BCX 4040 controller not being displayed in Continuum Explorer tree under the Infinity side but is on the bacnet side
  • BCX 4040 controller not being displayed in Continuum Explorer tree under the Infinity side but is on the bacnet side
  • AdamSteele
    AdamSteele
  • Carl_Slack
    Carl_Slack
‎2018-09-07 06:07 AM
BCX not showing up on infinity side but shows up on the Bacnet side.
Continuum Cyberstation Explorer
View options in the Continuum Explorer were set to view the Continuum Bacnet device as Bacnet Only.
  1. In Continuum Explorer, select the menu item View
  2. Select Show Continuum Bacnet Device As
  3. Select Infinity Controller and Bacnet Device
  • 4590