Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,848
  • TAC IA Series 1,824
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 331
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 15
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 8
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 38
    • 39
    • 40
    • …
    • 508
  • Next »

Moving an Energy Expert database to a new server

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue An Energy Expert system is being moved to a new server and/or the virtual image is being upgraded. The historical records held in the SQL database of the Power Monitoring Expert (PME) system need to be backed up and properly restored on to the new server. Product Line EcoStruxure Building Operation Environment EcoStruxure Energy Expert (formally Power Manager) Power Monitoring Expert (PME) Enterprise Server Cause The system administrator has deemed it necessary to upgrade the Windows server that the Energy Expert system is installed on for security and/or resource reasons. Resolution It is important to remember that an Energy Expert installation is really just two Schneider Electric offers, EcoStruxure Building Operation and Power Monitoring Expert, installed together and set up to pass information back and forth. This means that appropriate steps must be followed for each system to backup the historical data and properly restore it on the new server. For more detail regarding how the system is laid out, please see the Difference between EcoStruxure Energy Expert (Power Manager) and Power Monitoring Expert (PME). Steps to move an Energy Expert database Backup the Power Monitoring Expert (PME) SQL database, dashboards and reports. The Configuration Manager tool available on the Exchange can be used to back all of these items up automatically. Run the tool on the existing server and it will create a zip file to be used later on when restoring to the new server. See Migrating a PME 8.0 System to a New Server for more information. The Schneider Electric Technical FAQs website also contains many other helpful troubleshooting articles for PME including different versions of the product. Return the Energy Expert license(s) from the Floating License manager in order to move them to the new server. For more information see Video: Licensing Guide for Power Monitoring Expert (PME) 8.x and 7.2.x and ENM 8.3.x. If moving the Enterprise Server, make a historical backup of the EcoStruxure Building Operation (EBO) ES from the existing server. See Backup of StruxureWare/EcoStruxure Building Operation AS and ES for more information. If the Enterprise Server and other EBO licenses are installed on the existing server, then they may need to be returned as well so they can be moved to the new server. See Removing a Local License or Returning a Network License for more information. Next the ETL project files must be retrieved and saved so they can be moved to the new server (if using architecture 1 in the Energy Expert offer). Go to the file location below and save all ETL project files that are needed on the new server. C:\Program Files > Schneider Electric > ETL X.X (SBO to PME) > Jobs If moving the Enterprise Server, install the EBO software on the new server, rehost the EBO licenses, and restore the EBO server backup(s). See Restoring the EcoStruxure BMS Server for more information. Install the Energy Expert software (the software includes PME, ETL and the integration utility). The information on how to download the Energy Expert software can be found on the Exchange. Once the software has been installed, the Energy Expert license can be hosted to the new server in the Floating License manager. Next, install the PME Configuration Manager tool on the new server. The zip file from step 1 can be loaded using this tool to restore the SQL database, PME dashboards and PME reports. Add the previously saved ETL project files to the same location on the new server C:\Program Files > Schneider Electric > ETL X.X (SBO to PME) > Jobs Since the server has changed, the configuration settings must be updated in the ETL projects to reflect the new server name. The settings in the EWS interface on the EBO server will also need to be updated as well. Note: It may be easier to delete the existing EWS interface in EBO and then use the integration utility to create a new XML import file to simply rebuild the interface.
View full article
Administrator Cody_Failinger Administrator
‎2018-10-30 11:24 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:57 PM

