Issue
When using the IC_LON Plug-in, an error is reported:
Unknown SNVT Type: nn
This indicates that the SNVT (Standard Network Variable Type) is not supported by the IC3-LON controller.
Product Line
Satchwell BAS & SigmaEnvironment
Sigma IC-LON Version 1.E
Cause
The Sigma IC3-LON controller is designed to work with LONMARK Resource Files Version 11. However, not all SNVT types defined in this version are supported by the controller.
Resolution
To resolve this issue:
-
Verify Supported SNVTs
Refer to the IC3-LON Release Notes to confirm which SNVT types are supported. -
Avoid Unsupported SNVTs
If an unsupported SNVT is required, consider alternative approaches such as:- Using a supported SNVT with similar functionality.
- Reconfiguring the device or network to bypass the unsupported SNVT.
-
Firmware Reference
See the attached document:
📎 Release_Note_4-05 Firmware_IC3-LON.pdf