How to set up a door for keypad OR card validation

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to set up a door for keypad OR card validation
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Carl_Slack
    Carl_Slack
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2333 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to set up a door for keypad OR card validation

Picard Product_Support
‎2018-09-06 02:54 PM

Issue

Sample Plain English program to set up a door to allow for either keypad OR card validation.

Environment

  • Continuum
  • Plain English
  • Infinity
  • NetController

Cause

Allowing the NetController to respond to a keypad as well as a card reader allows for flexibility in the security solution.

Resolution

How do I setup a door for keypad OR card validation

Create the following InfinityProgram in the NetController for each door. Change each program to the correct door name.

NOTE: If using this program, make sure that you do not have validate pin mode selected on the entry reader tab of the door editor.
--------------------------------------------------------------------------------------------------
'Looping, AutoStart Program

'Change officedoor to the name of your door
Watching:
IF officedoor\doorfault IS 2 THEN '0 for normal operation 2 if Fault (Tamper) detected
officedoor\entrynormmode = 8 'PINMode

officedoor\entrynocommmode = 8 'PINMode

GOTO Counting
ENDIF

Counting:
IF TS > 5 THEN 'Wait 5 seconds before switching back to SiteMode + CardMode
officedoor\entrynormmode = 3 'SiteMode + CardMode

officedoor\entrynocommmode = 3 'SiteMode + CardMode


GOTO Watching
ENDIF
---------------------------------------------------------------------
Press the # key once, it will place the door in PINMode (8) for the 5 seconds then back to SiteMode+CardMode (3).
--------------------------------------------------------------------------------------------------------
Here are the available EntryNormMode and ExitNormMode values

SiteMode = 1
CardMode = 2
GeneralMode = 4
PINMode = 8

If you plan to use more than one add the two numbers together (Example: SiteMode + CardMode + PinMode = 11)
------------------------------------------------------------------------------------------------------
Here are the available DoorFault values

1 = Database of doors, areas, and personnel is not functioning normally
2 = Entry Keypad is being tampered with
4 = Exit Keypad is being tampered with
8 = Entry Card Reader is being tampered with or has failed
16 = Exit Card Reader is being tampered with or has failed

---------------------------------------------------------------------------------------------------------
My Test case:

I created a person with a valid card and a valid PIN. When I used the card the door would open, after relock I pressed the # and immediately entered the PIN plus the #, the door unlocked.

If you have a door switch you could probably use it instead of the 5 second timer this would give you a little more control over the door so that the next person in line (with a card) would not have to wait.

CyberStation (v1.52.0.20021120)
NetController (v1.520010)
AC1 (v22)
HID ProxPro with Keypad

Note: this works on an ACX(5740/5720) also

IMPORTANT:

The sample PE program above only sets the EntryNormMode of the door. The program needs to set also the EntryNoCommMode and possibly the EntryNodataMode. If the door is a dual reader door then the corresponding attributes on the exit side of the door must also be set.

Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 2770
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore