Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

LON device can communicate in Vista, but fails in a Xenta Server / XBuilder

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • LON device can communicate in Vista, but fails in a Xenta Server / XBuilder
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Benji
    Benji
  • CraigEl
    CraigEl
  • SESA116857
    SESA116857
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2144 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

LON device can communicate in Vista, but fails in a Xenta Server / XBuilder

Picard Product_Support
‎2018-09-07 03:34 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:17 AM

Issue

Vista Server can read values on a LON device, but when this same device is used in an Xbuilder project for a Xenta Server no values can be read.

Product Line

TAC Vista

Environment

  • FT-10 LON Network
  • Xenta Server
  • Xenta 511, 527, 701, 711, 721, 731, 913

Cause

The XIF file of the LON Device does not conform to LonMark standards for self documentation. Vista Server can recover from this and assumes all SNVTs are from the default function block, but XBuilder cannot.

On the third line of each variable declaration is the self documentation:

1: VAR nvo01Value 2 0 0 0
2: 0 1 63 1 0 1 0 1 0 1 0 0 0
3: "@1|2

The correct format is to show the functional block number and the member number separated by either a | or # character.

Improperly formatted self documentation include the following:

  • "nvo01Value - Does not define the function block or member number.
  • "@_1|_1 - Uses _1 which is not a valid number.
  • "&3.4@0,20000-MP580 - Uses a - (dash) which is not valid

It can also be because SNVTs from devices are bound directly to Menta programs in a Xenta 7XX. If the procedure below doesn't solve the issue, refer to Graphic values not updating in a network that includes a Xenta 7XX.

Resolution

The XIF file must be edited to correct the self documentation.

  1. Right click on the controller in Vista Workstation and open the properties window.
  2. On the XIF file tab find the file name of the XIF file. Open this file from the $thisfil directory in the Vista database folder.
  3. Modify the XIF by manually correcting these invalid lines of self documentation. It is recommended to use the default function block (0) and start with member index 50 to ensure no overlap. Increment the member number for each SNVT.
    "@0|50
    "@0|51
    ....
  4. Once the XIF file has been updated save it under a new name in the $thisfil directory.
  5. In the device properties browse to the new XIF file.
  6. Log out of workstation.
  7. Log in to workstation.
  8. Insert the LON network into Xbuilder.
  9. Generate the project and send to the device.
Labels (1)
Labels:
  • TAC Vista
Tags (2)
  • Find more articles tagged with:
  • 4051
  • underscore
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of