Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC Vista
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac vista"

View in: "Building Automation Knowledge Base" | Community

2029 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 43
    • 44
    • 45
    • …
    • 102
  • Next »
Label: "TAC Vista" Show all articles

Adding an LNS Network to an XBuilder Project

Issue Cannot select LNS Database in Explorer after Browsing to the desired database. Can click on the LNS Database but it doesn't do anything. Correct way to add LNS Network to an XBuilder Project. Environment XBuilder Xenta Server LNS Network Cause Selecting an LNS network to add to an XBuilder project requires dragging and dropping the LNS network object rather than just clicking it Resolution In the Network pane of XBuilder expand the Xenta 5XX / 7XX / 9XX device to locate the LON port object. Right click the LON port object and select Insert Network from LNS... to open the TAC LNS Explorer. Drag the TAC LNS Explorer window to make the LON port object in the Network pane of XBuilder visible. In the TAC LNS Explorer select the File menu and select Open > Local LNS Networks. (This is assuming that the LNS network is on the local computer.) Identify the desired LNS network and click and drag it from the TAC LNS Explorer to the LON port object in the Network pane of XBuilder. The LNS network will then populate below the LON port object.
View full article
Picard Product_Support
‎2018-09-10 04:55 AM

Labels:
  • TAC Vista
1100 Views

Downloading a APB or NXE file to a controller in NL220

Issue Updating a application specific controller with a later firmware version Environment NL220 Cause Enhancements in firmware version need to be implemented into existing controllers of older firmware versions Resolution Here are the steps to download a new APB or NXE file in NL220. Locate the controller you wish to update in NL220. Right mouse click and select "Copy configuration values to memory" Right click on the same controller and select  "Download Program" Browse to the new APB or NXE file you want to download Once the download is complete you can paste the configuration back into the controller. Right click on the controller again and select "Paste configuration value(s) from memory" The controller is now updated with the new application.
View full article
Picard Product_Support
‎2018-09-10 04:53 AM

Labels:
  • TAC Vista
1106 Views

Blank page, No ID code or number displayed in login webpage and can not login to Xenta Server

Issue This issue has symptoms as below: Blank page, No ID code or number displayed in login webpage and can not login to Xenta Server. Can not access Xenta Server via webpage. The following blank page is displayed: Login page is displayed, but project name and ID code or ID number are not: Environment Windows Server Environment TAC Vista 5.1.X Xenta Server Ver 5.1.X Cause Windows Server "Internet Options" Security Settings are not set properly. Resolution Need add the Xenta Server IP address into "Trusted Sites" in "Internet Options>>Security>>Trusted Sites". If didn't add the IP address into "Trusted Sites", blank page would display; If just "http://%Xenta Server IP address%" is added into the "Trusted Sites", would get login webpage which didn't include project name and ID code in the login page; Need remove "http://%Xenta Server IP address%" from "Trusted Sites", and add "https://%Xenta Server IP address%" into "Trusted Sites" list;   Then could get correct login webpage,  
View full article
Picard Product_Support
‎2018-09-10 05:00 AM

Labels:
  • TAC INET
  • TAC Vista
1147 Views

Is it possible to remove the folder tree and alarm pane from webstation?

Issue Is it possible to remove the folder tree and alarm pane from webstation? Environment Vista webstation 5.1.X Cause Certain users have access to graphics and nothing else. It would therefore be better to be able to maximize the graphic resolution and not see the other panes. Resolution The folder View and Alarm View can be removed by editing the DefaultPage.aspx file. The DefaultPage.aspx file can be found in the folder C:\Inetpub\wwwroot\TACVistaWeb51X.
View full article
Picard Product_Support
‎2018-09-10 04:51 AM

Labels:
  • TAC Vista
1177 Views

Cannot reserve graphics object. Cause: Read-Only because object refers to a standard file

Issue Vista does not allow the user to edit standard graphics. Attempting to edit a standard object will result in the following error: Environment TAC Vista OGC Graphics Cause Vista does not allow the user to edit a standard graphic file within the vista database. A standard graphic is more of a shortcut to the master graphic in the root directory of TAC Vista Resolution Only make edits to the master graphic within the root directory of TAC Vista. This change will automatically be changed to all standard graphics associated to it.
View full article
Picard Product_Support
‎2018-09-10 04:50 AM

