Issue
Values are coming into Vista without issue but do not update on the graphics in the Xenta 7XX.
Product Line
TAC Vista
Environment
- Workstation
- Graphics
- Xenta Server 701, 711, 721, 731
Cause
If there is a Xenta Server in the database, when connection objects are not used to bind values between a controller and a Menta program in the Xenta Server, this graphic update can occur.
It can also be because of the XIF for a device being formatted incorrectly. If the procedure below doesn't solve the issue, refer to LON device can communicate in Vista, but fails in a Xenta Server / XBuilder
Resolution
There are two options to correct this issue:
- Re-engineer the XBuilder project to use connection objects between the controller and the Menta program in the Xenta controller.
- The control task speed of the Menta program in the XBuilder project can be changed to a lower speed setting.