Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Accessing Continuum Security Key information using MMC instead of Excel

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Accessing Continuum Security Key information using MMC instead of Excel
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • Alan_Wood
    Alan_Wood
  • Clifton_eakes
    Clifton_eakes
  • Cody_Failinger
    Cody_Failinger
  • sesa116834_brid
    sesa116834_brid
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
4231 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Accessing Continuum Security Key information using MMC instead of Excel

Product_Support
‎2018-09-06 02:52 PM

Last Updated: Alan_Wood Leader ‎2022-04-14 07:18 AM

Issue

Accessing Continuum Security Key information using MMC to determine what features are enabled.

Product Line

Andover Continuum

Environment

Continuum Security Key

Cause

Users need the ability to know what version of Continuum is supported on their key

Resolution

Note: The MMC method for viewing enabled key features mentioned below no longer works with Windows10 or greater and because of CyberSecurity issues ActiveX controls have been deprecated by Microsoft in favor of more secure web technologies. 

This feature will not be updated for Cyberstation.

 

Some Cyberstations do not have Microsoft Office with Excel installed but the security key information may be accessed using Microsoft Management Console instead.

  1. Go to Start> Run, Type in MMC.exe and click OK
  2. Select File> Add/Remove Snap-in
  3. Click the Add button (bottom left)
  4. Click On ActiveX control and click Add
  5. Click Next while in the Insert ActiveX Control dialog
  6. Scroll Down until you find SecurityKeyReader Control and highlight it and click Next
  7. Leave the default name and click Finish
  8. Close the Stand Alone Snap-in dialog
  9. Click OK on the Add/Remove Snap-in dialog
  10. Click on the SecurityKeyReader Control and highlight it and it will display the Key info
  11. If you want to save it, File> Save and enter the name SecurityKey.msc

Windows 7 

(32-bit system) Go to Start> Run, Type in MMC.exe and click OK

(64-bit system) In Command Prompt  enter  mmc /32

  1. Select File> Add/Remove Snap-in
  2. Click On ActiveX control and click Add
  3. Click Next while in the Insert ActiveX Control dialog
  4. Scroll Down until you find SecurityKeyReader Control and highlight it and click Next
  5. Leave the default name and click Finish
  6. Click OK in the Add or Remove Snap-in dialog
  7. Double click on the SecurityKeyReader Control in the right-hand pane and it will display the Key info
  8. If you want to save it File> Save and enter the name SecurityKey.msc

To reopen

  1. Go to Start> Run, Type in MMC.exe and click OK
  2. File> Open and select Ex. SecurityKey.msc

To copy to another computer

  1. File Search> Enter SecurityKey.msc (or whatever you named it above)
  2. Copy the file to the other computer and paste it into the Administrative Tools folder
    Ex. C:\Documents and Settings\Administrator\Start Menu\Programs\Administrative Tools

 

Labels (1)
Labels:
  • Andover Continuum
Tags (5)
  • Find more articles tagged with:
  • 2868
  • AlanWood22
  • CliftonEakes22
  • dongle
  • options
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore