How to configure universal input for SE8000

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to configure universal input for SE8000
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • sesa346290_brid
    sesa346290_brid

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3313 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to configure universal input for SE8000

Picard Product_Support
‎2018-09-10 10:25 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 11:22 PM

Issue

Unable to configure universal input from the thermostat

Product Line

EcoStruxure Building Expert

Environment

SE8000

1.png

Cause

Universal inputs aren’t configurable at the thermostat

Resolution

There are two ways to configure inputs on SE8000;

More often is via a BACnet front end and secondly is via a Lua script. The input shall be configured to Priority 3.

SE8000 INPUTS:

•       UI16 fixed as binary input

•       UI17 fixed as binary input

•       UI19 configurable as temperature sensor, binary input or 0 -10 VDC input

•       UI20 configurable as temperature sensor

•       UI22 configurable as temperature sensor

•       UI23 configurable as temperature sensor

•       UI24 configurable as temperature sensor, binary input or 0 -10 VDC input

2.png

 

For example UI19 configuration:

UI19 LUA AnalogValue:202 ; this point is to write a Lua via Bacnet for UI19.

LUA: 

if not init then
ME.MV6 = 2  -- set network units to imperial
ME.MV145 = 2  -- room temp local
ME.AV25_Desc = "UI19 TEMP"  -- UI19 Present Value
ME.AV26_Desc = "UI20 TEMP"  -- UI20 Present Value
ME.MV140 = 1  -- UI19 thermistor
ME.MV141 = 1  -- UI20 thermistor
init = true
end

ME.AV25 = ME.AV104
ME.AV26 = ME.AV105
ME.AV100_PV[16] = (ME.AV104 + ME.AV105) / 2  -- average UI20 remote sensor and UI19 remote sensor
Labels (1)
Labels:
  • EcoStruxure Building Expert
Tags (4)
  • Find more articles tagged with:
  • 19520
  • configuration SE8000 series
  • se8300
  • se8600
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of