How to read float type point using the Modbus RTU Xdriver
Andover Continuum
  • Modbus RTU (RS484)
Which Xdriver function code to use.
When polling for a point of Float type and using the Xdriver. Use one of the Special function codes available in the Xdriver parameter list. For Float type use function code 245 or 248.
See User Guide for further details.