Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: Andover Continuum
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "andover continuum"

View in: "Building Automation Knowledge Base" | Community

2197 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 47
    • 48
    • 49
    • …
    • 110
  • Next »
Label: "Andover Continuum" Show all articles

Unable to open or delete a controller program. Every attempt results in an "A cached program cannot be opened while it is being written" error and program is unable to ...

Issue An  "A cached program cannot be opened while it is being written"  error is displayed when attempting to open a program on a controller.  When attempting to remove the program it does not delete and an error is shown in the distribution Properties - 'A cached program cannot be saved because the synchronization lock times out'.  Environment Continuum Controller Cause The program has not compiled properly in the controller and is in a locked state. Resolution Take the Workstation into offline mode. Export the program to a dump file to back it up. Still in offline mode, delete the program. Reload the controller. Once the reload is complete, create the program again and then add the code from your dump file backup. Save the program and test.
View full article
Picard Product_Support
‎2018-09-10 05:40 AM

Labels:
  • Andover Continuum
1499 Views

How to configure Event Notification object to deliver event to BACnet client

Issue How to configure Event Notification object to deliver event to BACnet client Environment CyberStation bCX4040 b3s Cause Delivery of Event Notifications to BACnet clients Resolution When adding a recipient in the Event Notification object check the BACnet Address check box then in the Recipient field specify whether the delivery will be a broadcast or sent to a specific destination. In the screen shot below, the notification will be delivered to the recipient with the MAC address 01 on the 2801 Network.
View full article
Picard Product_Support
‎2018-09-10 04:54 AM

Labels:
  • Andover Continuum
1586 Views

The bCX and b3 controllers are BACnet compliant, why do they not support all defined BACnet object types?

Issue  The bCX and b3 controllers are BACnet compliant, why do they not support all defined BACnet object types? Environment Continuum BACnet 3rd Party BACnet Device Cause Misunderstanding of what BACnet compliant means and/or misinterpretation of BACnet Product Information Conformance Statement (PICS). Resolution BACnet compliant devices are not required to support all of the defined object types. However, if an object is supported it must comply with the standard object model for that object type. This includes a number of required as well as optional properties. The PICS for a BACnet device is used to define what LAN options the device supports as well as supported objects and optional properties (it’s implied that the required properties are supported and these may or may not be shown in the PICS). In our current products, we do not support some optional objects such as Life Safety Point and Life Safety Zone, this is clearly stated by the omission of  these objects in our device PICS. Looking at our bCX1-CR as an example, we support 19 of the optional standard BACnet object types. The list of those objects below was taken from our device PICS located here.
View full article
Picard Product_Support
‎2018-09-06 08:41 PM

Labels:
  • Andover Continuum
1654 Views

Error opening personnel object from PIM.

Issue  The following error comes up when attempting to open a personnel object with the Personnel Manager. (no issue if old style Personnel Editor is used) Personnel Manager Error getting personnel info Error getting profile info for Employee Error getting profile info for Employee. Error getting attribute info XmlInfo Error reading a database table. Environment CyberStation Cause Corrupted Personnel Manager configuration file. Resolution In the Continuum installation folder (typically C:\Program Files\Continuum) delete the PMAppButtonConfiguration.xml file. NOTE: PIM application customization settings are kept in the PMAppButtonConfiguration.xml file and will therefore be lost unless a backup of this file exists or the file can be copied from a second Workstation.
View full article
Picard Product_Support
‎2018-09-06 01:25 PM

Labels:
  • Andover Continuum
1699 Views

How to determine the part number for the card format required?

Issue Card part numbers are built up using the manufacturer, technology, type and format. How is this defined? Environment All systems using access control cards and readers. Cause Clarification on the part numbering is required. Resolution The part numbers for all cards and readers are built up using the format below, also full details of the products and all available part numbers are defined in the Electronic Access Control (EAC) catalogue. Any cards or tags that have a part number that ends in 000 will be un-programmed i.e. 654 xxxx 000. Readers that have a part number that ends in 000 will operate with and pass through all formats with the corresponding technology. i.e. A HID ProxPoint reader part number 654 1301 000 will operate with all formats of prox cards and tags. Other technologies may require the reader format to match the card to operate correctly. i.e. A FlexPass reader 654 2306 400 is formatted with Continuum 37 bit format it will require matching cards like the ISO cards 654 2352 400 that also has the 37 bit format. When ordering cards: if it is a new site specify this on the order, you will then be sent cards with a card number 1 through the number of cards ordered, and the next available site code (also called facility code). However if you are ordering cards for an existing site you will need to specify the range of card numbers required and the site (or facility) code required.
View full article
Picard Product_Support
‎2018-09-10 02:41 AM

Labels:
  • Andover Continuum
  • Field Devices
  • TAC INET
1488 Views

How to associate an alarm condition with a strings text color in a Pinpoint graphic.

Issue Want to have an alarm condition change the text color in a graphic to red when alarm and black when no alarm. Environment Continuum Pinpoint Graphics Cause When using a String object, you are unable to attach alarms to it. Therefore unable to use the "Alarm States And Colors" settings to control the text color. Another solution is required. Resolution One way that you can change the text color of a string objects value when an alarm changes state is to use the state of the string object (Enabled/Disabled) as the flag for the text color. In pinpoint on your "Active Text Object", change the Object State Enabled and Disabled colors to what you want the text color to show during your two conditions. On the controller, you will need to have an InfinityProgram that monitors your alarm condition/value and changes the State attribute of your String object to reflect the color you want to show. An example of the code used would be "STR_Text State = Alarm1", where STR_Text is your string and Alarm1 is a binary numeric or Input being monitored. See below image for details.
View full article
Picard Product_Support
‎2018-09-10 01:26 AM

Labels:
  • Andover Continuum
1136 Views

BACnet alarm not delivered to CyberStation.

Issue Event Enrollment shows Event State in alarm but the alarm notification is NOT delivered to CyberStation in the Event Notification recipient list. Environment CyberStation bCX4040 b4920 b3s Cause Download To BACnet Device option NOT selected when adding recipients in Event Notification object. Resolution When an Event Notification object resides in a controller (bCX or b3) the recipient information MUST be downloaded to the controller in order for alarm delivery to work. If in the list of recipient an entry has the Download field set to false remove the recipient from the list and add it again making sure the Download To BACnet Device checkbox remains checked.
View full article
Picard Product_Support
‎2018-09-06 01:29 PM

Labels:
  • Andover Continuum
1706 Views

Server error in '/webClient' Application

Issue Get server error in '/webClient' Application when attempting to connect with the WebClient Environment WebClient 1.93 Windows 7 Cause Bad installation Resolution 1. Run aspnet_regiis.exe -i (This is done from a DOS prompt, C:\Windows\Microsoft.net\Framework\v2.0.50727)  2. Re-install Continuum WebClient
View full article
Picard Product_Support
‎2018-09-10 12:33 AM

Labels:
  • Andover Continuum
1511 Views

Use a relay to control 3 stages with only 2 outputs

Issue A controller with only 2 available outputs is being used to control a 3 stage device. Environment Three stage device control where lower stages must remain active. Cause Hardware or space limitations may prevent there from being enough outputs to control a three stage device. Resolution Two controller outputs in conjunction with a DPDT (dual pole, dual throw) relay can be configured to control a three stage device. This will allow you to activate stage 1, stages 1 and 2 or all three stages by activating either one or both of the controller outputs. An example of when this might be used is to control three stages of heat or a three stage fan. A standard "ice cube" type relay can be used (IDEC RH2B or similar) and should be wired as shown in the diagram below.   The controller should be programmed to activate only output 1 for stage 1, activate only output 2 for stages 1 and 2 and finally to activate both outputs for stages 1, 2 and 3. Note that certain application specific controllers may not allow the outputs to be configured in the way described above and thus cannot take advantage of this setup.
View full article
Picard Product_Support
‎2018-09-06 01:35 PM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1636 Views

How to capture Continuum Cyberstation activity using ACCTrace

Issue Is there a way to capture CyberStation transactions so that I can debug workstation issues. I have been asked to send an ACCTrace capture file to Schneider Product Support.  How can I capture an ACCTrace record? Product Line Andover Continuum Environment CyberStation Workstation Continuum ACCTrace Extended logging Alarm delivery Alarm Logging Cause Some alarms are not being logged in continuum. Extended log data is missing or non existent. Resolution ACC Trace is a utility that can be used to capture the transactions CyberStation makes with controllers and with the Continuum database. ACCTrace.exe can be found in the Program Files\Continuum folder of the workstation PC. Once it is running, either use the default file name for the ACCTrace file, or a folder path and custom file name.  The extension should remain ".csv".  Note: ACCSniffer is a tool PSS generally does not use.  Once the capture file information is entered, select Start Trace.  Once the capture has been started, exercise the Continuum operations that are being tested.  Once the test is completed, select Stop Trace. The ACCTrace file is a complex record which cannot be readily interpreted by someone who does not have an advanced knowledge of Continuum software. It is often a good idea to include a Continuum Activity Log and Continuum Error log and possibly a Continuum Event log for cross analysis.
View full article
Picard Product_Support
‎2018-09-09 09:18 PM

Labels:
  • Andover Continuum
2812 Views

No response from I/O module when learning in an IOU

Issue An error was detected while attempting to set an attribute in a remote Infinity object Infinity Controller error: No response from I/O module Environment 99xx 9680 Continuum Cause FTT-10 IOU modules are not compatible with RS-485 Netcontrollers RS-485 IOU modules are not compatible with FTT-10 Netcontrollers Resolution There are a few ways to determine what bus topology type was built into a IOU module or Netcontroller  Take a look at the original purchase order which will indicate the type Look at the inside cover of the IOU module(s) and in the model description RS-485 or FTT-10 may be indicated Inside the cover of the Netcontroller and the IOU module there is a black component on the circuit board that has Echelon FTT-10 on it near the comm bus connector if it is FTT-10 Get the serial number of each of the IOU modules and the Netcontrollers and let Product Support know what they are, PSS can cross reference the number to determine the topology scheme from when it was manufactured If this isn't the issue then try the IOU with only that IOU connect in a different part of the IOU bus or by itself on the Netcontroller Under the cover RS-485 version - CX9900 Netcontroller 1   Under the cover FTT10 version - CX9900 Netcontroller 1
View full article
Picard Product_Support
‎2018-09-07 02:31 PM

Labels:
  • Andover Continuum
2719 Views

BACnet Schedule goes into Fault and shows a value of "ConfigurationError" in its Reliability field.

Issue After configuring a BACnet Schedule in a BCX or a b3 controller, it goes into Fault with its Reliability field showing "ConfigurationError". Environment CyberStation WebClient BCX40xx b3 BACnet Schedule Object Cause Configuration of BACnet schedule Incorrect point type used to configure BACnet schedule Resolution For each object type within BACnet (input, numeric, trendlog, etc.) each object property identifier (property) has an associated data type.  A list of data types for the each property can be found in Chapter 12 of the BACnet spec under the section for each object type.  The correct data type to configure in the schedule is determined by the Object property that is being controlled by the schedule object.  When using a schedule to control the value of a BinaryInput, BinaryOutput and BinaryValue objects, the Data Type that should be used is Enumerated. When using a schedule to control the value of a AnalogInput, AnalogOutput and AnalogValue objects, the Data Type that should be used is Real. When using a schedule to control the value of a MultiStateInput, MultiStateOutput and MultiStateValue objects, the Data Type that should be used is Unsigned Integer The Schedule object can be tricky to configure, however. There are several properties (Weekly_Schedule, Exception_Schedule, Schedule_Default) that must contain the same data type for all events. Since Enumerated is the “default” data type, the user may need to manually remove any existing events with the Enumerated type and replace them with the desired data type. If while configuring the schedule a message similar to the one above is displayed and accepted  all the events MUST be deleted otherwise a configuration error will result.
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

Labels:
  • Andover Continuum
2053 Views

EPI Builder will not run even though the security key is enabled for badging

Issue EPI Builder will not run even though the security key is enabled for badging Get error Badge Manager Cannot init license after clicking on Create/Edit Badge in Personnel Manager BadgeManager Cannot init license Environment Continuum EPI Builder Windows XP Keywords: account, admin, administrator, user, account, dongle, permission Cause The logged in user account does not have enough permission to run EPI Builder Administrator account runs EPI Builder OK Resolution Give the required user account enough permission to run EPI Builder Eg. Windows "Users" account may not have enough permission to run EPI Builder, where Windows "Power Users" normally have enough permission to run EPI Builder
View full article
Picard Product_Support
‎2018-09-07 06:54 AM

Labels:
  • Andover Continuum
1734 Views

BCX 4040 controller not being displayed in Continuum Explorer tree under the Infinity side but is on the bacnet side

Issue BCX not showing up on infinity side but shows up on the Bacnet side. Environment Continuum Cyberstation Explorer Cause View options in the Continuum Explorer were set to view the Continuum Bacnet device as Bacnet Only. Resolution In Continuum Explorer, select the menu item View Select Show Continuum Bacnet Device As Select Infinity Controller and Bacnet Device
View full article
Picard Product_Support
‎2018-09-07 06:07 AM

Labels:
  • Andover Continuum
1495 Views

webClient browser will not log on to Single User system, shows "Waiting for ServerName/WebClient/LogOn.aspx" in Internet Explorer.

Issue webClient browser will not log on to Single User system, shows "Waiting for ServerName/WebClient/LogOn.aspx" in Internet Root\ " ". Then check out the Workstation (Single User) screen, this will show error message: "The root path name could not be read, the root path name will be set to "Root\ " " See Screenshot: Environment Continuum webClient Single User V1.81 running on Windows XP SP2 Note: This scenario could also occur if a LAN Cyberstation were to be run up on the webClient IIS Server, but this is not a valid installation. Check out the webClient Installation guide on the software CD for valid LAN webClient configurations. Cause As the webClient IIS connections use the Cyberstation software to access the system SQL database, limiting the Cyberstation functionality will stop the additional webClient users from accessing the system. Resolution Ensure any users logged on to a Single user system have full system access or are logged off when connecting using the webClient Browser. Also use the inactivity timer in the User configuration to automatically log off users not active on the system. This issue does not apply to LAN systems where the webClient server is not used as a regular workstation.
View full article
Picard Product_Support
‎2018-09-07 04:05 AM

Labels:
  • Andover Continuum
1334 Views

b2 and i2 Controller Object Format property

Issue What is the b2 and i2 Controller Object Format property used for? Product Line EcoStruxure Building Operation Environment Continuum Conversion i2 Controller objects b3 controller objects Cause i2 and b3 Controller objects include a a Format field for objects created using the Continuum Conversion tool. What is this used for and how does the value effect the operation?     Resolution These Format values are propagated through the Continuum Conversion Tool for reference only and have no impact on operation in EBO. The values cannot be modified. In EBO there are two ways to configure numeric display formats. -In WorkStation property pane and watch window, the number of decimals displayed to the right of the decimal point is inherited from the WorkStation PC's regional settings. This setting applies to all values displayed in WorkStation except for values in graphics. -In graphics, the number decimals displayed to the right of the decimal point is configured value-by-value in the Graphics Editor.   The format value is not stored in an EBO export and if objects are manually created, then standard formats are used for the type of object created .
View full article
Dave_Shore Schneider Alumni (Retired)
‎2021-07-16 12:09 AM

Last Updated: Sisko DavidChild Sisko ‎2021-07-16 12:09 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
981 Views

Modbus RTU Float type polling using special function codes

Issue How to read float type point using the Modbus RTU Xdriver Product Line Andover Continuum Environment Modbus RTU (RS484) Cause Which Xdriver function code to use. Resolution When polling for a point of Float type and using the Xdriver. Use one of the Special function codes available in the Xdriver parameter list. For Float type use function code 245 or 248. See User Guide for further details.
View full article
Picard Product_Support
‎2018-09-06 01:52 PM

Last Updated: Sisko DavidChild Sisko ‎2021-04-22 07:53 AM

Labels:
  • Andover Continuum
1758 Views

Door reports "Valid Access No Entry" even though physically opened

Issue Upon presenting valid credentials at the door and physically entering thru it, the event reported for the transaction is "Valid Access No Entry" instead of the normal Valid Access event. The door is properly configured with a door switch but the controller does not see the door switch open. Product Line Andover Continuum Environment Continuum CX Gen 1 Continuum Net Controller II Cause For unknown reasons the door's entry and exit IOU are set to the same value, typically the GUI will not allow such invalid configuration. Resolution Edit the door and set the Exit IOU to zero (for a single-sided door) or to the appropriate IOU number associated with the AC1/AC1Plus on the exit side of the door. 
View full article
Captain AbeMeran Captain
‎2021-04-20 10:14 AM

on ‎2021-04-20 10:14 AM

Labels:
  • Andover Continuum
1190 Views

AS-P with infinet devices crashes during Spring time-change

Issue AS-P that has infinet devices connected to it, crashes during the Spring time-change of daylight savings. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Andover Continuum, infinet devices Cause Infinet schedules are sent down to the controller on a weekly basis. Having changed from default to be on Sunday between the time of 2:00 AM and 2:59 AM causes issues during daylight savings time "spring forward" due to that hour time span not existing. This causes the AS-P to crash. Resolution If you have schedules being download differently from the default time interval, ensure that they are not being done on Sundays, between the time of 2:00 AM and 2:59 AM. If they are, update them forward or back an hour to avoid further issues.
View full article
Commander JonGreen Commander
‎2021-03-26 12:58 PM

on ‎2021-03-26 12:58 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
789 Views

Passing InfinityString object between Continuum controllers

Issue InfinityProgram that sets the value of a local string object from the value of a remote string object frequently gets disabled. Product Line Andover Continuum Environment CyberStation CX9900 CX9702 CX9640 CX9680 ACX5720 ACX5740 i2 field devices Cause Passing string objects between controllers does not use the system's Import/Export system, strings are passed by point to point operation which can produce large amounts of traffic on the Infinet field bus. The program will disable if not properly written to account for events in the field bus that will knock controllers offline (i.e. field bus reconfigurations) Resolution Care must be taken when writing the program to 1. Fetch the string value at a reasonable interval instead of in every scan 2. Keep the program from disabling due to communication errors, bus reconfigurations etc, typically an error line (E:) is added to the problem to handle errors graciously. If possible transfer the value via a numeric point so that the I/E system is used as opposed to point to point.
View full article
Picard Product_Support
‎2018-09-06 02:00 PM

Last Updated: Sisko DavidChild Sisko ‎2021-03-17 07:30 AM

Labels:
  • Andover Continuum
1707 Views
  • « Previous
    • 1
    • …
    • 47
    • 48
    • 49
    • …
    • 110
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore