How to configure universal input for SE8000
  • How to configure universal input for SE8000
  • CraigEl
    CraigEl
  • sesa346290_brid
    sesa346290_brid
‎2018-09-10 10:25 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 11:22 PM
Unable to configure universal input from the thermostat
EcoStruxure Building Expert
SE8000
Universal inputs aren’t configurable at the thermostat
There are two ways to configure inputs on SE8000;
More often is via a BACnet front end and secondly is via a Lua script. The input shall be configured to Priority 3.
SE8000 INPUTS:
•       UI16 fixed as binary input
•       UI17 fixed as binary input
•       UI19 configurable as temperature sensor, binary input or 0 -10 VDC input
•       UI20 configurable as temperature sensor
•       UI22 configurable as temperature sensor
•       UI23 configurable as temperature sensor
•       UI24 configurable as temperature sensor, binary input or 0 -10 VDC input
For example UI19 configuration:
UI19 LUA AnalogValue:202 ; this point is to write a Lua via Bacnet for UI19.
LUA:
if not init then
ME.MV6 = 2  -- set network units to imperial
ME.MV145 = 2  -- room temp local
ME.AV25_Desc = "UI19 TEMP"  -- UI19 Present Value
ME.AV26_Desc = "UI20 TEMP"  -- UI20 Present Value
ME.MV140 = 1  -- UI19 thermistor
ME.MV141 = 1  -- UI20 thermistor
init = true
end
ME.AV25 = ME.AV104
ME.AV26 = ME.AV105
ME.AV100_PV[16] = (ME.AV104 + ME.AV105) / 2  -- average UI20 remote sensor and UI19 remote sensor
  • EcoStruxure Building Expert
Tags (4)
  • 19520
  • configuration SE8000 series
  • se8300
  • se8600