LonWorks Sunblind Actuator Rolls Back After Full Movement
  • LonWorks Sunblind Actuator Rolls Back After Full Movement
  • CraigEl
    CraigEl
  • Benji
    Benji
  • MikaelKrantz
    MikaelKrantz
‎2018-09-06 08:41 AM
Last Updated: Administrator CraigEl Administrator ‎2025-11-11 03:51 PM
When opening (pulling up) the sunblind, it stops at the end of runtime and then rolls back down. Similarly, when closing (pulling down), it stops at the end of runtime and then rolls back up.
EcoStruxure Building Operation, TAC IA Series, TAC Vista
Lonworks devices including REG-N MSE4 (SVEA 32237-346) Sunblind actuators
The actuator is preconfigured for venetian blinds, which include lamella angle adjustments. For simple sunblinds, these parameters cause unintended motor actions after reaching the end position.
For non-venetian blinds:
  • Set the following parameters to zero:
    • UCPTdownPanelAngle
    • UCPTupPanelAngle
    • UCPTpanelTurnTime
    • UCPTpanelTurnTimeBottom
  • Ensure SNVTsetting commands have zero in the rotation part.
This disables unnecessary panel angle adjustments and prevents rollback after full movement.
Labels (3)
  • TAC IA Series
Tags (2)
  • 18376
  • CraigEllis25