-Dbg
  4. Write alrproc
  5. Click Add
  6. Choose the Time radio button
  7. Click Poke
  8. Click Close
  9. Wait for the warning to happen in the b0warlog.log
  10. Open b0dbglog.logfile in notepad and search for "your error"

Just above the line found you should see which alarm object that sent the alarm
Example: (Searching for Error:81)
Tue Nov 23 13:26:02 2010 :alrproc  >> ProcessAlarmEvent EventId:TGML_test-731-Lon-XG-Xenta401-$NETMON.offline EventType:1 Pri:9 Txt:Xenta group offline
Tue Nov 23 13:26:02 2010 :alrproc  >> ValidateDataSpec Id:TGML_test-731-Lon-XG-Xenta401-$NETMON ObjType:EE_MESS
Tue Nov 23 13:26:02 2010 :alrproc  >> Processed Error:81
 

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4138
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore