Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Using XBuilder to Control I/NET points

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Using XBuilder to Control I/NET points
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1982 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Using XBuilder to Control I/NET points

Picard Product_Support
‎2018-09-10 06:29 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 06:39 PM

Issue

When a specific application request exceeds the standard capability of I/NET it is sometimes possible to use XBuilder to expand possible applications.

Product Line

TAC INET, TAC Vista

Environment

  • I/NET
  • XBuilder
  • I/NET Host Tool

Cause

When a specific application request exceeds the standard capability of I/NET it is sometimes possible to use XBuilder to expand possible applications.

Resolution

This is a sample access control application to demonstrate the possibility. Minimum requirements for this are :Xenta 527 Web Server. If you wish to use Menta Programming, use a Xenta 731 or Xenta 913.

Application: Customer Requests an Audible Buzzer be triggered when a door is forced open, but not shut off until the alarm has been acknowledged.

  1. Create a DO point to controller your buzzer/light/alarm indicator (buzzer DO)
  2. Create an internal AO point to function as a translator (logic AO)
  3. Add a Calc to the buzzer DO: ~(P0=C0) where P0 is the logic AO and C0 is 80
  4. Perform a Station save
  5. In XBuilder, create a project for the 527 Web Server
  6. Insert or re-insert the I/NET network
  7. Add a connection object
  8. Drag the Flags attribute of the Doors DO point to the "from" part of the connection object
  9. Drag the Value attribute of the logic AO point to the "to part of the connection object
  10. Generate the Project and Send to Target.

The response time of the buzzer coming on or going off is dependent on the Scan interval of the buzzer DO.  The reason it works is that the flag attribute of the Door point will equal exactly 80 if you have an alarm flag and the point is still in alarm (the alarm has a value of 64 and unack has a value of 16 totaling 80. See Decoding the I/NET signal "flags" attribute for more information). The door point will stay in alarm until it is acknowledged so this will stay at 80 until someone acknowledges the alarm, or puts the point in Manual/Test.  The Buzzer will not activate if the point is in Manual or Test

The above solution will trigger off any alarm specified from the door editor (Door Open To Long, Door Forced, Bad Card read, etc).  Turn off the other possible alarms, or create an addition internal point labeled Door Forced.  The Door DO point can trigger an event sequence based on Forced door to control the additional point. If you do this the calc will need to be modified to ~((P0=C0)|(P0=C1)|(P0=C2))  C0=16 C1-64 C2=80. This will allow for the buzzer to be on until the point has been acknowledged and return to normal

Labels (2)
Labels:
  • TAC INET
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 6261
  • digital
  • output
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore