Issue
Some MSTP Devices show up when learned but other are not coming in. They worked fine on the Continuum install with the same MSTP network.
Environment
Automation Server
Cause
The AS has a maximum of 50 MSTP nodes and the b3 controllers that are not coming in are above this NodeId.
Resolution
Change the b3's NodeId's to a value below 50.
1. Use the Continuum system to change the Id by deleting the device object from the database, recreating it with the new NodeId.
2. Clear the controller to factory default.