Labels:
  • TAC Vista
1139 Views

Error writing to device when trying to make changes to Xenta 121

Issue After making changes to Xenta 121 in ZBuilder and clicking OK or Apply an error is returned that says: Error writing to device - Errors occurred while writing to the device. Database and device may not be synchronized. Please download values from database and restart device manually Environment Xenta 121-FC,  Xenta 121-HP Vista Workstation ZBuilder Cause This error can occur if Vista is unable to connect to the Xenta 121 controller. Resolution Ensure that the Xenta 121 controller is powered on and that there is a reliable connection to the controller. To verify that the controller is talking to Vista either right click on the controller in Vista and select properties then click on the Neuron Status tab and check that the state is Configured, online. Alternatively, this can be checked in LonMaker by right clicking the device and selecting Properties and then clicking the Attributes tab. The State should say Configured, Online.
View full article
Picard Product_Support
‎2018-09-10 04:47 AM

Labels:
  • TAC Vista
1181 Views

Is it possible to create a switch, in TGML, which has a popup dialog to confirm the action taken (Yes/No)?

Issue Is it possible to create a switch, in TGML, which has a popup dialog to confirm the action taken (Yes/No)? Environment TGML editor 5.1.X Vista workstation 5.1.X Webstation 5.1.X Cause A customer wishes to confirm changes before applying them, to avoid setting variables by mistake. Resolution In the components library in TGML editor, there is a check box component which has a confirm function. Drag & drop the component onto the workspace and study the code. This can be used as a basis for a switch component.
View full article
Picard Product_Support
‎2018-09-10 04:49 AM

Labels:
  • TAC Vista
2178 Views

SNVTs supported in Xenta server 5.1.6

Issue Are the following SNVTs supported in Vista 5.1.6? SNVT_Amp_ac SNVT_Count_32 SNVT_Volt_ac Environment Xenta X5XX, X7XX, X9XX with firmware 5.1.6 Cause The SNVTs  SNVT_Amp_ac, SNVT_Count_32 and SNVT_Volt_ac are not included in the Xenta 5.1.6 firmware. They will be included in 5.1.7. There is however a workaround available in 5.1.6  Resolution Locate the SNVTtype.def file in the Xenta server. Connect to the Xenta server using an FTP client and locate the SNVTtype.def file under configdb/Lon/SNVTTYPE.def. Copy the file to your PC and make a backup copy Edit the file with a suitable text editor (notepad, notepad2 etc) -Locate the SNVT_amp definition -Add the following lines after SNVT_amp definition (see screenshot below): //---// amp_ac 139 2 1   INTEGER,,2,0,65535,1,0 //---// Repeat the process with the other 2 SNVTs - SNVT_count_32: Add the following lines after SNVT_count definition: //---// count_32 183 4 1 INTEGER,,7,-2147483648,2147483647,1,0,raw //---// - SNVT_volt_ac: Add the following lines after SNVT_volt definition: //---// volt_ac 138 2 1   INTEGER,,2,0,65535,1,0 //---// Replace the SNVTType.def file in the Xenta server using the FTP client.
View full article
Picard Product_Support
‎2018-09-06 01:09 PM

Labels:
  • TAC Vista
946 Views

Airflow reading in Xenta 102-AX fluctuates or is zero

Issue Airflow reading from Xenta 102-AX is jumping around and will not stabilize or is 0. Environment Vista Xenta 102-AX Plug-in LonMaker, NL-220 Cause For a variety reasons parameters may get changed in a Xenta 102-AX adversely affecting the controller's performance. Resolution Ensure that all of the parameters that affect the airflow reading are set properly. In some cases it may be best to restore the default parameters. Parameters that should be checked may be found through the Xenta 102-AX plug-in or through Vista but are grouped below how they are found in the plug-in starting with Unit Parameters: Unit Parameters Duct Area Ensure that the duct area is set properly for the box size. If a formula was used to determine the duct area from duct diameter verify that it yielded the correct result. For square or rectangular ducts use the following formula: For round ducts use the following formula: Pickup Factor The pickup factor is sometimes known as the K factor and is determined by examining the airflow curve diagram provided by the box manufacturer. It can often times be found on the box itself or in the manufacturer's literature. If the manufacturer's specs cannot be obtained use the default pickup factor, which is 2951.6. Box Constant The box constant is a product of the pickup factor and the duct area. It is sometimes available from the box manufacturer. If the manufacturer's data cannot be obtained use the default value, which is 1588.5. Note that the box constant will be changed from default if a CBC, or, calibrate box constant is performed. Airflow Parameters Velocity Pressure Gain The default settings here are 10 / 10 and are changed when a calibration is performed. If these numbers factor out to be very far from one you may want to reset them to their defaults and investigate if something went wrong with the calibration. For example these values may read 2957 / 3054 but since that factors out to 0.968 which is only about 3% off from one. However, if these numbers were 2957 / 6043 this would be a clear indicator that there was something wrong. Velocity Pressure Offset The default value here should be zero and considering that sensor is nominally set up for a 0-1" scale numbers greater than +0.1 or less than -0.1 should be cause to investigate further for mistakes during the calibration process.
View full article
Picard Product_Support
‎2018-09-06 01:10 PM

