Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 141
    • 142
    • 143
    • …
    • 509
  • Next »

Test a REST gateway in SmartConnector using Swagger

Issue After setting up a REST gateway in SmartConnector, how can it be tested to see that it is working using the built in test client called Swagger? Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central SmartConnector   Cause Swagger is a built in test REST client which can be used to read and set values in EBO. So it can be used instead of a "real" REST client to test the REST gateway in the SmartConnector and test that the connection between SmartConnector and EBO is working. Resolution The objective in this video is to set up a REST gateway in SC and show how we can test that the gateway is working using the built in test REST client called Swagger. Please see video.
View full article
Janeway Jonas_Brissman Janeway
‎2023-09-11 06:50 PM

on ‎2023-09-11 06:50 PM

Labels:
  • EcoStruxure Building Operation
1816 Views

How does the autobaud feature work on b3 controllers

Issue What process do the bCX and b3 controllers use to automatically establish their communication bus speed. Product Line Andover Continuum Environment bCX b3 Auto Baud MSTP Cause Having issues with b3 controllers selecting the wrong bus speed. Resolution The process by which the b3 controllers establish their communication speed is as follows. When the b3 controllers power up, they listen to the network for 2.5 seconds If they hear communication at their last known Baud rate, they start talking when they hear the poll for master. If they hear no communication after 2.5 seconds, they start their own poll for master at their last known Baud Rate. If they hear garbled communication during the 2.5 second listen mode, they begin hunting different Baud Rates while listening until they have synced to the Baud Rate they are listening to. Then they join the token passing when they receive the Poll for Master. Note:  There was a issue with the autobaud process in earlier versions of the b3 and BCX40xx controllers which would cause them to set the communication speed incorrectly.  This issue was corrected in the following firmware versions. BCX40xx ==> 4.500053 b3xxx      ==> 4.500064 b-3xxx-V ==> 4.501064
View full article
Picard Product_Support
‎2018-09-06 11:09 AM

Last Updated: Sisko GavinHe Sisko ‎2023-04-19 08:13 AM

Labels:
  • Andover Continuum
1840 Views

StruxureWare Building Operation Enterprise Server Application Error occurs at computer start up

Issue The ES crashes during startup   SE.EnterpriseServer.exe - Application Error occurs, and the Building Operation Enterprise Server service cannot be started.  Error contains "The memory could not "written"".   The port fields in software administrator shows a red indication on one or more of the ports Environment Enterprise Server Software Administrator IP ports Cause A program is already using the ports defined for the Enterprise Server     In general   You can check which program it is, by entering the following command in a command prompt, replacing ":port number" with the number you want to check, e.g. "0.0.0.0:80" for port 80: netstat -aonb | find "0.0.0.0:port number"     Now in the task manager, enable the coloumn "PID (Process Identifier)", and look for the process ID you get to the far right when running the command above. That will show what program is taking the port.       Skype   If you are running Skype on the Enterprise Server PC there could be a conflict between the default IP port settings and the IP port settings in Software Administrator. The default ports for SmartStruxure Enterprise Server are 80 and 443. By default, Skype will "use port 80 and 443 as alternatives for incoming connections" if the configured port is unavailable. When Skype is launched it appears to search for an open IP port. If it cannot find an open port within a period of time it may default to ports 80 and 443 as a backup. This behaviour appears to be intermittent.    TeamViewer In newer versions of TeamViewer this is no longer an issue, but it's good practice to select "Use UDP" in the advanced settings of TeamViewer Resolution In general, you can change the ports used by the Enterprise Server in the Building Operation Software Administrator.   If the issue is Skype do the following: In the Skype tools menu go to “Options…” Expand the “Advanced” settings on the left hand side. Click “Connection” in the Advanced section. Uncheck the setting that says "Use port 80 and 443 as alternatives for incoming connections"
View full article
Picard Product_Support
‎2018-09-06 11:55 AM

Labels:
  • EcoStruxure Building Operation
1858 Views

Access Expert Mercury Controller Types and Features

  Issue List of Mercury Controller Types and Features Product Line EcoStruxure Access Expert Environment Access Expert V3 Hosted Cause Mercury Controller Types and features to use with Access Expert Resolution Overview Mercury controllers are an open architecture controller made by Mercury Security. Feenics currently supports the LP series boards, the series 2 and series 3 MR SIO series boards.   Mercury Controllers   Equivalent Features FN-C1501 EP1501 The EP1501 is an intelligent controller that is expandable up to 8 downstream SIO controllers and up to 16 MR51e network-ready door controllers (for a total of 17 doors/openings). 240,000 Cardholders 50,000 Transaction buffer 32 Access Levels per cardholder 2 Onboard Readers 1 SIO bus (note: connects via Reader Port 1) FN-C3202 EP1502 The EP1502 is an intelligent controller for controlling two connected doors and managing up to 64 doors/openings. 240,000 Cardholders 50,000 Transaction buffer 32 Access Levels per cardholder 2 Onboard Reader Ports 1 SIO bus FN-C3200 EP2500 The EP2500 is an intelligent controller for managing up to 64 doors/openings. 600,000 Cardholders 50,000 Transaction buffer 32 Access Levels per cardholder 2 SIO Buses FN-C4502 EP4502 The EP4502 is an intelligent controller for controlling two connected doors and managing up to 64 doors/openings and complies with the BACnet standard. 2,000,000 Cardholders 50,000 Transaction buffer 32 Access Levels per cardholder 2 Onboard Readers 2 SIO Buses FN-LP1501 LP1501 The LP1501 is an intelligent controller that is expandable up to 8 downstream SIO controllers and up to 16 MR51e network-ready door controllers (for a total of 17 doors/openings). 240,000 Cardholders 50,000 Transaction buffer 255 Access Levels per cardholder Supports up to 130 inputs and 130 Outputs 2 Onboard Readers 1 SIO bus (note: connects via Reader Port 1) FN-LP3202 LP1502 The LP1502 is an intelligent controller for controlling two connected doors and managing up to 64 doors/openings. 240,000 Cardholders 50,000 Transaction buffer 255 Access Levels per cardholder Supports up to 520 inputs and 516 Outputs 2 Onboard Reader Ports 1 SIO bus FN-LP3200 LP2500 The LP2500 is an intelligent controller for managing up to 64 doors/openings. 600,000 Cardholders 50,000 Transaction buffer 255 Access Levels per cardholder Supports up to 1024 inputs and 1024 Outputs 2 SIO Buses FN-LP4502 LP4502 The EP4502 is an intelligent controller for controlling two connected doors and managing up to 64 doors/openings and complies with the BACnet standard. 2,000,000 Cardholders 50,000 Transaction buffer 255 Access Levels per cardholder Supports up to 1024 inputs and 1024 Outputs 2 Onboard Readers 2 SIO Buses FN-M5-IC M5-IC An intelligent control device for the replacement of the Casi PX, PXN and PXNplus CPU controller. The single controller supports up to 64 readers across multiple enclosures. 128 Access Levels per cardholder FN-M5-ICS M5-ICS A multi-device interface panel that is a direct retrofit of Software House’s Pro GCM module. A 64 reader capacity 600,000 Cardholders Mercury - PW6K1IC Prowatch 6000  The PW6K1IC is an intelligent controller that is expandable up to 8 downstream SIO controllers and up to 16 MR51e network-ready door controllers (for a total of 17 doors/openings). 15,000 Cardholders 10,000 Transaction buffer 32 Access Levels per cardholder   EP Controllers - End of Life  Feenics used to support the EP Series controllers, however, they have been replaced with the LP series. Related article - Updating Mercury Firmware https://community.se.com/t5/Building-Automation-Knowledge/Access-Expert-Updating-Firmware-on-an-SSC-or-Mercury-Controller/ta-p/410961  
View full article
Admiral Alan_Wood Admiral
‎2022-10-20 08:19 PM

on ‎2022-10-20 08:19 PM

Labels:
  • EcoStruxure Access Expert
1893 Views

PCT error installing EBO package

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue During the installation of the EBO package, an error is displayed about PCT_temp.vbox already in existence.   ERROR_(3), UNABLE_TO_EXECUTE__COMMAND(99), reason=VBo xManage.exe: error: Machine settings file Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool (PCT) Cause Leftover folder/file from previously failed installation Resolution Close PCT if running Take note of the folder/file that the error refers to, in this case "C:\Users\sesaxxxxxx\.VirtualBox\PCT_temp\PCT_temp.vbox Make a backup of the folder/file as a precaution (in case it has to be put back) Delete the folder or file, in this case, delete the PCT_temp folder Re-launch PCT and attempt to install the EBO package once again
View full article
Captain AbeMeran Captain
‎2022-09-15 09:49 AM

Last Updated: Administrator CraigEl Administrator ‎2023-07-12 06:43 PM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
1828 Views

Transfer EBO 2022 or higher data to Azure IoT hub via MQTT protocol

Issue How to transfer EBO 2022 or higher data to Azure IoT hub via MQTT protocol Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Need to configure EBO MQTT interface and Azure IoT Hub, so EBO can send MQTT messages to Azure MQTT IOT Hub. Resolution The following video will illustrate how to: Create Azure IoT hub and IoT device using Azure Portal Create IoT interface and Azure MQTT client in EBO Configure the MQTT connection Create and configure a data group Test the connection Things you need: EBO 2022 or later with valid MQTT license or demo license (Enterprise Server, AS-P or AS-B) valid Azure Subscription with possibility to use free account during testing. For each Azure subscription one IoT hub in the free tier can be created, refer to IoT Hub | Microsoft Azure Visual studio code to be used to test the connection between EBO and Azure IoT hub, can be download from: Visual Studio Code
View full article
Kirk Mahmoud_Sayed Kirk
‎2022-09-15 12:41 AM

on ‎2022-09-15 12:41 AM

Labels:
  • EcoStruxure Building Operation
1892 Views

How to disable UNC power monitoring

Issue How to disable UNC power monitoring Environment I/A Series R2 Universal Network Controller (UNC) I/A Series Niagara R2 version 2.301.318 or later Cause UNC that is installed with I/A Series Niagara R2 version 2.301.318 or later has power monitoring enabled. UNC-410 and UNC-520 have the following parameters monitored. Power Loss - alarm on AC power loss Battery fail - alarm if backup battery test fail There could be situations where the monitoring of these parameters needs to be disabled.  Resolution You can disable the UNC's power monitoring function by editing the UNC's driver.properties file.  To access the driver.properties file, in WorkPlace Pro Admin Tool, connect to the UNC and go to the 'Installation' tab. Click on the 'Edit drivers.properties' button.  The line 'power.enabled=true' enables the power monitoring. To disable power monitoring, change the line to 'power.enabled=false'.  After the change, save the changes (File > Save) and reboot the UNC.   For more details, refer to the Niagara System and Power Monitoring Engineering Notes. 
View full article
Picard Product_Support
‎2018-09-10 01:22 PM

Labels:
  • TAC IA Series
1817 Views

Acknowledging BACnet alarm from a Continuum WS causes issue to some type of 3rd party BACnet Operator Workstations (BOWS) when the 3rd party BOWS is registered as one of the recipi...

Issue When a Bacnet alarm from BACnet controller (BCX and b3 controller) is acknowledged,  alarm recipient Continuum WS sends out Change-Of-Bitstring packet to the 3rd party BACnet Operator Workstation (BOWS) when the 3rd party BOWS is registered as one of the recipients in the EventNotification of the alarm. Environment Continuum WS. BCX. B4920. B3 controllers.. Cause This packet shows some proprietary behavior of Cyberstation we refer to as the "workstation to workstation ack", that happens in addition to the normal workstation to controller acknowledgement. Cyberstation uses the information in the Recipient List of the NotificationClass object of the original alarm to determine which other devices receive the original alarm, and therefore, should receive the proprietary alarm ack. Resolution As a workaround is as below: From the existing EventNotification, remove all the 3rd party devices from its recipient list. Create a new EventEnrollment & EventNofitication for the same alarming point, and add only the 3rd party devices to its recipient list.
View full article
Picard Product_Support
‎2018-09-06 10:49 AM

Labels:
  • Andover Continuum
1820 Views

Cannot do a backup to flash on bCX4040. ACCStatusBackup is set to ACCBackupInactive.

Issue Cannot do a backup to flash on bCX4040. Distribution Properties indicates "The flash for this controller does not need to be backed up." Product Line Andover Continuum Environment bCX4040 Cause ACCStatusBackup is set to ACCBackupInactive when ACCRestartMode is set to ACCWarmStartOnly. This occurred when a bCX9640 was flashed to a bCX4040.  ACCWarmToCool is the default ACCRestartMode for the bCX4040. Resolution Change ACCRestartMode to ACCWarmToCool and then try the backup. For more information on the ACCRestartMode refer to Chapter 5 of the bCX1 Series Controller Technical Reference document # 30-3001-890.
View full article
Picard Product_Support
‎2018-09-06 10:45 AM

Last Updated: Administrator CraigEl Administrator ‎2024-04-28 10:37 PM

Labels:
  • Andover Continuum
1897 Views

Veris - Schneider Electric part number cross reference

Issue When ordering Veris products through Schneider Electric, SE part numbers must be used. Environment Veris products Cause Cross reference needed between Veris and Schneider Electric part numbers. Resolution   Veris Part no SE Part no H708 3240100000 H709HV 3240101000 H308 3240102000 H608 3240103000 H908 3240104000 H909HV 3240105000 H800 3240106000 H300 3240108000 H600 3240109000 H900 3240110000 H721LC 3240201000 H721HC 3240202000 H921 3240203000 H722LC 3240204000 H722HC 3240205000 H723LC 3240206000 H723HC 3240207000 H922 3240208000 H923 3240209000 H221 3240210000 H321 3240211000 AH01 3240301000 AH-27 3240302000
View full article
Picard Product_Support
‎2018-09-06 10:41 AM

Labels:
  • Field Devices
1882 Views

ODBC (Open Database Connectivity) with EcoStruxure Building Operation

Issue ODBC used with EcoStruxure Building Operation Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Building Operation Edge Server - Standard Cause ODBC (Open Database Connectivity), a standard C programming language middleware API. is used to access database management systems (DBMS). Resolution ODBC is not supported with the current or previous releases of EcoStruxure Building Operation.
View full article
Picard Product_Support
‎2018-09-06 10:35 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2023-08-21 05:00 AM

Labels:
  • EcoStruxure Building Operation
1833 Views

SEZ7000 Series Zone Controllers

Issue SEZ7000 Commercial zoning systems Environment Need for commercial application with zone controlling Cause What does the SEZ7000 series unit provide? What would be a comparable replacement for an obsolete Trend IQ222 Resolution The SEZ commercial zoning system has been specifically designed to bring a simple scalable solution to mid-market commercial applications without the cost associated with a typical DDC zoning system. Models include roof top and heat pump units controlling analogue heat, CO2 levels, and indoor air quality. Zoning controllers that provide floating and analogue damper control are also available. A single central controller unit can support up to 64 individual zone controllers. All zoning system controllers can be ordered with an on-board passive infrared (PIR) occupancy sensor cover that allows for advanced occupancy strategies, enabling greater energy savings to zones during scheduled events when no occupants are present.
View full article
Picard Product_Support
‎2018-09-11 01:27 AM

Labels:
  • Field Devices
1867 Views

Can you replace a B-Link with an Infilink200?

Issue Are the Infilink and B-Link interchangeable or can they be converted? Product Line Andover Continuum, EcoStruxure Building Operation Environment Infilink 200 B-Link Cause Both units are RS-485 repeaters; is there a difference? Resolution You cannot convert from an Infilink 200 to a B-Link. They are both RS-485 repeaters, but the circuitry is slightly different to handle the electrical requirements of the BACnet MS/TP and the Infinet. You must use the correct unit for the network type you have. The multiple ports on both repeaters (Infilink and B-Link) allow you to construct a star topology configuration, but note that devices in each spoke (port on the repeater) MUST be connected in a daisy chain topology. Neither product contains any firmware that can be changed.
View full article
Picard Product_Support
‎2018-09-06 10:14 AM

Last Updated: Administrator CraigEl Administrator ‎2023-05-30 06:28 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1877 Views

What will the pressure drop across a 32mm valve be?

Issue The pressure drop across the valve is required. Environment Valve Pressure Drop Cause Customer needs to know what the pressure drop across a 32mm valve will be. Resolution Example: two 32mm V211T valves with flows of 0.549 l/s and 0.483 l/s through them. To calculate the pressure drop use this formula - Pressure drop = (Flow rate in M3/Hr / KVs) squared. Flow rate of 0.549 l/s 32mm V211T has a KV of 16 Converting flow to M3/Hr - 0.549 * 3.6 = 1.9764 Pressure Drop = 1.9764 / 16 = 0.123525 squared = 0.015258 Bar * 100 = 1.526 kPa Flow rate of 0.483 l/s 32mm V211T has a KV of 16 Converting flow to M3/Hr - 0.483 * 3.6 = 1.7388 Pressure Drop = 1.7388 / 16 = 0.108675 squared = 0.0118102 Bar * 100 = 1.181 kPa To review the Satchwell Valve sizing data sheet, please click HERE.
View full article
Picard Product_Support
‎2018-09-11 09:22 AM

Labels:
  • Field Devices
1864 Views

Controller serial numbers are now being shipped greater than 4,194,303 range (800xxx or 900xxx). Does this cause a problem with the devices BACnet Device Id setting and it's ab...

Issue Previously the BACnet Device Id of the controller would default to the devices serial number, this is no longer possible due to the maximum BACnet Device Id being 4,194,303. Serial numbers greater than 800xxx can give an error 'Device Node id is out of range' (1 to 4,194,303) Environment Continuum BACnet Controllers Cause Concern about what the default BACnet Id will be set to a value higher than what is supported or to a value that has already been set to a previous controller. Will this conflict with existing controllers on a site when adding new controllers when all are using the default BACnet Device Id? Resolution There is an internal calculation done that uses the Serial number as a seed to then calculate the BACnet Device Id so that it falls within the 4,194,303 max. This calculated value will be unique to every other Continuum BACnet Devices default BACnet Device Id so you should be fine when newer controllers are being added to existing sites. If you want to ensure there are no address conflicts though you may want to set the value yourself when commissioning the controllers through creating the Device object manually and setting the BACnet Device Id at that time or if the device is already configured delete it from the BACnet side and then edit it from the Infinity side and enter a new and unique device id, then perform a find BACnet devices to bring the device back on the BACnet side with its new device id.
View full article
Picard Product_Support
‎2018-09-06 10:09 AM

Labels:
  • Andover Continuum
1817 Views

Method to disable credential access on doors at different controllers from a single variable

Issue How to disable credential access on Doors at different controllers using a single variable. Product Line Andover Continuum Environment Continuum Access Control Cause Require a method of securing multiple Doors at the same time. Resolution The best way to secure a number of Doors from a single variable is to use the Door Force Lock Schedule attribute in the Door object. This is accomplished by adding a numeric to the attribute on the Options tab of the Door object; IMPORTANT: The attribute name Door Force Lock is misleading, it DOES NOT lock the door in any way, all it does is disable credential access at the door. For Area/Door Lockdown refer to the linked KB article And also on the Entry Reader or Exit Reader tabs, ticking the checkbox under either Normal and/or Comm Fail for Door Forced Lock Schedule. Setting this Door Force Lock Schedule field to a local or remote InfinityNumeric point will provide the following conditions: When the Numeric is on, access is permitted to all personnel by card swipe and/or keypad entry. (Allow use of the door.) When the Numeric is off, card reader and keypad access are denied to all personnel. (No Access) You could have this numeric located in a central controller and all the rest of the controllers reference this numeric from the Door objects. No other points or plain English is required. If you want to ensure that the updates are received, you can force the IE entry for this numeric to update on a regular interval, see Use just one schedule to control doors or access to areas across different controllers that discusses how to accomplish this.  
View full article
Picard Product_Support
‎2018-09-11 09:16 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:48 AM

Labels:
  • Andover Continuum
1822 Views

Availability of SLC-82XX and SLC-83XX

Issue Availability of SLC-82XX and SLC-83XX Environment Site with Single Loop Proportional Temperature Controller with Sensor Cause Obsolescence of the SLC-82XX and SLC-83XX Resolution The SLC-82xx and/or SLC-83xx are obsolete. These are old analog technology controllers which have been obsolete since January 01, 2011 There is no replacement for these items. The only suggestion would be to do a complete re-control with digital equipment. To do this one of Schneider Electric's Partners would need to visit the site to see what is needed to control the space. This would require new controllers, thermostats, actuators and other items. Since it is such a major re-control we do not have a single solution that will allow you to use some of the older equipment. Contact your Regional Manager in your area to provide a contact for the site upgrade.  The manual for the SLC-82xx and SLC-83xx is available here.
View full article
Picard Product_Support
‎2018-09-11 06:08 AM

Labels:
  • Field Devices
1811 Views

Sensor Calibration certificate, Veris portfolio

Issue   A calibration certificate is sometimes requested by the end customer Product Line Field Devices Environment Veris sensors Cause   To ensure that a sensor is keeping measurement values within specification, a certificate is sometimes requested by the end customer. Resolution Calibration certificates are available for some Veris models and must be requested at the time of ordering by selecting  “N” in NIST block for 1% and 2% humidity transmitters. Temperature transmitters can be ordered with 1 or 2 point calibration certificates by selecting 1 or 2 in the in the Temp Cert Block. The following example shows how the model numbers are built up: As can be seen in the second example above the model HD2NVCTC2 has a 2% accuracy RH element with a NIST traceable certificate, it also has a 1K platinum RTD with a 2 point  calibration certificate. For information on NIST traceability see the National Institute of Standards and Technology website
View full article
Picard Product_Support
‎2018-09-11 02:48 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 09:39 PM

Labels:
  • Field Devices
1844 Views

Display PDFs in webpinpoint

Issue There is a need to be able to display pdf files from within a webpinpoint graphic Environment Webclient Windows XP Windows 7 Windows Server 2003 Windows Server 2008 Cause instructions to open a pdf file with webpinpoint Resolution Within a graphic in Cyber Pinpoint, add a Windows Control> Web Browser object Edit the object and go to object properties and select the .pdf to display (Change the file type drop down to all files from .htm)  It is recommended to place the pdf files in C:\program files\Continuum\NewGraphicsFiles for permissions reasons.  Once that object has been selected, it can be saved and run in Cyber Pinpoint The same object will open up webpinpoint and the pdf will display.
View full article
Picard Product_Support
‎2018-09-06 09:46 AM

Labels:
  • Andover Continuum
1875 Views

Schneider Electric Security Statement Regarding the Heartbleed Vulnerability

Issue Vulnerability affecting certain versions of OpenSSL. Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment OpenSSL Cause Software vulnerability Resolution Information and Customer Statement located at the following link on the community: Schneider Electric Security Statement Regarding the Heartbleed Vulnerability. A corporate statement on this can also be found here: Schneider_Electric_Heartbleed_Customer_Statement_APR_15_2014.pdf.
View full article
Picard Product_Support
‎2018-09-11 03:02 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1841 Views
  • « Previous
    • 1
    • …
    • 141
    • 142
    • 143
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of