Labels:
  • EcoStruxure Building Operation
3404 Views

Accessing Continuum Security Key information using MMC instead of Excel

Issue Accessing Continuum Security Key information using MMC to determine what features are enabled. Product Line Andover Continuum Environment Continuum Security Key Cause Users need the ability to know what version of Continuum is supported on their key Resolution Note: The MMC method for viewing enabled key features mentioned below no longer works with Windows10 or greater and because of CyberSecurity issues ActiveX controls have been deprecated by Microsoft in favor of more secure web technologies.  This feature will not be updated for Cyberstation.   Some Cyberstations do not have Microsoft Office with Excel installed but the security key information may be accessed using Microsoft Management Console instead. Go to Start> Run, Type in MMC.exe and click OK Select File> Add/Remove Snap-in Click the Add button (bottom left) Click On ActiveX control and click Add Click Next while in the Insert ActiveX Control dialog Scroll Down until you find SecurityKeyReader Control and highlight it and click Next Leave the default name and click Finish Close the Stand Alone Snap-in dialog Click OK on the Add/Remove Snap-in dialog Click on the SecurityKeyReader Control and highlight it and it will display the Key info If you want to save it, File> Save and enter the name SecurityKey.msc Windows 7  (32-bit system) Go to Start> Run, Type in MMC.exe and click OK (64-bit system) In Command Prompt  enter  mmc /32 Select File> Add/Remove Snap-in Click On ActiveX control and click Add Click Next while in the Insert ActiveX Control dialog Scroll Down until you find SecurityKeyReader Control and highlight it and click Next Leave the default name and click Finish Click OK in the Add or Remove Snap-in dialog Double click on the SecurityKeyReader Control in the right-hand pane and it will display the Key info If you want to save it File> Save and enter the name SecurityKey.msc To reopen Go to Start> Run, Type in MMC.exe and click OK File> Open and select Ex. SecurityKey.msc To copy to another computer File Search> Enter SecurityKey.msc (or whatever you named it above) Copy the file to the other computer and paste it into the Administrative Tools folder Ex. C:\Documents and Settings\Administrator\Start Menu\Programs\Administrative Tools  
View full article
Picard Product_Support
‎2018-09-06 02:52 PM

Last Updated: Admiral Alan_Wood Admiral ‎2022-04-14 07:18 AM

Labels:
  • Andover Continuum
3424 Views

"Database upgrade failed!" when attempting to upgrade a Server database from 1.7.x to 1.8.1

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support Services for assistance. Issue While upgrading a database from 1.7.1 to 1.8.1 that has already been prepared, the upgrade log states that a MAP file is missing (similar to one shown below), and the upgrade is cancelled and reports "Database upgrade failed!" MAP file is required for upgrading the type public.lon2.devicetemplates.pidxxxxxxxxxxxxxxxx but none could be found Product Line EcoStruxure Building Operation Environment Upgrade LonWorks Pre-upgrade add-on Observed in version 1.7.1 and 1.7.2 Cause At some point in a previous version of StruxureWare Building Operation, the import of a device template has gone wrong in the sense, that the XIF has been imported and parsed correctly, but stored incorrectly. That means that we have cases where the actual content of the XIF stored in the database, can either be another completely different XIF, or even in some cases just random files. The issue can be verified by performing a "Content Analysis" using the "SBO xbk Analyzer" version 1.0.9 and above. You'll get a message like this: Error in XIF file: Mismatching program ID (SBO: 90001347000604A0 - XIF: 90:00:13:47:00:06:04:3C) This means that Building Operation has a device template with PID 90:00:13:47:00:06:04:A0 but that the actual file this device template points to is 90:00:13:47:00:06:04:3C Resolution A hotfix has been produced to allow replacing the wrong XIF with the correct one. With the following procedure you can manually fix the issue if you don't have the hotfix: Firstly ensure you have run the Pre-Lonworks upgrade configuration and try the upgrade again. Check if the template is in use by searching the specific template while logged in directly to the server Once the device has been identified, proceed with the following steps: Record Neuron ID(s) - this is required since the Export Process does not retain this information. Export device(s) If you have multiple devices you can Export the folder containing these devices, it is not critical to export the devices individually. Delete device(s) remembering to keep references. Import latest XIF for device From WorkStation select: File > LonWorks > Device Template Browse in the correct XIF. Import exported device(s) in step 2 Commission device(s) Run the Pre-Lonworks upgrade configuration The database should now successfully upgrade.
View full article
Picard Product_Support
‎2018-09-11 06:50 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:48 PM

Labels:
  • EcoStruxure Building Operation
3412 Views

Virtual USB Dongle, AnywhereUSB

Issue Using Sigma with a Virtual USB Dongle / Virtual USB Dongle / AnywhereUSB Product Line Satchwell Sigma Environment Sigma 4.05 SP2 Sigma 4.05 SEB Windows XP Windows 7 AnywhereUSB/5 Gen 2 Cause The requirement for the Sigma dongle to be installed remote from the Sigma server PC. Resolution 1. Install AnywhereUSB hardware. 2. Follow AnywhereUSB manufacturer's instructions and install device software and drivers on PC where Sigma Server is to be installed and assign a static IP address. 3. Install Sigma dongle. 4. Install Sigma software if not already installed and run. Download manufacturers datasheet http://www.digi.com/pdf/prd_usb_anywhereusb.pdf Download manufactures manual https://www.digi.com/resources/documentation/digidocs/PDFs/90001085.pdf   Schneider Electric can now provide a software license in replacement for the Sigma dongle. See knowledge base article Sigma parallel port dongle or USB dongle upgrade to SBO/EBO software license exchange, for more information.  
View full article
Picard Product_Support
‎2018-09-07 04:30 AM

Last Updated: Gary Schneider Alumni (Retired) ‎2022-08-24 06:56 AM

Labels:
  • Satchwell BAS & Sigma
3423 Views

How to configure universal input for SE8000

Issue Unable to configure universal input from the thermostat Product Line EcoStruxure Building Expert Environment SE8000 Cause Universal inputs aren’t configurable at the thermostat Resolution There are two ways to configure inputs on SE8000; More often is via a BACnet front end and secondly is via a Lua script. The input shall be configured to Priority 3. SE8000 INPUTS: •       UI16 fixed as binary input •       UI17 fixed as binary input •       UI19 configurable as temperature sensor, binary input or 0 -10 VDC input •       UI20 configurable as temperature sensor •       UI22 configurable as temperature sensor •       UI23 configurable as temperature sensor •       UI24 configurable as temperature sensor, binary input or 0 -10 VDC input   For example UI19 configuration: UI19 LUA AnalogValue:202 ; this point is to write a Lua via Bacnet for UI19. LUA:  if not init then ME.MV6 = 2 -- set network units to imperial ME.MV145 = 2 -- room temp local ME.AV25_Desc = "UI19 TEMP" -- UI19 Present Value ME.AV26_Desc = "UI20 TEMP" -- UI20 Present Value ME.MV140 = 1 -- UI19 thermistor ME.MV141 = 1 -- UI20 thermistor init = true end ME.AV25 = ME.AV104 ME.AV26 = ME.AV105 ME.AV100_PV[16] = (ME.AV104 + ME.AV105) / 2 -- average UI20 remote sensor and UI19 remote sensor
View full article
Picard Product_Support
‎2018-09-10 10:25 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 11:22 PM

Labels:
  • EcoStruxure Building Expert
3463 Views

Download LonMark SNVT Master List, SNVT Enumerations, and XIF File Reference Guide

Issue Download LonMark SNVT Master List, SNVT Enumerations, and XIF File Reference Guide Product Line TAC IA Series, TAC Vista, EcoStruxure Building Operation Environment LNS SNVT types Cause Investigating problems with LON integrations can sometimes involve inspecting the raw XIF file for different SNVT types or enumeration values. These documents from LonMark detail the LON protocol for SNVT communication and device interface file syntax. Resolution LonMark SNVTs & SCPTs Introduction LonMark SNVT Master List LonMark SCPT Master List LonMark Standard Enumeration Master List LonMark Device Interface File (XIF) Reference Guide To check for updated information, please visit LonMark International's Developers Guides.
View full article
Picard Product_Support
‎2018-09-10 04:58 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-02-11 10:56 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
3418 Views

Software Support for Design 360 and Studio 360

Issue Technical support contact information for Design 360 and Studio 360 Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Design 360 Studio 360 Cause Design 360 or Studio 360 has issues requiring technical support assistance which is not provided by PSS. Resolution Schneider Electric Employees should contact PSS who will provide you with your Branch Administrator and Technical Expert contact information. Partners may contact Smartware directly for any support of the tool at: Email: techsupport@smartwaretech.com Phone: (716) 213-2222
View full article
Picard Product_Support
‎2018-09-10 10:33 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
3448 Views

Explanation of BACnet MAC address

Issue In EBO BACnet device discovery, how is the BACnet MAC address defined? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Enterprise Server Cause A BACnet device is uniquely identified by a network number and a MAC address. Resolution BACnet MS/TP A BACnet MS/TP device supports device MAC addresses in the range 0-127 for masters and 0-254 for slaves. Device MAC addresses are often configured using DIP switches or a configuration tool.   BACnet/IP MAC addresses for BACnet/IP devices are a combination of the IP address and BACnet/IP UDP Port expressed in hexadecimal notation. For example, if a BACnet/IP device is configured with an IP address of 192.168.1.5 and a UDP port of 47808 then:   IP address expressed in hexadecimal is 192 = C0, 168 = A8, 1 = 01, 5 = 05 UDP port expressed in hexadecimal is 47808 = BAC0   Therefore the MAC address will be, C0:A8:01:05:BA:C0   BACnet/SC BACnet/SC nodes are identified by their 6-octet virtual MAC (VMAC) address in form of a IEEE EUI-48 identifier which is randomly generated. A BACnet/SC device attempts to resolve its own VMAC in the network. If it detects another device is already using this VMAC, it will generate a new Random-48 VMAC address and try again.
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-10-26 03:04 PM

on ‎2022-10-26 03:04 PM

Labels:
  • EcoStruxure Building Operation
3499 Views

Integrating EBO with ESMI Fire Detection Panel

Issue Would like to monitor and control points and alarms from an ESMI Fire Detection Panel in EBO. Product Line EcoStruxure Buildning Operation Environment Building Operation Automation Server Premium (AS-P) ESMI Fire Detection Panel Cause The integration between ESMI Fire Detection Panel and EBO enables the user to visualize and operate ESMI Fire detection systems effectively from graphics in EBO. Resolution The interface between the ESMI Fire panels and EcoStruxure Building Operation (EBO) is handled by the AS EN54 FIRE SmartDriver. The event and command information is sent/received by the Fire panel using RS-485 communication to/from the AS-P using the SmartDriver.   This resolution is in three steps: Enable communication via RS485 (INFO protocol in Fire panel) Use the AS EN 54 Fire Configurator to create the layout for EBO Install/configure the SmartDriver and create the Fire graphics in the AS-P   Step 1 - Enable communication via RS485 (INFO protocol in Fire panel) This video shows how to enable communication from an ESMI Fire panel and an AS-P over RS485. This is a prerequisite for using the Fire SmartDriver in the AS-P.     Step 2 - Use the AS EN 54 Fire Configurator to create the layout for EBO This video will give you a quick introduction to the AS EN54 Fire Configurator. The AS EN54 Fire Configurator is a Windows application that imports floor plans and configuration files to create the EBO interface, devices, points, alarms and graphics.     Step 3 - Install/configure the SmartDriver and create the Fire graphics in the AS-P This video shows how to connect an EBO SmartX Server to an Esmi Sense Fire detection panel (FDP). And how to create and edit the Fire graphics in the EBO SmartX Server, The fire graphics provide the user interface to visualize and operate Esmi Fire detection systems.  
View full article
Janeway PeterEdvik Janeway
‎2021-11-24 02:24 AM

on ‎2021-11-24 02:24 AM

Labels:
  • EcoStruxure Building Operation
3433 Views

Continuum "Find New BACnet Device" fails to find BACnet devices

Issue Find New BACnet Device fails to find BACnet devices Product Line Andover Continuum Environment Continuum CyberStation Cause Third Party BACnet software may interfere with the CyberStation Bacnet Find process. NOTE: There are other reasons that bacnet devices may not be found not covered within this document. See: Cannot find new BACnet devices. Could not learn in a new 3rd Party BACnet device Bacnet 3rd party controller will not respond to Find New Bacnet Devices (Who-Is/I-Am) Resolution Stop the BACnet service in Administrative Tools\ Services. One example would be Cimetrics service Bacstac Protocol Once the BACnet devices have been found the BACnet service can be restarted, although it may be best to uninstall any non-Continuum bacnet software from a CyberStation
View full article
Picard Product_Support
‎2018-09-10 11:19 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 06:30 PM

Labels:
  • Andover Continuum
3421 Views

SLP Sensor Modbus RTU issue when used with RPC or Automation Server

Issue SLP Sensor Modbus RTU issue when used with RPC or AS Communication errors are seen during normal Values are updated very slowly, can take up to two minutes to populate/update the 15 objects within the SLP.   Product Line EcoStruxure Building Operation Environment Modbus RTU RPC Modbus Automation Server + Premium  SLP SpaceLogic Sensors LSA_APP_REV2.03.19 and REV2.05.21 Cause Once the Modbus communication is set up between RPC (or AS) and the SLP,  although the values updates fairly regularly, multiple communication errors are also seen The SLP read speed needs to regulated to prevent overwhelming it The SLP Modbus transmission voltage is less than the AS Resolution Use with RP-C SLP struggles to respond to every request from the RP-C, changing the baud rate to 9600/19200 and increasing the "Silence characters" in the interface to 255 (maximum possible) should stabilize the communications.  The character spacing cannot be adjusted enough in the RP-C to allow communication at 38400 or 76800 Use with AS/AS-P  Adjust the “Poll point delay” in the Modbus Interface to 80ms The Silence characters and Transmit guard bits may also need to be increased Baud rate up to 38400 has been tested.  
View full article
Dave_Shore Schneider Alumni (Retired)
‎2021-02-03 06:29 AM

Labels:
  • EcoStruxure Building Operation
3454 Views

SmartStruxure - SE IntesisBox does not support Read Property Multiple (RPM).

Issue Binding a SmartStruxure Analogue value to a Analogue output in the SE IntesisBox (Panasonic Air Conditioning). Environment IntesisBox Panasonic RPM Read Property Multiple Cause Attempting to bind the analogue value to the IntesisBox analogue output causes the following error; Resolution In this case, the AS database has the wrong unit (no-units) associated with the object, since it does not match to the units in the device "Degrees-Celsius" the failure occurs' This is corrected in StruxureWare Building Operation 1.5, where the unit id is not uploaded if the device does not support read-property-multiple, and it appears from the device documentation, that the IntesisBox does not support RPM. As an immediate workaround, the user can configure the unit id of the analog output object directly - configure the "Value" property to have a unit of Degrees Celsius.  To view the IntesisBox Panasonic manual, please click HERE.
View full article
Picard Product_Support
‎2018-09-11 06:57 AM

Labels:
  • EcoStruxure Building Operation
3493 Views

UPC Barcodes and EAN Barcodes

Issue UPC Barcodes and EAN Barcodes Environment Site ordering parts from Schneider-Electric Cause What are UPC Barcodes and EAN Barcodes Resolution The EAN contains a 13 digit number and the UPC contains a 12 digit number. EAN = 0012345678905 UPC = (0)012345678905 or 012345678905 GS1, the original source for barcodes has created the confusion between UPC (Universal Product Codes) and EAN (European Article Numbers also called International Article Numbers) Below is an example of a Schneider Electric SHR110 room RH/Temp sensor:
View full article
Picard Product_Support
‎2018-09-11 09:05 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • TAC INET
  • TAC Vista
3433 Views

SmartStruxure Hardware Input and Output Specifications

Issue Questions regarding specifications of SmartStruxure Hardware Inputs and Outputs Product Line EcoStruxure Building Operation Environment SmartStruxure I/O Modules: AO-8, AO-8-H AO-V-8, AO-V-8-H DI-16 DO-FA-12, DO-FA-12-H DO-FC-8, DO-FC-8-H RTD-DI-16 UI-8-AO-4, UI-8-AO-4-H UI-8-AO-V-4, UI-8-AO-V-4-H UI-8-DO-FC-4, UI-8-DO-FC-4-H UI-16 Cause Different I/O modules have different electrical specifications Resolution Universal Input Specifications Universal inputs can be configured as voltage, current, thermistor, resistance, digital or supervised inputs. Voltage Input Specifications: Range - 0 to 10 VDC Resolution - 12 bit Accuracy - ±(0.7mV + 0.2% of reading) Current Input Specifications: Range - 0 to 20 mA Resolution - 12 bit Accuracy - ±(0.03 mA + 0.4% of reading) Resistance Input Specifications: 10 Ohm to 10 kOhm 10 kOhm to 60 kOhm Thermistor Input Specifications: Range - -50 to 150° C (-58 to 302° F) Thermistors: 10k Type I (Continuum), 10k Type II (I/NET), 10k Type III (Satchwell), 10k Type IV (FD), 1.8k (Xenta), 10k Linearized (Satchwell DRT), 10k Type V (FD w/ 11k shunt), 1k (Balco), 20k (Honeywell), 2.2k (Johnson Controls) Digital Output Specifications Form C Relay: Terminal - Common (C), Normally Open (NO), Normally Closed (NC) Minimum Pulse Width - 100 ms minimum Isolation - 1500 VAC minimum, coil to contact Cycle Life - At least 100,000 cycles Contact Rating - 250 VAC, 30 VDC, 3 A Form A Relay: Terminals - Common (C), Normally Open (NO) Minimum Pulse Width - 100 ms minimum Isolation - 1500 VAC minimum, coil to contact Cycle Life - At least 100,000 cycles Contact Rating - 250 VAC, 30 VDC, 2 A LED Specifications: LED Polarity - Represents the actual state of the output; ON if the output is active, OFF if the output is inactive LED Color - Green Analog Output Specifications Analog outputs can be configured as voltage or current. Module Voltage Output: Range - 0 to 10 VDC Resolution - 50 mV Accuracy - ±100 mV Terminals - Voltage (V), Return Minimum Load - Source, 2 mA; Sink, -1mA Current Output: Range - 0 to 20 mA Resolution - 0.1 mA Accuracy - ±0.2 mA Terminals - Current (I), Return Maximum Load - Output load should not exceed 650 Ohms Supervised Input Specifications Supervised inputs can be used to detect sabotage. Detected resistor values - Open circuit, short circuit, contact open, and contact closed. 5 volt circuit, 1 or 2 resistors, monitored - Series only, parallel only and series and switch combinations. For a 2-resistor configuration, each parallel. Resistor value range - 1k to 10 k resistors should have the same value. The selected resistor value needs to be defined in the system. RTD Input Specifications The specifications of the RTD-DI-16 are extensive and thus are best viewed directly in the data sheet available on the Buildings Download Center: RTD-DI-16 Specification Sheet You can also download the specification sheet here: IO Module RTD-DI-16 Specification Sheet (July 2014).pdf.
View full article
Picard Product_Support
‎2018-09-11 01:25 PM

Labels:
  • EcoStruxure Building Operation
3411 Views

Failed to establish connection with server when attempting to log into WorkStation for Projects

Issue Failed to establish connection with server. (HTTPS) 1.5 Server version not compatible with client (HTTP) 1.5 Failed to establish connection with server. (HTTPS) 1.6 Failed to access the server, a network error occurred. (HTTP) 1.6 Environment StruxureWare Building Operation 1.5 and newer Cause Attempting to log into WorkStation for Project and you either do not have the Project Configuration Server installed or the Project Configuration Server is not running. Resolution Reboot the machine. Check that the Project Configuration server service is running.  Note: One other possibility is that you have a different instance of Projects Configuration server already running from a concurrent installation. (Example: You are trying to log into Projects 1.8.1 but you already have Projects server 1.7.1 running). This will cause a Failed to establish a connection with the server error.
View full article
Picard Product_Support
‎2018-09-11 08:13 AM

Labels:
  • EcoStruxure Building Operation
3405 Views

Communication failure due to routing device not available

Issue Can no longer see BACnet point values at the Cyberstation.  BCX will not communicate with Cyberstation after IP addressing changes to the system. Product Line Andover Continuum Environment Cyberstation 1.74xx and up BCX 40xx Cause This can happen if the controller needs to be reloaded when accessing some, but possible not all objects. This can also happen if you change the BACnet Port Number - UDP in the bCX configuration webpage.  Resolution Edit the BCX and Cyberstations BBMD registrations Correct the invalid IP addresses. After adding the BCX bbmd entry, reload the controller.
View full article
Picard Product_Support
‎2018-09-06 01:57 PM

Labels:
  • Andover Continuum
3453 Views

In a Niagara G3 station, the BACnet Service indicates "routing enabled = false", even though it had been set = true. What caused the change?

Issue In a Niagara G3 station, the BACnet Service indicates "routing enabled = false", even though it had been set = true. What caused the change? Environment Niagara G3 station in an ENC with BACnet / IP enabled Cause The ENC has detected a routing loop and automatically stops routing BACnet / IP messages, and sets the "Routing Enabled" flag = false. Resolution This can be caused by having two or more devices routing to the same network number.  Network numbers must be unique throughout the entire BACnet network.    Locate and remove the cause of the routing loop, which is more than one path to a BACnet device.   Procedure Details: Open platform director Watch output for network number error.   (e.g. Bacnet Network Misconfiguration detected(3): Network number update frequency indicates possible router loop on network 20!!!)  Check BACnet devices with Routing enable and make sure all networks have a unique network ID. 
View full article
Picard Product_Support
‎2018-09-06 01:33 PM

Labels:
  • TAC IA Series
3387 Views

Change CX level controllers message count to improve I2 communications

Issue How to change the CX level controllers message count to improve I2 Infinet communications. Throttling adjustments using accinfoframe1 and accinfoframe2. Product Line Andover Continuum Environment accinfoframe, accinfoframes, acc info frame Continuum Cyberstation CX 9680 Infinet I2 bus Cause Improve I2 communications on the infinet bus. Changing the CX level controller's message count on the Infinet bus to improve alarm delivery and exported data times when heavy polling is occurring. Resolution TPA-BOST-00-0004.00 describes several fixes, including one that improves field bus with heavy traffic. One of the fixes speeds up graphics and field bus reloads. With the latest version of the firmware the ability to throttle the number of messages during token passing has been added. This will allow a variable to adjust an Infinet bus based on the amount of traffic a particular bus is experiencing. With the latest firmware versions 2.100028, 2.000030 for the Netcontroller 9680 there are variables that can be used to adjust the number of messages per token pass. This is very similar to the MaxInfoFrames setting on Bacnet the devices; we'll call them “accinfoframe” for this document and examples. The value can be adjusted for values of 1-128. Since the TPA was issued, the value is defaulted to 128 and if no accinfoframe variable is created the default value is 128. In order to have the ability to adjust the number of messages in the supported controllers, an infinity numeric needs to be created in the CX/BCX. The name of the variable has to be correctly spelled but is case insensitive. The names are accinfoframe1 and accinfoframe2. Accinfoframe1 will be the setting for comm1 one and accinfoframe2 will control the setting for comm2. When configuring accinfoframe1 or accinfoframe2, make sure to select the SetPoint and back up the flash on your controller, so that you retain the settings in case of power failure. Example of when to use throttling: There will be instances where the accinfoframe variables will need to be throttled. For instance, lets theorize a site “ChillerPlant” and the ChillerPlantCX(9680) has 100 infinet controllers located on Comm1. In our scenario we have 3 workstations each running a graphic polling 2 points(200 points) from each Infinet controller and we are running listviews of infinitynumerics on 8 of the Infinets controllers or perhaps hundreds of points that are being collected for extended logging. As one might think, communications would begin to slow down when polling for values on approx 600 points not to mention the point to point communications of the listviews and extended logs. With all of this traffic, the CX will dominate the network token. Since it can do 128 messages when it receives the token and it receives the token between every Infinet, the token round time can go into minutes. This means that the Infinet controllers can take minutes to deliver alarms and exported data. Another potential scenario is if one selected 4 Infinet controllers to reload, the bus may very well be overloaded at this time and may be receiving errors on the reloads in the distribution window. One of the error messages that could be expected is “Unable to reload object CarlNet\My_9680\My_I2_814\Num_1. An invalid response was received from a remote service request.” In this example we could create a infinity numeric on the CX named accinfoframe1(for Comm1) and start to reduce the number of messages CX would generate before passing the token. On the other extreme, if the ACCInfoFrame setting is set too low, such as to 1 as in the earlier versions of Netcontroller II firmware, this extreme traffic could cause such issues as extreme slowness of graphics and listview updates, Extended logging not being capable of retrieving the required data at the required intervals, and possibly the Infinet controllers randomly appearing to be offline to the system. In the example above the question is “What value should the accinfoframe1 be set to?” The answer entirely depends on how much traffic is on the Infinet bus. How many extended logs, how many listviews, how many graphics, alarms and Plain English programs are creating traffic on the bus? The quick way out here would be set the accinfoframe1 to a value of 1. We know for a fact that this would slow the bus down, and you might want to increase the number to 5. As mentioned this is all dependent on the amount of traffic on the Infinet bus. Or we could take a more in depth approach and find out what the token round time is on the bus and adjust our accinfoframe1 based on token round time. We could create the following points. TOKEN ROUND TIMER PROGRAM InfinityNumeric MaxTokenItem InfinityNumeric MaxTokenRound InfinityNumeric TokenRoundTime Logsize:100 Logtype: LogMaximum InfinityProgram TokenRoundCalc InfinityDateTime LastDateExport Program code: Initialise: LastDateExport = PointMapsTests\Infinity2\i2_851\Date Goto DoTokenRoundCalc DoTokenRoundCalc: If LastDateExport <> PointMapsTests\Infinity2\i2_851\Date then TokenRoundTime = (PointMapsTests\Infinity2\i2_851\Date - LastDateExport) – 1 LastDateExport = PointMapsTests\Infinity2\i2_851\Date Endif MaxTokenRound = maximum(TokenRoundTime) MaxTokenItem = maxitem(TokenRoundTime) E: If TS >= 5 then Goto Initialise The program and points above created in the CX will allow the token round time to be captured and one could essentially get very creative and change the accinfoframe value dynamically through Plain English programming. For these examples we just want to find out the token round time and manually adjust the accinfoframe1 variable to avoid any reload errors. The TokenRoundTime, MaxTokenRound and MaxTokenItem numerics can be added to a watch window or a graphic to visually monitor the TokenRoundTime. If you see that your TokenRoundTime is 5, 10 15 seconds, this is an indication you need to reduce the accinfoframe1 value. As a rule of thumb a TokenRoundTime of less then 2 seconds is acceptable, while keeping the TokenRoundTime below 0.7 seconds is ideal.
View full article
Picard Product_Support
‎2018-09-07 05:18 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-07-09 09:00 AM

Labels:
  • Andover Continuum
3394 Views

Modicon Switch Ordering and RSTP Configuration using EBO with MPX/RPX

Issue Modicon Switch Ordering options and how to configure the Ethernet Switch for RSTP for EBO Product Line EcoStruxure Building Operation Environment Modicon RSTP Switch (Not Connexium) Building Operation Automation Server Premium MPX and/or RPX Controllers Ethernet Switch Configurator Cause Schneider Electric Industry Offers an RSTP enabled Ethernet Switch that can be used with EBO instead of 3rd party Switches Resolution The following video will illustrate the following steps for Ordering and installing the Modicon Ethernet Switch with EBO The Modicon Connexium Ethernet Switch has been replaced by the updated Modicon Switch Modicon Switch Part Numbers and Email address for ordering Connect and use the SE Ethernet Switch Configurator executable for Switch configuration Set the Time and use the Syslog for troubleshooting Configure EBO and the controllers (MPX/RPX) for RSTP Test the Modicon Switch, EBO, and the MPX/RPX controllers for RSTP     Related Links: Modicon Switch Part Numbers and Ordering Information - (see attached Part Number slide) MCSESM Switch Installation Manual MCSESM Switch Configuration Manual Ethernet Switch Configurator Software - look for  SchneiderElectricEthernetSwitchConfigurator2303_Windows_x86.zip Other Modicon Switch documents RSTP Troubleshooting Community Thread TGML Graphic Setup Video (Training Department)
View full article
Admiral Alan_Wood Admiral
‎2022-07-06 08:35 AM

Labels:
  • EcoStruxure Building Operation
3484 Views

PARSER_CODE_ERROR Error in COD file - Error:15

Issue   PARSER_CODE_ERROR Error in COD file - Error:15 When directly downloading a Menta file a Parser Code Error is displayed. This is a Parser Error that is alerting you to the fact that there is a problem with your Code. An error in the Menta file is stopping it from downloading successfully. Product Line TAC Vista Environment Menta Xenta programmable controllers Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B Cause Direct downloading a Menta file (via the RS-232 port, a serial cable, and Online Simulation Mode) can bring to light Parsing Errors that are not reported by the System Plug-in. These errors will result in unsuccessful download attempts without any indication of the failure. To find them, direct download the Menta file. The download gets to where it is parsing the file before it fails:  There are three known reasons why the parsing of a Menta file will fail with Error Code 15. With some careful investigation of the error the cause can be determined, although checking all known causes is not prohibitively time consuming. Either the Menta application is too large, contains SmartStruxure Function Block following a cut-and-paste of code, or the file has corrupted public values indicated by the values being shown in scientific notation. Resolution First, determine the source of the error. Three known issues are discussed below: Corrupted public values show in scientific notation The Error:15 window attempts to show the user where in the Menta code the error is occurring. Without a fairly intimate knowledge of the inner workings of Menta, this can be less than helpful. However, if scientific notation in a PVR is causing the error, the error window will show this. The first line states: PVR     3,Z4 R1.0762e-042 This is showing that a PVR in the Menta program has a value of 1.0762e-042. It may take some searching, but you will need to locate the PVR in the Menta file that has this corrupted value and change it back to something valid. Also check public constants in the file to make sure they are not corrupted.   SmartStruxure Function Blocks in TAC Menta application This error also appears if there are any SmartStruxure specific Function blocks in the application. RO, BO, RI, BI, TSCHI, ERROR, II, IO, PI, PO Check the if any of the blocks are in the COD file (in the error window), find the blocks and replace/remove them.   Menta Application is too large The only other option is that the Menta application is too large. So if the Error:15 window comes up and does not indicate scientific notation in any of the values, it has to be that the file didn't fit inside the controller. Check the memory in Menta under Options > Memory Usage. You want to see free space in all categories. If there are any negative numbers then that portion of the application is too large. Bear in mind that this is a simple estimation by Menta as to the memory needed. Trend logs, OP tree, network description files and the Menta application all need to be stored in the controller, so sometimes a very low, albeit positive, number can indicate problems as well. Try cutting down on trend logs or OP trees to free up space if the application cannot be reduced.
View full article
Picard Product_Support
‎2018-09-07 03:17 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-17 06:58 AM

Labels:
  • TAC Vista
3385 Views
  • « Previous
    • 1
    • …
    • 38
    • 39
    • 40
    • …
    • 508
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now