Event Enrollment shows Event State in alarm but the alarm notification is NOT delivered to CyberStation in the Event Notification recipient list.
CyberStation
bCX4040
b4920
b3s
Download To BACnet Device option NOT selected when adding recipients in Event Notification object.
When an Event Notification object resides in a controller (bCX or b3) the recipient information MUST be downloaded to the controller in order for alarm delivery to work.
If in the list of recipient an entry has the Download field set to false remove the recipient from the list and add it again making sure the Download To BACnet Device checkbox remains checked.