Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,841
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 101
    • 102
    • 103
    • …
    • 507
  • Next »

Get "Error: Device type specified in MTA file is not what TAC Vista expected, Info: Download Application and Parameters" when downloading to a Xenta controller from TAC V...

Issue Get "Error: Device type specified in MTA file is not what TAC Vista expected, Info: Download Application and Parameters"  when downloading to a Xenta controller from TAC Vista. Environment TAC Vista TAC Xenta 30x, 28x, 401 Cause The type of controller that you specify in the device specification in the Menta application have the be to exact type you are downloading to. So either there is a mismatch or there is another controller on the network with the address you are using. Resolution Right click and Edit the controller in TAC Vista Workstation. Log in to view the Menta application Check in Options > Device Specification that it is the right type. If not, change to the right type.
View full article
Picard Product_Support
‎2018-09-06 01:53 PM

Labels:
  • TAC Vista
2041 Views

TGML Graphics Editor Error: Could not load file or assembly vjslib

Issue Error: "Could not load file or assembly 'vjslib, Version=2.0.0.0, Culture=neutral, PublicKeyToken=b03f5f7f11d50a3a' or one of its dependencies. The system cannot find the file specified." when starting TGML editor    Can not start TGML editor. Product Line TAC Vista Environment TAC Graphics TGML editor Cause TGML editor needs Microsoft Visual J#® 2.0 Redistributable Package to be installed on the machine for the TGML editor to run. If this for some reason is missing it needs to be installed. Resolution Go to the following link http://www.microsoft.com/downloads/en/confirmation.aspx?FamilyID=e9d87f37-2adc-4c32-95b3-b5e3a21bab2c Download and install the program
View full article
Picard Product_Support
‎2018-09-09 09:44 PM

Last Updated: Lt. Commander Ramaaly Lt. Commander ‎2023-03-30 12:48 PM

Labels:
  • TAC Vista
2025 Views

Cannot see third party LON devices when using the I/A Series Lon Device Manager to find and learn the devices on the LON Network.

Issue Cannot see third-party LON devices when using the I/A Series Lon Device Manager to find and learn the devices on the LON Network.  The third party devices are known to be defined with a specific Lonworks Domain address. When using the I/A Series R2 (Niagara) WorkPlace Pro to commission LON controllers with specific a Lonworks Domain address, configure the Local LON device to match the Domain Length, Domain ID, and Subnet ID programmed in the third-party device. Environment I/A Series R2 (Niagara) WorkPlace Pro UNC 520 Third party LON controllers Cause When a third-party network management tool is used to define and configure / commission a LON network, the commissioning tool frequently uses specified domain address instead of the default "zero-length" domain address.  When using the I/A Series (Niagara) R2 WorkPlace Pro to learn a previously commissioned network, Workplace Pro will not be able to discover the LON devices until it has been configured to match the domain address of the network. Resolution Perform the following steps using WorkPlace Pro to configure the LON interface of the UNC and to learn the LON network. Open the Netmgmt page for the Local Lon Device then set the domain length and domainId to match the domain address of the device.  Apply the changes.  (See example here). Open the Properties page for the LocalLonDevice and select the Engineering tab.  Set the subnetId to match the subnet address of the devices.  (See example here). Recommission the Local Lon Device. Use the Lonworks Device Manager to find and learn the devices on the LON network.
View full article
Picard Product_Support
‎2018-09-10 06:34 AM

Labels:
  • TAC IA Series
2019 Views

Unable to use a Feature of Power Monitoring Expert due to license limitation

Issue Unable to use a Feature of Power Monitoring Expert due to license limitation.    Environment Power Manager Power Monitoring Expert Cause Open the PME Management console Select Help>About You should see the active License Modules as shown below. You may or may not also see additional features that are part of the 90 day trial.   Resolution Contact your sales representative to purchase the additional licenses
View full article
Picard Product_Support
‎2018-09-11 07:10 AM

Labels:
  • CCTV
  • EcoStruxure Building Operation
2028 Views

Only getting the RTN of an alarm (or vice versa)

Issue When point goes in alarm nothing is displayed in the active alarm viewer but when the point returns to normal the RTN shows up in the alarm viewer. Environment CyberStation Cause The Alarm Enrollment allows you to specify the transitions that gets sent to the active alarm viewer, make you the appropriate check boxes are checked. Resolution Configure the alarm enrollment to deliver both the alarm and the RTN
View full article
Picard Product_Support
‎2018-09-11 12:59 AM

Labels:
  • Andover Continuum
2030 Views

Gathering Trace Log information for the Infinet bus in EBO.

Issue There is a performance issue affecting the Infinet bus under an AS-P. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Premium Cause Product Support has requested a Trace log with increased reporting for use in troubleshooting the Infinet bus.  Resolution 1. Under the System Tree in Workstation, expand the Modules folder.        2. In the Module folder, under the Trace folder expand the Loggers folder.   3. Under Loggers, navigate to the following modules. nsp.pin.BACnet.Continuum nsp.BACnet.Continuum (EBO versions 2.0 and below only). 4.  Right click on each module to expose the module Properties and increase the reporting level to Trace.     5. Just below the Loggers folder, right click on the Trace Settings folder.   6. In the context menu under Trace Settings, select Get trace log.     The Trace log will appear as a text file in a text editor.  Save the log to an appropriate folder.   Be sure to return the reporting level on all modules to Information once you are finished gathering the logs.   Leaving the reporting level at Trace will fill up the Trace logs with Infinet log entries leaving very little room for anything else. 
View full article
Admiral StephenYang Admiral
‎2019-04-26 12:39 PM

Last Updated: JohnBoehmer Schneider Alumni (Retired) ‎2019-06-10 08:06 AM

Labels:
  • EcoStruxure Building Operation
2033 Views

Workplace Tech error "Server Busy" when trying to configure communications.

Issue Workplace Tech error POP-UP "Server Busy.... action can't be completed because the other program is busy. Choose 'switch to' to activate the busy program and correct the problem."  when trying to configure communications.   Environment Workplace Tech Tool, revision 5.x  OpenLDV 3.40 OpenLDV 4.0 Cause Possible causes: 1. Multiple versions of Echelon drivers installed. 2. WinPcap may have been uninstalled, quarantined, or blocked. Resolution Only one version of LDV32.DLL should exist on the system and it should be the latest version.  WorkPlace Tech 5.7 and later uses OpenLDV 3.40 or OpenLDV 4.0. Verify the following: OpenLDV 3.40 or later is the only Echelon driver installed in the Windows Control Panel Add/Remove Programs dialog.  If the LonWorks PCLTA-20/PCC-10/PCLTA-10 for Windows is installed, do the following: From the Control Panel, Add/Remove programs, uninstall the OpenLDV driver Uninstall the PCLTA-20/PCC-10/PCLTA-10 for Windows driver. Reinstall the OpenLDV driver. Search the hard drive to locate all LDV32.DLL files on the pc.   Make certain all the LDV32.DLL files found are the same version as is found in the \LonWorks\Bin folder.    Verify the LON Flow Balance still communicates, if applicable. Verify winpcap 4.1.2 installed.  Use the link below to download and install WinPcap, if required.  http://www.winpcap.org/install/default.htm  UNCHECK THE FOLLOWING DURING INSTALLATION, UNLESS YOU HAVE UAC (User Account Control, in Windows 7 and Windows Vista) ENABLED!  If UAC is enabled, the checkbox should be CHECKED!
View full article
Picard Product_Support
‎2018-09-10 05:02 AM

Labels:
  • TAC IA Series
2025 Views

Error: "Ensure that Vista Server is started" when trying to log into TAC Vista Workstation. The server is started.

Issue Error states: "Ensure that Vista Server is started" when trying to log into TAC Vista Workstation. The server is started. Product Line TAC Vista Environment TAC Vista Workstation 4.2.5, 4.3.0-4.5.0, 5.0.0 and higher Microsoft Windows XP Service Pack 2 Cause Microsoft Windows XP Service Pack 2 has security changes/upgrades from previous service packs.  This affects the DCOM permissions that Vista Server relies on. a variety of other reason could result in an error in DCOM parameters in later operating systems. Resolution Vista 4.2.5 Apply settings described in this TPI to get TAC Vista to work properly. Vista 4.3.0-4.5.0 Apply settings described in this TPI to get TAC Vista to work properly. Vista 5.0.0 and higher Apply settings described in TAC Software Installation Manual available on The Exchange Download Center. This can be done using the DCOM Utility in Helpful Vista Utilities - Configure DCOM instantly, Register ASP.NET. Error Message: Ensure that Vista Server is started lists manual steps to access DCOM.
View full article
Picard Product_Support
‎2018-09-07 01:31 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:53 PM

Labels:
  • TAC Vista
2021 Views

What is the IP Network bandwidth requirement for a Continuum controller?

Issue What is the bCX and NCII required bandwidth? 10Mb, 100Mb Network Connections, GSM Modems. Environment Continuum Ethernet level controllers: ACX57xx, Netcontroller II and bCX1 Cause IT Departments often ask for the required IP Network bandwidth for the CX and bCX controllers; as it is not listed on the datasheets. Is there a bandwidth calculator available? Resolution The Network usage of a bCX/ CX/ ACX controller will vary constantly depending on what is happening on the system at the time. It will be affected by user commends, Graphics, Plain English programming, Access events, reloading or re-flashing controllers and time triggered events. The 2nd generation controllers network connection supports a 10Mb half duplex or 100Mb full duplex auto sensing permanent connection. Note: Older 1st generation controllers (CX9200, CX9400, CX9900 series) only support 10Mb half duplex. So a corresponding up to 10Mb or 100Mb connection would be ideal. GSM Modem or other packet based communication networks are unlikely to be able to provide the continuous data throughput required by Continuum. In terms of bandwidth an absolute minimum of 1Mb in both directions is recommended but this will depend on the specific site requirements you have, for example if there is a requirement to update graphic or alarm values within a specific time then a 10Mb connection would be more appropriate. The following Bandwidth Calculator can be used to determine the % network usage on a 10Mb network connection. This was created specifically for typical Access Control projects, so for HVAC applications the following should also be considered: data logging, PE programs passing data, IP based X Drivers. Fill in the appropriate values in Column D for the system: Bandwidth Calculator.
View full article
Picard Product_Support
‎2018-09-10 03:09 AM

Labels:
  • Andover Continuum
2024 Views

Security Expert PSU has Fault Icon lit and Status Light Flashing Red

Issue Security Expert PSU has Fault Icon lit and Status Light Flashing Red Every 3 Seconds indicating an issue with PSU Addressing Product Line EcoStruxure Security Expert Environment Security Expert PSU Cause The module address 254 is the default value which all modules are shipped with and is outside the range the controller can accept. This must therefore be changed during commissioning. See Page 41 of the Operator Reference Manual for details. There is an overall limit of 250 modules that can be connected to a single controller with the following limit on each type of module: Keypad Modules: 200 Input Expanders: 248 Reader Expanders: 64 Output Expanders: 32 The module addressing is defined per module type not by the position of that module on the network. You could have all modules at the same address as long as they are all different types. Example: With the following modules we could have all modules be set to use address 1: 1 x Controller 1 x Keypad 1 x Reader Expander (In this case onboard Reader) 1 x Analogue Expander (PSU) Resolution 1. Right Click on the SP-C Controller and select Module Addressing. Change the Address of the Analog Expander (PSU) from its default value of 254 in this case to a value of 1. 2. Then Update all Modules. 3. Select the Analog Expander (PSU) in the System and also change its Physical Address to also be 1. Save the changes. 4. The PSU should now come online and the Fault Icon on the PSU will no longer be lit.
View full article
Picard Product_Support
‎2018-09-10 07:49 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-12 12:17 AM

Labels:
  • EcoStruxure Security Expert
2034 Views

Xenta Servers support in StruxureWare Building Operations

Issue Are Xenta Servers supported in StruxureWare Building Operations? Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Xenta 701, 711, 721, 731, 511, 527, 555 Cause Want to use Xenta Server as a controller in StruxureWare Building Operations. Resolution No there are no special support for Xenta servers. But you can add them as normal LonWorks devices. You can only read/write SNVTs from the Xenta server. Normal Lon rules applies here, you can have a maximum of 64 nodes to a segment (we recommend to keep it under that). TAC Xenta Server I/O modules will not be seen in StruxureWare Building Operation, but they will count towards the 64 nodes on the segment. See Maximum number using StruxureWare Building Operation (Scalability and Capacity) for more information on Lonworks units in StruxureWare Building Operation.  
View full article
Picard Product_Support
‎2018-09-10 12:06 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2022-08-12 01:47 AM

Labels:
  • EcoStruxure Building Operation
2023 Views

Web Service XML response empty and Web Service offline right after successfully creating it

Issue Right after successfully creating a simple XML Web Service all the values show 0 and the Web Service is offline Product Line EcoStruxure Building Operation Environment Simple XML Web Service Workstation Enterprise Server Automation Server Cause Possible cause 1: SmartStruxure Workstation can handle URL's both with and without the final forward slash even if the URL is just an IP address and a port number. The ES or AS can't handle that, and so after creating the variables through Workstation, the Web Service goes offline after it is added to the server. Possible cause 2: The XML file or response is not UTF8 encoded but "UCS-2 LE BOM" encoded or something else. Resolution Solution 1: Add a final forward slash to the Web Service URL - e.g. http://localhost:8000 should be http://localhost:8000/ Solution 2: Make sure the XML file is correctly encoded in UTF8 - you can check and change the encoding with e.g. Notepad++
View full article
Picard Product_Support
‎2018-09-11 09:06 AM

Labels:
  • EcoStruxure Building Operation
2020 Views

How should the MZ20A / MZ20A-R actuator be connected?

Issue Connection details for the MZ20A / MZ20A-R actuator. Product Line Field Devices Environment MZ20A-R Wiring Connections Cause How do the cable colours relate to the connection numbers on an MZ20A / MZ20A-R actuator? Resolution The MZ20A / MZ20A-R actuator connection details are shown below.   For the actuator data sheet please click .HERE
View full article
Picard Product_Support
‎2018-09-10 11:32 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-14 11:12 PM

Labels:
  • Field Devices
2030 Views

BBMD table limits in EcoStruxure Building Operation

Issue Continuum has a limit on the number of entries that can be added to the BBMD table in the bCX and CyberStation. Do the AS and ES servers have the same limitation? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server (AS-P, AS-B) Building Operation Enterprise Server Continuum Cause Limitations must be known for engineering design. Resolution The number of BDT Entries you can add to the BBMD table in EcoStruxure Building Operation is limited only by the available resources, so for all practical purpose there is no limit. Device BDT (Broadcast Distribution Table) FDT (Foreign Device Table) ES only limited by memory 64 (up to v1.4) 600 (from v1.5) AS only limited by memory 64 (up to v1.4) 254 (from v1.5) ASB only limited by memory 50 bCX1 32 32 Cyberstation 1024 1024 Always refer to the Architectural Guidelines for the latest information
View full article
Picard Product_Support
‎2018-09-06 10:31 AM

Last Updated: Sisko DavidChild Sisko ‎2022-02-10 07:38 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
2034 Views

License Administrator fails install on uninstall process

Issue License Administrator fails install with an "Uninstall failed, installer cannot continue" error Product Line EcoStruxure Building Operation Environment Building Operation License Administrator Cause Building Operation uses Flexera (Revenera) Software Technology for licensing. Other Schneider-Electric products may also use this technology for their licensing. Resolution Check to see if the site has other software programs/products using the Flexera (Revenera) Software Technology. Other Schneider Electric offers such as Unity Pro - IEC Programming Software for Modicon PAC, Power Monitoring Expert & TAC Vista as well as third party programs also use Flexera (Revenera) for their licensing. During installation of the Building Operation License Administrator the dialog below is shown: The default behavior of the Building Operation License Administrator installation program is to install both Building Operation License Administrator and a new local license server instance. If the default behavior is accepted, the installation program will attempt to uninstall any previously installed local license servers. If the Building Operation License Administrator installation program  does not have sufficient access rights to uninstall the license server previously installed by another product a "Failed to install Building Operation License Administrator" error will occur.   Multiple products can share a single Flexnet License server instance. If there is an existing Flexnet install then the License Server checkbox should be unchecked during installation of the Building Operation License Administrator This leaves the existing local license server installed by the other product intact, while still allowing Building Operation License Administrator to run. The license server used by Building Operation License Administrator can easily be changed by the user on the License Server Address tab in Building Operation License Administrator, if necessary.  
View full article
Picard Product_Support
‎2018-09-06 10:05 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-21 04:47 PM

Labels:
  • EcoStruxure Building Operation
2038 Views

Configure REX button to be able to permanently lock or unlock a door

Issue Configure REX button to be able to permanently lock or unlock a door if pressed for a set amount of seconds. Product Line EcoStruxure Security Expert Environment Security Expert Server Cause REX button does a momentary unlock then relatches the door. Would like to unlock or lock doors using the REX as determining factors are too dynamic to use a schedule. Resolution What is needed 2 Inputs (A & B) 4 Outputs (A, B, C, D, & E) 4 Programmable Functions (A, B, C, & D) 1 Dummy Area (Test Area) 2 Input Types (Input Triggers Output & Input Toggles Output) 1 Door with REX connected (Door X) Inputs Input A (REX Button) General Tab Control Output: Output A Areas and Input Types Tab Area: Test Area Input Type: Input Triggers Output Input B General Tab Control Output: Output E Areas and Input Types tab Area: Test Area Input Type: Input Toggles Output Input Types Input Triggers Output Options 1 Tab Generate Alarms checked Options 3 Tab Activate Input Control Output on Alarm checked Deactivate Input Control Output on Restore checked Input Toggles Output Options 1 Tab Generate Alarms checked Options 3 Tab Toggle Input Output State checked Outputs Output A, B, C, and E are just standard virtual outputs Output D General Tab Activation Time (seconds): the amount of time you want to hold the REX to activate the unlock/lock (I.E. 5 seconds would require you hold the REX button for 5 seconds) Programmable functions: Programmable Function A: Type: Ripple Output Output to trigger: Output A Stage 1: Output B Stage 2: Output C Inter Stage on Ripple Time: 5 Programmable Function B: Type: Logic Control Logic Function Mode: 7 Follow Logic And First Output to Check: Output A Second Output to Check: Output C Output to Control: Output D Programmable Function C: Type: Input follows Output Input follows Output: Input B Output to follow: Output D Programmable Function D: Type: Door Control Door Function Mode: 0 Follow and Test Output Door control Mode: 1 Latch Door unlock Output to Check: Output E Door to Control: Door X Make sure you right-click each programmable function and start them. Go to the Test Area and set it to Armed.
View full article
Commander JonGreen Commander
‎2020-03-11 07:23 AM

Last Updated: Kirk AdamSteele Kirk ‎2024-11-26 08:56 PM

Labels:
  • EcoStruxure Security Expert
2041 Views

EBO doesn't support upload function from B3 controllers

EBO doesn't support save from controller for B3s
View full article
Admiral StephenYang Admiral
‎2019-01-04 12:00 PM

on ‎2019-01-04 12:00 PM

Labels:
  • EcoStruxure Building Operation
2024 Views

Holidays in Access Expert

Issue A site configured a schedule to have 2 different holiday durations during a spring break holiday week. The schedule is not working as expected. The Holiday week is set up as a range for Monday - Friday and assigned to a single Holiday group.   Two new schedule durations have been added with the respective days selected that they would like the durations to activate on. On the 2 new durations, they added the Holiday group in the "Always Active On" area.   Product Line EcoStruxure Access Expert Environment Access Expert V3 Hosted Access Expert V3 Premise Cause Holiday and special date durations will activate on the holiday dates regardless of the day(s) of the week selected in the scheduled duration. The day(s) of week checkboxes in each duration is only used for setting a recurring weekly activation on those days and are not required for Holidays. For durations that will only be used during holidays, do not select any day(s) of the week. Resolution In this case, since you need two different durations during your holiday week, you will need two new durations but with different holiday groups for each duration. Set the M, W, and F duration as holiday group A and T, R for holiday group B. Now apply the Holiday Groups to the right dates via the Holidays Menu.      
View full article
Commander JonGreen Commander
‎2022-12-29 09:26 AM

on ‎2022-12-29 09:26 AM

Labels:
  • EcoStruxure Access Expert
2023 Views

Failed to call pILiveData error when editing Schedule object in Continuum 1.94

Issue After upgrading to Continuum 1.94, Cyberstation throws the following error: Failed to call pILiveData -> GetLiveData().  ACDataServices has an error. Product Line Andover Continuum Environment Continuum 1.94 Schedule Error Cause This behaviour is due to a bug that was described in TPA-BOST-12-0002 00 Schedule Exception Errors. Resolution Install the CyberStation v1.94 SP1 - Software which can be found on the Exchange Extranet.
View full article
Picard Product_Support
‎2018-09-11 07:25 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-30 06:14 AM

Labels:
  • Andover Continuum
2016 Views

Reports Tree not shown when logging in to Web Reports

Issue When logging in to Web Reports, the "Reports Tree" to the left is not shown, and an error message is shown stating that login has failed for the user "NT AUTHORITY\IUSR". Product Line EcoStruxure Building Operation Environment Building Operation WebReports Cause This is a result of not following the Web Reports installation guide.  The SQL Server must be installed with an instance name, and the SQL Server must be started by the user "SYSTEM". Resolution There are two solutions to this issue: Reinstall the SQL Server and Web Reports following the installation guide Use the SBO Reports Agent Config tool on the Community to give access to the 'NT AUTHORITY\IUSR' Alternatively for a more in-depth answer consult How to Fix Login Failed For User NT AUTHORITY IUSRS to add the user "NT AUTHORITY\IUSR" to the SQL Server
View full article
Picard Product_Support
‎2018-09-11 01:45 PM

Last Updated: Sisko GavinHe Sisko ‎2024-09-17 05:33 AM

Labels:
  • EcoStruxure Building Operation
2018 Views
  • « Previous
    • 1
    • …
    • 101
    • 102
    • 103
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of