Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

PARSER_CODE_ERROR Error in COD file - Error:15

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PARSER_CODE_ERROR Error in COD file - Error:15
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa150555
    sesa150555
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3967 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PARSER_CODE_ERROR Error in COD file - Error:15

Picard Product_Support
‎2018-09-07 03:17 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-11-17 06:58 AM

Issue

parser_code_error.png

 

PARSER_CODE_ERROR
Error in COD file - Error:15

When directly downloading a Menta file a Parser Code Error is displayed. This is a Parser Error that is alerting you to the fact that there is a problem with your Code. An error in the Menta file is stopping it from downloading successfully.

Product Line

TAC Vista

Environment

  • Menta
  • Xenta programmable controllers
  • Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B

Cause

Direct downloading a Menta file (via the RS-232 port, a serial cable, and Online Simulation Mode) can bring to light Parsing Errors that are not reported by the System Plug-in. These errors will result in unsuccessful download attempts without any indication of the failure. To find them, direct download the Menta file. The download gets to where it is parsing the file before it fails: 

parsing.png

There are three known reasons why the parsing of a Menta file will fail with Error Code 15. With some careful investigation of the error the cause can be determined, although checking all known causes is not prohibitively time consuming. Either the Menta application is too large, contains SmartStruxure Function Block following a cut-and-paste of code, or the file has corrupted public values indicated by the values being shown in scientific notation.

Resolution

First, determine the source of the error. Three known issues are discussed below:

Corrupted public values show in scientific notation

errorincodfile.png

The Error:15 window attempts to show the user where in the Menta code the error is occurring. Without a fairly intimate knowledge of the inner workings of Menta, this can be less than helpful. However, if scientific notation in a PVR is causing the error, the error window will show this. The first line states:

PVR     3,Z4 R1.0762e-042

This is showing that a PVR in the Menta program has a value of 1.0762e-042. It may take some searching, but you will need to locate the PVR in the Menta file that has this corrupted value and change it back to something valid. Also check public constants in the file to make sure they are not corrupted.

 

SmartStruxure Function Blocks in TAC Menta application

Error15.png

This error also appears if there are any SmartStruxure specific Function blocks in the application.

RO, BO, RI, BI, TSCHI, ERROR, II, IO, PI, PO

Check the if any of the blocks are in the COD file (in the error window), find the blocks and replace/remove them.

 

Menta Application is too large

codfiletoobig.png

The only other option is that the Menta application is too large. So if the Error:15 window comes up and does not indicate scientific notation in any of the values, it has to be that the file didn't fit inside the controller.

Check the memory in Menta under Options > Memory Usage. You want to see free space in all categories. If there are any negative numbers then that portion of the application is too large. Bear in mind that this is a simple estimation by Menta as to the memory needed. Trend logs, OP tree, network description files and the Menta application all need to be stored in the controller, so sometimes a very low, albeit positive, number can indicate problems as well. Try cutting down on trend logs or OP trees to free up space if the application cannot be reduced.

Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 3935
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.