Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Access Expert unable to bring interfaces(downstream devices) online

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Access Expert unable to bring interfaces(downstream devices) online
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Alan_Wood
    Alan_Wood
  • DavidFisher
    DavidFisher
  • BillNeville
    BillNeville
  • sesa119747
    sesa119747
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2039 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Access Expert unable to bring interfaces(downstream devices) online

Picard Product_Support
‎2018-09-06 08:35 AM

Last Updated: Administrator CraigEl Administrator ‎2023-07-13 05:08 PM

Issue

Unable to bring interfaces(downstream devices) online, showing as unknown

Product Line

EcoStruxure Access Expert

Environment

  • Access Expert in Cloud or On-Premise
  • SSC (Security System Controller)
  • Downstream controllers

Cause

Offline interfaces can occur under a number of circumstances, below are the most common reasons.

  1. The controller is not yet active. Once all interfaces, readers, and I/O have been added, it’s important to remember set the device as active.
  2. Interfaces were added to the controller after it was made active. The controller requires a reboot to download the correct configuration.
  3. Dipswitches and addressing on the board may be incorrect
  4. Check Wiring 

Resolution

Go through the following steps to get interfaces online

  1. Set the device as active (Go go back to the controller page )
  2. Reboot the controller (containing the interface)
  3. Check that the DIP switch settings are correct on the controller (see the Mercury hardware manual)
    Switches 1-5 on an interface module set the address in binary, this means 32 addresses are available (0-31). Users must set the correct address inside Access Expert that matches the DIP switch value. Switches 6 & 7 set the Baud rate, both on for default 38400. Switch 8 should be off to disable AES key encryption. (Communication is instead encrypted over TLS 1.2)

    Note: The orientation of the DIP switches may be upside down compared to some labels on other connectors, so it's easy to have everything inverted. On this MR52 board, the On label on the connector is DOWN.
    These dip switches are configured for address 0, baud rate 38400, and no encryption.
    MR52 Dip Switch Orientation.png
  4. Check wiring
  5. Ensure that the panels are wired correctly. Verify your RS485 communication and refer to the hardware installation guides
  6. Verify End of Line Termination
  7. Verify End of line termination jumpers are set, refer to hardware installation guides
Labels (1)
Labels:
  • EcoStruxure Access Expert
Tags (4)
  • Find more articles tagged with:
  • 18967
  • AlanWood23
  • controllers
  • downstream
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of