Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,899
  • TAC IA Series 1,682
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 496
    • 497
    • 498
    • 499
    • 500
  • Next »

How to generate an invalid attempt alarm

Issue How to generate an invalid attempt alarm. Product Line Security Expert Environment Security Expert Cause It is not clear how an alarm for an invalid attempt at a Door is configured. Resolution The easiest way to setup an alarm to trigger when an invalid attempt is made at a reader is to trigger an Alarm off of the required Event. An example would be: Under Events create a new Event Filter, go to Event Types tab, un-tick "Include all event types" and add the events you want to monitor. In this case "User Door Group Not Valid At Door Using Access Level" should suffice as a start. To ensure you have the correct events you can create the event condition and confirm exactly what the event recorded is. Under Events create a new Alarm and set the Event Filter to the Event filter you created in step 1. Under Monitoring setup a Status Page that includes All Alarms (or alternatively is filtered for the specific alarms you want to see).
View full article
Picard Product_Support
‎2018-09-06 07:34 AM

Labels:
  • EcoStruxure Security Expert
1964 Views

Using the Save command in Plain English programs

Issue When the Save statement is used to save objects in a BCX4040 to the database. Steps to reproduce problem: Create an InfinityString object (Test.Str) with a manual array size of 1 in a BCX4040. Create a program in the BCX that sets the value of Test.Str[1] to 'Success' From command line, print the value of Test.Str[1] while the workstation is in OnLine mode. The value should = 'Success' From command line, print the value of Test.Str[1] while the workstation is in Offline mode.  No value should be returned as the value has not been updated in the database. Create a fallthrough/autostart program in the workstation with the following code: FIRSTLINE: Save \TestNet\TestACX\Test.Str -0 Goto StopLine STOPLINE: Stop From command line, print the value of Test.Str[1] while the workstation is in Offline mode.  The value should now = 'Success'.  Expected result: The value returned for Test.Str when the workstation is in Offline mode (Database value) should 'equal the value returned when the workstation is in Online mode (Live Value), i.e. = Success' Actual result: The Offline value of Test.Str[1] does not change and does not equal the value live value. The resulting ACC_Dump_Debug that is produced is found to have no contents. Product Line Andover Continuum Environment Continuum  Plain English Cause The following Plain English code does not accomplish a Save to Database. FIRSTLINE: Save \TestNet\TestACX\Test.Str -0 Goto StopLine The functionality of the Save command is not to perform a "Save to Database" operation. This is a functioning as designed. The Save command, which is equivalent to the Dump command, dumps the contents of the passed-in arguments (i.e. objects) to a file if provided Resolution Workaround: When a manual Save to Database is done on the object, the database value is updated with the current Live value.
View full article
Picard Product_Support
‎2018-09-06 07:34 AM

Labels:
  • Andover Continuum
1490 Views

Default List views are missing columns after being re-created with Continuum database initialization update database option.

Issue After a missing or deleted default list view is re-created using the Continuum database initialization utility; the list view does not contain any columns. Environment Cyberstation Cause This issue is caused by a Continuum defect issue that cannot be corrected at this time. QC#2222. Resolution There are several workarounds that can be used to resolve this issue. 1)      Columns can be manually added back to the list views re-created by the database update option. 2)      The default list views can be reimported from the DefaultListViews.dmp file in the Continuum folder.  This would overwrite all default list views there by losing any customization to existing list views. 3)      Individual list views can be imported from a dump file created from another Continuum Systems to provide pinpointed recovery of certain listviews.
View full article
Picard Product_Support
‎2018-09-10 12:55 PM

Labels:
  • Andover Continuum
1228 Views

Error when saving photo in Badge Manager: Invalid width/height -11

Issue After selecting a photo and trying to save it in the Image Enhancement screen, the error Invalid width/height -11 pops up.   Environment Cyberstation Cause This is caused by the resize box under the capture options being checked and the sizes being set to 0. Resolution This can be resolved by one of the following suggestions below:   Uncheck the resize box under the capture options Set the x: and y: options to something other than 0
View full article
Picard Product_Support
‎2018-09-10 11:41 AM

Labels:
  • Andover Continuum
1792 Views

License no longer appears in License Administrator after re-installing Open Minds HAS.

Issue After re-installing Open Minds HAS causes, the license no longer appears in License Administrator. Environment License Open Minds HAS 8.6   Cause Re-installing LifeKeeper may have affected License Administrator installation due to the Open Minds volume monitor. Resolution Re-install License Administrator. Licese will show and operate after re-installation.
View full article
Picard Product_Support
‎2018-09-06 07:32 AM

Labels:
  • EcoStruxure Building Operation
1350 Views

Supported web-browsers for Access Expert hosted instance

Issue It is not documented what web-browsers should be used with an Access Expert hosted instance. Product Line Access Expert Environment Access Expert hosted instance - V2 & V3 Cause It is necessary to know what web-browsers should be used with an Access Expert hosted instance. Resolution IE 11 or Google Chrome should be used to logon to an Access Expert hosted instance. Firefox is NOT a supported web-browser and should not be used. 
View full article
Picard Product_Support
‎2018-09-06 07:32 AM

Labels:
  • EcoStruxure Access Expert
1828 Views

How to configure heating on SE7600X

Issue Unable to turn the heat on SE7600X   Environment   SE7600 Cause Wiring issue or misconfiguration Resolution You may refer to the diagram below to avoid wiring mistakes. Do not forget  jumper J1 on terminals |RC |RH|     Configuration Two important parameters to configure for heating.   Number of heating stages.  Default value = 2 stages When selected the device will revert the operation of 2 stages thermostat to single stage operation or to modulating 0 to 10Vdc heating output: 0 = 0-10Vdc analog heating output (AO) 1 = 1 heating stage (W1) 2 = 2 heating stages (W1 & W2)   Fan control Default value = On When selecting on; the Terminal Equipment Controller in all cases will always control the fan (terminal G). Valid for On or Auto fan mode When selecting Off; the fan (terminal G), when heating stages (terminals W1 & W2) are solicited, will not be energized. The fan in this case will be controlled by the equipment fan limit control. Valid only for Auto fan mode.   On fan mode will leave the fan always on. For multistage models, fan control applies to W1 & W2 For heat pump models, fan control applies to W1 only (Emergency heat)
View full article
Picard Product_Support
‎2018-09-10 09:47 AM

Labels:
  • EcoStruxure Building Expert
  • Satchwell BAS & Sigma
1553 Views

Where can I find the details for UK and Ireland Smartstruxure or EcoStruxure partners.

Issue Locating partners Environment Partner SmartStruxure Building Operation EcoStruxure Building Operation Cause Require engineer to visit for maintenance, servicing, installation or advice. Resolution Click Here to be linked to the available UK and Ireland SmartStruxure / EcoStruxure partner list. Note: For Ireland, enter Belfast, and partners in Ireland will also be shown.
View full article
Picard Product_Support
‎2018-09-10 08:51 AM

Labels:
  • EcoStruxure Building Operation
1590 Views

Alarm Control Panel - Number of entries for Cause Note, Action Note and Checklist

Issue Alarm Control Panel - Number of entries for Cause Note, Action Note and Checklist  Environment SnartStruxure Building Operation Workstation 1.9 Cause The maximum number of entries that can be added for Cause Note, Action Note and Checklist are not indicated in available documentation.  Resolution There are no hard coded limits to the number of entries that can be added for the Cause Note, Action Note and Checklist
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • EcoStruxure Building Operation
1499 Views

Report Server Localisation

Issue Customers want to know how to localise their Reports Server  Environment SBO 1.9.3. Cause User may wish to change language on produced Reports etc.. Resolution Localisation of the Reports Server is currently not supported although there are plans to add this feature in a later revision.
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • EcoStruxure Building Operation
2220 Views

Badge Printing in Access Expert Version 3

Issue Unable to print a badge preview when designing a layout in Access Expert Product Line Access Expert Environment Access Expert Win8.1 Premise Hosted SQl 2012 R2 SQL 2014 Cause Operating system incompatibility with version 3. Version 3 only support Windows 8.1 and above. Resolution If the user is running Windows 7, the Preview will not work. Use a compatible OS, like Windows 10, and try again.
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • EcoStruxure Access Expert
1734 Views

Personnel Manager not operating correctly but Personnel Editor is fine

Issue Personnel Manager not operating correctly but Personnel Editor is fine Product Line Andover Continuum Environment Seen in Continuum 1.94 Cause Personnel Manager seems to run correctly but the Area names, Assigned and Unassigned data does not show correctly and cannot be modified. Blank spaces at the end of the Area Names or Alias cause the Peronnel data (Assigned and Unassigned Areas) to show incorrectly in Personnel Manager, but all correct in Personnel Editor. Resolution Remove the spaces at the end of the Area Names and Aliases Restart Continuum
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • Andover Continuum
1605 Views

Converting an Access Expert site from V2 to V3

Issue Needing to convert a site from V2 to V3. Product Line Access Expert Environment Win 8.1 and above Hosted Version 2 Version 3 Cause There are no directions on how to convert a Hosted Site on V2 to V3. Resolution When converting from V2 to V3 there are a few things that need to be verified first before attempting this action: Verify that the site does not have any SSC's that are configured as FN-4502, this information would have to be passed on prior to attempting the conversion by creating a case with your local country support group. Once the all clear has been given by product support, then the process can be started. Using two monitors bring up an instance on each for comparison Verify that all users, Access Levels, Schedules, Trigger and Procedures etc are in place Once confident, then connect to each SSC and change the Host IP name from the xxx.accessxpert.com to us.accessxpert.com Click on the View All Hardware Icon to see when the SSC comes online Once this happens, click on the Update firmware to get to the latest version downloaded to the controller When the device comes back online, verify that all the sub devices comes online as well If not then perform a Push Controller Database to the controller again When the controller comes online, all the subdevices should come online as well as Readers etc. At this point everything in V2 will become Unknown and can then be deactivated
View full article
Picard Product_Support
‎2018-09-06 07:30 AM

Labels:
  • EcoStruxure Access Expert
2801 Views

Enrollment Reader in Access Expert

Issue Need to a method to automatically enroll users into Access Expert? Product Line Access Expert Environment Premise Install Hosted Instance Cause Enrollment readers are not used in Access Expert.  Resolution When a card is read at the Door Reader, it will result in an "Access Denied/Card Pin Not Found" event being generated. This event can then be used to create a new user. Once this user has been created and added to the system, the card will become active and have access to the doors it's assigned to. 
View full article
Picard Product_Support
‎2018-09-06 07:30 AM

Labels:
  • EcoStruxure Access Expert
2059 Views

Locked in SmartXKiosk after first-time startup before a password has been set

Issue After starting up the SmartX Advanced Display for the the first time, the operator finds himself stuck in SmartXKiosk mode before having any chance to select a password/PIN code. Product Line EcoStruxure Building Operation Environment Advanced Display v1 Advanced Display v2 Cause SmartXKiosk has been selected as launcher. The first time the SmartX Advanced Display is booted up the operator is presented of a choice to use  SmartXKiosk or TouchWiz as launcher. If SmartXKiosk then is selected instead of TouchWiz the operator will enter SmartXKiosk without having set a password first. Resolution Request an unlock code (PIN) from your local support center, which will enable the operator to exit Kiosk Mode. Press the Home (Hardware) Button at the SmartX Advanced Display. This will enable you to choose launcher again. Make sure that "TouchWiz" is selected. Note: In the next release this will note be an issue, since you are forced to select "TouchWiz" at first use to proceed (if SmartXKiosk is selected, you will be prompted to choose again)
View full article
Picard Product_Support
‎2018-09-06 07:29 AM

Labels:
  • EcoStruxure Building Operation
2442 Views

MPX firmware versions from the controller error log

Issue Converting the entries from an MPX controller error log can be useful when there has been a software revision change. Product Line EcoStruxure Building Operation Environment EBO MPX Cause There may be an entry in an MPX error log that shows as follows: 25 I 2018-07-02 10:07:36.56 0x00006409 0x20000015 0x80018a15 0x10000134 0x18061101 Software revision change Resolution The ability to extract the firmware revision numbers from the controller error log is useful especially if you do not have the device report. Take a look at the last 2 numbers of the following line: 25 I 2018-07-02 10:07:36.56 0x00006409 0x20000015 0x80018a15 0x10000134 0x18061101 Software revision change 0x10000134  == 1.00.01.00134  (please disregard the missing 01) 0x18061101 == 2018 06 11 (ignore the trailing 01 in the hex number)
View full article
Picard Product_Support
‎2018-09-06 07:28 AM

Labels:
  • EcoStruxure Building Operation
2114 Views

Replacement of Satchwell AZ2401 Rotary Actuator due to obsolescence.

Issue Satchwell AZ2401 Rotary Actuator requires replacement. Product Line Field Devices Environment Satchwell AZ2401 Rotary Actuator installed on Satchwell MBF Series Rotary Shoe Valve Body. Cause Obsolescence of Satchwell AZ2401 Rotary Actuator Resolution The Satchwell AZ2401 actuator would normally have been installed on a Satchwell MBF Valve Body. The Actuator comprised a 6 wire electrical connection enabling it to be operated from a Satchwell Z Monotronic or CZT Climatronic Proportional Controller as follows: Terminal 1 – Open signal Terminal 2 – Close signal Terminal 3 – Common Terminal A – 135 ohm Feedback Potentiometer – winding Terminal B – 135 ohm Feedback Potentiometer – wiper Terminal C – 135 ohm Feedback Potentiometer – winding If all 6 wires are connected then the AZ2401 actuator may be replaced by following SE actuators: MD20B-24 + Linkage Kit 914-1070-000 from Schneider Electric and an accessory kit   P140A from Belimo If only 3 wires are connected, that is to terminals 1, 2 and 3 then the P140 accessory kit is not required.
View full article
Picard Product_Support
‎2018-09-06 07:27 AM

Labels:
  • Field Devices
1290 Views

Forta actuator zero point check/adjustment on power up

Issue Is there an option to disable the Forta actuator zero point check/adjustment on power up?  Environment Schneider Electric Forta actuators Cause The Forta actuator running the zero point check/adjustment on power up is causing an issue in the control sequence of the plant.  Resolution It is not possible to disable the zero point check/adjustment on power up of the the Forta actuator by any configuration of the dipswitches. The function is coded into the actuator firmware. 
View full article
Picard Product_Support
‎2018-09-06 07:27 AM

Labels:
  • Field Devices
1333 Views

Issue creating Lon bindings

Issue Trying to create a Lon binding from two or more nvo's in one Lon device (hub) to two or more nvi's in many Lon devices (targets), a so-called fan-out binding. The binding between the first Lon devices works fine, but when trying to create the binding from the Hub Lon device to the second Lon device (target) it does not work. The binding window for the second Lon device (target) is opened; the Lon device (hub) is chosen in the browser window on the right side; and the nvo in the hub is dragged to the nvi in the second target device. But the binding tool will not accept this binding. It is not possible to release the nvo from the Hub Lon device on the nvi in the second target Lon device. Product Line EcoStruxure Building Operation Environment Building Operation Workstation LON Devices Cause Normally when creating a binding using the EBO binding tool you open the binding window for the target (receiver of the value). But in this particular case you need to do it the other way around and open the binding window for the hub (sender of the value) instead, and then drag the target to the hub. Read more about Fan-out Bindings in the Webhelp. Resolution Go to the Lon device with multiple ins or outs (hub) and open the bindings window In the browser window on the right side find the target Lon device Drag the nvi from the target device to the nvo in the hub Lon device
View full article
Janeway Jonas_Brissman Janeway
‎2019-03-22 07:07 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-05-20 07:22 AM

Labels:
  • EcoStruxure Building Operation
1801 Views

Downloading the MP-V Flow Balance Data Object properties to a controller

Issue Unable to download MP-V Flow Balance Data object to a controller using download all Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Multi-purpose VAV Cause The inability to use download all is a protection added to prevent overwriting any flow balance data inadvertently Resolution All Flow Balance Data Object properties are downloaded by explicitly downloading the Flow Balance Data Object as shown in the video below    
View full article
Commander JonGreen Commander
‎2019-03-27 10:43 AM

Last Updated: Guinan RandyDavis Guinan ‎2019-04-15 07:39 AM

Labels:
  • EcoStruxure Building Operation
2816 Views
  • « Previous
    • 1
    • …
    • 496
    • 497
    • 498
    • 499
    • 500
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore