Error opening personnel object from PIM.
  • Error opening personnel object from PIM.
  • AbeMeran
    AbeMeran
‎2018-09-06 01:25 PM
 The following error comes up when attempting to open a personnel object with the Personnel Manager.
(no issue if old style Personnel Editor is used)
Personnel Manager
Error getting personnel info
Error getting profile info for Employee
Error getting profile info for Employee. Error getting attribute info XmlInfo
Error reading a database table.
CyberStation
Corrupted Personnel Manager configuration file.
In the Continuum installation folder (typically C:\Program Files\Continuum) delete the PMAppButtonConfiguration.xml file.
NOTE: PIM application customization settings are kept in the PMAppButtonConfiguration.xml file and will therefore be lost unless a backup of this file exists or the file can be copied from a second Workstation.