AS-P with infinet devices crashes during Spring time-change
  • AS-P with infinet devices crashes during Spring time-change
  • RandyDavis
    RandyDavis
  • JonGreen
    JonGreen
Commander JonGreen Commander
‎2021-03-26 12:58 PM
on ‎2021-03-26 12:58 PM
AS-P that has infinet devices connected to it, crashes during the Spring time-change of daylight savings.
  • Building Operation Automation Server
  • Andover Continuum, infinet devices
Infinet schedules are sent down to the controller on a weekly basis. Having changed from default to be on Sunday between the time of 2:00 AM and 2:59 AM causes issues during daylight savings time "spring forward" due to that hour time span not existing. This causes the AS-P to crash.
If you have schedules being download differently from the default time interval, ensure that they are not being done on Sundays, between the time of 2:00 AM and 2:59 AM. If they are, update them forward or back an hour to avoid further issues.
Labels (2)
  • JonGreen21