Labels:
  • TAC Vista
1848 Views

How to copy Xenta 102-AX parameters between controllers in NL220

Issue Is there a way to copy the setup parameters from one Xenta 102-AX VAV controller to another? Environment Xenta 102-AX NL220 Cause To assist in commissioning of many Xenta 102-AX controllers with similar configurations, parameters can be copied between controllers. Resolution Locate the controller you want to copy the parameters from. Right click on the controller and select "Copy configuration values to memory" Locate the controller you want to paste the parameters into. Right click on the controller and select "Paste configuration value(s) from memory" Then modify the parameters for that specific 102-AX as normal.
View full article
Picard Product_Support
‎2018-09-10 03:50 AM

Labels:
  • TAC Vista
1432 Views

Unable to make changes to LonMaker drawing.

Issue Attempts to make changes to LonMaker drawing results in error message that write access is not available. Environment LonMaker 3.1 Cause When the drawing is opened write access was not granted. By default write access is enabled, but it can be turned off when multiple users are accessing the same drawing file. Resolution When opening the network ensure that the "Show all network options dialogs" checkbox is checked. When you reach the Username prompt screen ensure that the "Write Access" field is checked and then complete opening the drawing.
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • TAC Vista
1219 Views

"This content cannot be display in a frame" error when using Vista WebStation

Issue When using a HyperLink in Vista WebStation graphic page the error message "This content cannot be display in a frame" is shown. Clicking the link to open this content in a new window will properly display the web page. Environment Vista WebStation 5.x.x Cause Newer web browsers support a HTTP header flag named X-Frame-Options which allows the remote web server to block display of its content within a web page frame. This is a security measure to stop "click jacking". Internet Explore 8, Internet Explorer 9 will display the error message Google Chrome will ignore the hyperlink. Resolution Instead of linking directly to the web page link to the folder that contains the Hyperlink object and then clicking on the hyperlink object will open the web page in a new window if the target property is empty or "_blank". Another alternative is simply click the "Open this content in a new window" link.
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • TAC Vista
1921 Views

Unable to set the nciSpaceTempOfst to a negative number in the Xenta 104-A plug-in

Issue The Xenta 104-A plug-in limits the temperature value input between 0°F and 18°F. It is not possible to input a negative value. Environment Xenta 104-A Plug-In Lonmaker 3.1 or Lonmaker 3.2 NL220 Cause The Xenta 104-A plug-in limits the temperature value input between 0°F and 18°F. It is not possible to input a negative value. Resolution In Vista follow these steps: Navigate to the Xenta 104-A controller. Browse down to the Node Object function block and find the nciSpaceTempOfst SCPT. Type in the designed space temp offset parameter from the default 32°F value. For example, if a -1°F offset is needed a value of 31 will need to be entered. If a +1°F offset is needed a 33 will need to be entered. 32°F represents zero offset.
View full article
Picard Product_Support
‎2018-09-06 01:12 PM

Labels:
  • TAC Vista
1646 Views

Unable to set the nciDischAirMax higher than 104°F in the Xenta 104-A plug-in

Issue The Xenta 104-A plug-in limits the temperature value input between 32°F and 104°F. Environment Xenta 104-A Plug-In Lonmaker 3.1 or Lonmaker 3.2 NL220 Cause The Xenta 104-A plug-in limits the temperature value input between 32°F and 104°F. Resolution In Vista follow these steps: Navigate to the Xenta 104-A controller. Browse down to the 8030 function block and find the nciDischAirMax SCPT. Type in the designed high discharge air temp value.
View full article
Picard Product_Support
‎2018-09-10 03:43 AM

Labels:
  • TAC Vista
1094 Views

Setting a Xenta 102-AX back to Factory Default Values

Issue How to set a Xenta 102-AX back to factory default values.  Environment Xenta 102-AX Vista LonMaker NL220 Factory Default Cause Unwanted changes can be reset back to factory values. Resolution To reset a Xenta 102-AX back to factory defaults, recommission the device and select Source of CP Values to default.
View full article
Picard Product_Support
‎2018-09-06 01:11 PM

Labels:
  • TAC Vista
1750 Views

The engine is in the process of converting a database. Internal. (Subsystem: NS, #165)

Issue The engine is in the process of converting a database. Internal. NS#165 error occurs when the user is attempting to delete a portion of the LNS database. For example, the error will occur when doing group bindings because the first step in the automated group binding process is to delete the old bindings. The error will also occur when deleting a controller, snvt, bindings, etc, out of the LNS database. Environment Lonmaker 3.2 NL220 Cause All instances of this error have been reported after upgrading an LNS 3.1 system to 3.2, and the upgrade process somehow does not finish. This has been reproduced in NL220 as well. Resolution Send your LNS database to Echelon for analysis at support@echelon.com.
View full article
Picard Product_Support
‎2018-09-10 04:04 AM

Labels:
  • TAC Vista
1143 Views

Is it possible to invert an alarm that comes from a BACNET (or other) device via a Xenta 913?

Issue Is it possible to invert an alarm that comes from a BACNET (or other) device via a Xenta 913? The signal is normally closed and the alarm is active when the signal = 0. Environment Tac Vista 5.1.X with alarms that come from devices under a Xenta 913 Cause Some devices have inverted (normally closed) alarm signal. Vista's default is that a signal is normally open. Resolution To invert the alarm signal go to the properties dialogue for the Change of State object and then the alarm tab. Change the Low limit to 0.5 and the high limit to -0.5.
View full article
Picard Product_Support
‎2018-09-10 04:08 AM

Labels:
  • TAC Vista
1269 Views

Vista OGC Graphics: Configuring Dynamic Text

Issue How to configure dynamic text in a Vista OGC Graphic. How do the set values affect the text and color? Environment Vista OGC Graphics OGC Editor Cause The order of the attribute values set in the OGC Dynamic Text editor will affect the operation on the live graphic page. Resolution Start by placing a generic text object on the page using the text tool from the toolbar.  Once the text has been placed on the page, double click it to open the Dynamic Text dialog. Browse to the Vista database value to monitor (ensuring that the Value attribute is selected). Enter the desired threshold values for each text string/color. Set the desired text and color for each value range. The values entered in the Value: dropdown list will act as a true hysteresis. In the above example with values 0, 10, 20, etc, if the value starts at zero, the text and formatting will remain constant until the value rises above 10. At that point, it will take on the text and style defined for 10. If the value drops back down to 9, it will remain unchanged. Only once it reaches the hysteresis value of 0 (or up to 20) will it change again. NOTE: Values defined in the Value: dropdown menu must be listed in sequential order or they will not perform as desired. For example, to add a value of -1 to the list, you would need to redefine all values 0-140 and > to come after the -1.
View full article
Picard Product_Support
‎2018-09-10 03:23 AM

Labels:
  • TAC Vista
1154 Views

Calibrate temperature sensors on a Xenta programmable controller.

Issue How can a temperature input be calibrated in a Xenta programmable controller. Environment Menta 5.x.x Cause The sensor input block in Menta does not have any calibration features. Instead these must be done with the program by the use of a calibration value. Resolution Use a PVR block and add this value to the raw senor input value to result in a calibrated value. By making the addition block public and giving it a name it will be visible from a Vista front end. If necessary it can be output as a SNVT as well. In this situation it might be advised to leave the AI block SAT_Raw public flag unchecked to provide a less cluttered view to the end user. While the calibration PVR is left at zero you will see the raw value from the sensor.
View full article
Picard Product_Support
‎2018-09-10 03:24 AM

Labels:
  • TAC Vista
1266 Views

Visio menu not displaying properly after installing Lonmaker 3.1 with Visio 2002

Issue After installing Lonmaker 3.1 with Visio 2002 the file menu within Visio is not displayed properly. You don't have any contacts in %s that can be chosen as your default business card. Using %s, add a contact and try to select a business card again. Or, select another PIM application from.... Product Line TAC Vista Environment Lonmaker 3.1 Visio 2002 Dell Latitude E600 & E610 Windows XP Cause The cause is unknown, but this issue has been observed on multiple occasions with fresh installs on Lonmaker 3.1 with Visio 2002, on Dell Latitude E600's & E610s with Windows XP Update: It seems to be the Bluetooth on these computers that causes this behavior.    Resolution Uninstalling Lonmaker 3.1 and reinstalling has proven to fix this issue on multiple occasions. If the uninstall and reinstall does not fix the issue please contact Echelon for further product support at lonsupport@echelon.com. Update: Before uninstalling LonMaker, try to disable the Bluetooth in BIOS and uninstall the Bluetooth software.  
View full article
Picard Product_Support
‎2018-09-10 03:21 AM

Labels:
  • TAC Vista
1583 Views
  • « Previous
    • 1
    • …
    • 43
    • 44
    • 45
    • …
    • 102
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore