Continuum Add-On Reports will not launch

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Continuum Add-On Reports will not launch
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2118 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Continuum Add-On Reports will not launch

Picard Product_Support
‎2018-09-06 01:33 PM

Issue

Continuum Add-On Reports will not launch

Environment

  • Continuum
  • Continuum Add-On Report Suite
  • Windows XP
  • Windows Vista
  • Windows 7
  • Windows Server 2003
  • Windows Server 2008

Cause

The reports may not launch because of configuration issues or because the Workstation Instance in the database is corrupt.

Resolution

  1. Ensure that Continuum Reports is installed in Add/Remove programs
  2. Check that the Programs are listed under the workstation after importing the Continuum_Reports.dmp file and that they contain the reports programming code. If they are empty, re-import or cut and paste the code from the dmp file and correct errors.
  3. Check that the programs are enabled, if not enable the report and try again.
  4. Test the report from the command line instead of launching from a button (Ex. Run Reports_Suite).
  5. The second to last line is a Shell command, check that the Reports.exe 0 ( the number represents each report) has a unique number. Reports_Suite=0, Alarms_Report=2. A duplicated number may not run correctly.
  6. As a last test, create a new program called TestCalc with the following one line of code:
    Shell "C:\Windows\System32\Calc.exe"
    Fall Thru, AutoStart=False
    Run TestCalc from the command line and the Windows Calculator should show.

Usually if you are at this point, it will not start. If that is the case do the following to correct this.

  1. Get a database backup
  2. Go offline Edit
  3. Export everything under the Cyberstation to a text (dmp) file and verify it's contents.
  4. Delete the Cyberstation and it's folder 
  5. Exit Cyber (You will get an error that it cannot find the object in the database - click OK)
  6. Open Database Initialization and select Workstation and re-initialize the WS
  7. Create TestCalc as mentioned above and verify that Calculator opens (It should)
  8. Go offline edit and import the .dmp file that had been created for this Workstation and verify all is working.

Note: If this is on a 64 bit system, the path may need to be changed.

reset_password.bat 

However, if you did not install Continuum Reports in the default directory, you must edit the Reset_Password.bat file and include the DOS installation path after “password” in the run string. 

ie: reports reset password D:\Reports

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 5671
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore