L-IP Firmware Upgrade.

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • L-IP Firmware Upgrade.
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Sacco
    Sacco
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2039 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

L-IP Firmware Upgrade.

Picard Product_Support
‎2018-09-07 06:43 AM

Issue

Upgrading Loytec L-IP to the latest firmware or checking current firmware version.

Environment

  • Loytec L-IP
  • Vista
  • Network Interface

Cause

UL 864 v.9 for Smoke Control requires at least version 5.04 firmware in all system L-IP's.

Resolution

Verifying L-IP Firmware Version via Console Connection

To use the serial interface, the DB9 console connector of the L-IP can be connected to the RS-232 port of a PC. The L-IP-3ECTB and L-IP-33ECTB use a standard null-modem-cable must be used to connect the L-IP’s DB9console connector to the RS-232 port of the PC. The PC will communicate with the L-IP using a HyperTerminal program with the communication settings set to 38,400 bps / 8 data bits / no parity / 1 stop bit / no handshake.

The L-IP displays the console menu shown in Figure 1 upon a successful HyperTerminal connection initiated by a “enter” keystroke or power cycle of the L-IP:

LOYTEC electronics GmbH
www.loytec.com
L-IP Configuration Menu
=======================
[1] Show device information
[2] Serial firmware upgrade
[3] System configuration
[4] EIA-709 configuration
[5] IP configuration
[6] EIA-852 device configuration
[7] EIA-852 server configuration
[8] Reset configuration (factory defaults)
[9] Device statistics
[0] Reset device Please choose:

Figure 1: L-IP main menu.

Select Option 1 to Show device information  This menu item shows information about the L-IP and the current firmware version. The output should look like what is shown in Figure 2.

Product information
===================
Product code: L-IP-3ECT
Firmware: L-IP
Primary image Version: 5.0.5
Build date: Fri Mar 18 10:41:29 2005
Serial number: 002304-80000000E73C
Free memory: 557K,57K
System temp: 33.3C
Supply volt: 12.0V
Unique Node IDs
===============
Port 1: 80 00 00 00 E7 3C
EIA852: 80 00 00 00 F7 92

Figure 2: Device information.

(For UL 864 v9: If the Firmware Version does not reflect a Version 5.0.4 or Version 5.0.5, you must update the firmware to an approved version in the next steps. If the L-IP contains an approved version, further action is not required.)

L-IP Firmware Upgrade

  1. To download the firmware via the console connected the L-IP to the RS-232 port of a PC via its console interface as outlined above.
  2. Download the lswitch_lipxxx.zip located at www.loytec.com to the PC.
  3. Install the LOYTEC serial upgrade tool (LSU Tool) by double clicking LSU_2_0_1setup.exe.
  4. Double click on the lswitch_lip_xxx.dlc file. This will start the LSU Tool and load the firmware image referenced in the . lswitch_lip_xxx.dlc file. The start window of the LSU tool is shown in Figure 3.

*note that the lswitch_lip_xxx.dlc file and the lswitch_lip_xxx.dl file must be stored in the same folder.

Figure 3: LSU Serial Upgrade Tool in idle mode.

  1. If the L-IP is not connected to COM1 you can change the port to COM1, 2, 3, or 4. Press “Download” to start the download. A progress bar as shown in Figure 4 can be seen.

Figure 4: Progress bar during firmware download.

  1. If the upgrade is successful the following window appears (Figure 5).

Figure 5: Successful firmware upgrade.

  1. Exit the LSU Tool. Reconnect through HyperTerminal connection and  initiate the console by a “enter” keystroke or power cycle of the L-IP. At the console main menu, select option [1] Show device information, and press Enter. This will bring up the current device information as shown in Figure 2, for verification that the firmware version has updated successfully.
Labels (2)
Labels:
  • Field Devices
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4688
  • lsd
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore